[Equest-users] Curtain wall system - how to model baseline?

Nathan Miller via Equest-users equest-users at lists.onebuilding.org
Thu Jul 28 10:18:34 PDT 2016


Also if, you have conditioned spaces in an unconditioned parking garage (elevator lobbies, heated storage, mech/elec spaces, back of house space, etc), the walls that separate the conditioned space from unconditioned count in your wall areas, and typically don’t have much glazing, and help bring your proposed glazing % down.


Nathan Miller, PE, LEED AP BD+C – Mechanical Engineer/Senior Energy Analyst
RUSHING | D 206-788-4577 | O 206-285-7100
www.rushingco.com<http://www.rushingco.com/>

From: Nicholas.Caton at schneider-electric.com [mailto:Nicholas.Caton at schneider-electric.com]
Sent: Thursday, July 28, 2016 1:12 PM
To: mcamp1206 at gmail.com; Nathan Miller <nathanm at rushingco.com>
Cc: equest-users at lists.onebuilding.org
Subject: RE: [Equest-users] Curtain wall system - how to model baseline?

Spandrel (opaque) sections of curtainwall are “walls” in both proposed and baseline cases as far as 90.1 terminology is concerned.  Consider them as such for determining both Proposed and Baseline case WWR’s.

In my past year of experience, similar to Nathan, I’ve dealt with many “fishbowl” buildings which appear all (or mostly) glass from the outside but typically have at least few feet of insulated envelope on the interior perimeter, so in that case it’s literally a wall construction with the outermost layer being glazing (or airspace then glass).

Be sure to dig up any relevant envelope sections/details to carefully draw the line between “opaque” and “not opaque.”

~Nick



[cid:image001.png at 01D1E8D2.8823F890]
Nick Caton, P.E.
  Senior Energy Engineer
  Energy and Sustainability Services
  North America Operations
  Schneider Electric

D  913.564.6361
M  785.410.3317
E  nicholas.caton at schneider-electric.com<mailto:nicholas.caton at schneider-electric.com>
F  913.564.6380

15200 Santa Fe Trail Drive
Suite 204
Lenexa, KS 66219
United States

[cid:image001.png at 01D189AB.58634A10]



From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Michael Campbell via Equest-users
Sent: Thursday, July 28, 2016 11:12 AM
To: Nathan Miller
Cc: equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: Re: [Equest-users] Curtain wall system - how to model baseline?

Thanks for the response Nathan.
There will be some spandrel glass, but I'm not sure how much.
But basically the spandrel portion would be considered a wall in the baseline.
Only the transparent window assemblies would be considered in the WWR.  Is that correct?
Thank you,
Mike

On Thu, Jul 28, 2016 at 11:53 AM, Nathan Miller <nathanm at rushingco.com<mailto:nathanm at rushingco.com>> wrote:
Would there really be no opaque portions (aka spandrel) of the curtain wall? At the very least I’d expect you’d have about a 1’ high slab-edge-bypass opaque section.

Our curtainwall projects (resi and office) typically have 40-50% vision glazing, and the rest is opaque, and gets modeled as a wall with calculated U-factor depending on the spandrel + inboard insulation configuration.


Nathan Miller, PE, LEED AP BD+C – Mechanical Engineer/Senior Energy Analyst
RUSHING | D 206-788-4577<tel:206-788-4577> | O 206-285-7100<tel:206-285-7100>
www.rushingco.com<http://www.rushingco.com/>

From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org<mailto:equest-users-bounces at lists.onebuilding.org>] On Behalf Of Michael Campbell via Equest-users
Sent: Thursday, July 28, 2016 11:51 AM
To: equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: [Equest-users] Curtain wall system - how to model baseline?

Hello,
I have a potential project in which the client is proposing a curtain wall system.
The model will be based on ASHRAE 90.1-2013 Appendix G.
I believe the appropriate way to model this would be to have a WWR of 100% (or near 100%) in the proposed case.  For the baseline case, the window area would have to be reduced to get the WWR down to 40%.
Is this the correct way or is there different guidance for modeling curtain wall systems?
Thank you,
Mike Campbell


______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
______________________________________________________________________
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20160728/d65ab767/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 255 bytes
Desc: image001.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20160728/d65ab767/attachment-0004.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.png
Type: image/png
Size: 7893 bytes
Desc: image002.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20160728/d65ab767/attachment-0005.png>


More information about the Equest-users mailing list