[Equest-users] Chiller or boiler seasonal lockout
via Equest-users
equest-users at lists.onebuilding.org
Wed Jul 27 08:28:51 PDT 2016
LOOP-OPERATION à SNAP to an outdoor temp of 55-65 is my go-to quick means of approximating a seasonal heating/cooling plant lockout (and an appropriate starting point or guess when you don’t/can’t know an exact schedule for manual shutoff).
As Bill says, you can go further and assign a specific schedule under LOOP-OPERATION using an ON/OFF/TEMP. Natural progression when you have calendar dates in mind for the lockout and/or you have a combination of snap behavior and forcing things off to consider.
If you need to lock out SPECIFIC boilers/chillers, then you gotta step up to equip-controls/load-management. Eliminate the simpler options before pressing forward.
~Nick
Nick Caton, P.E.
Senior Energy Engineer
Energy and Sustainability Services
North America Operations
Schneider Electric
D 913.564.6361
M 785.410.3317
E nicholas.caton at schneider-electric.com <mailto:nicholas.caton at schneider-electric.com>
F 913.564.6380
15200 Santa Fe Trail Drive
Suite 204
Lenexa, KS 66219
United States
From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Bishop, Bill via Equest-users
Sent: Wednesday, July 27, 2016 8:34 AM
To: Chris Jones; John Aulbach; equest-users at onebuilding.org
Subject: Re: [Equest-users] Chiller or boiler seasonal lockout
John,
I would just use LOOP-OPERATION -> SCHEDULED for the CHW loop instead of bothering with the equipment control and load management.
Regards,
~Bill
William Bishop, PE, BEMP, BEAP, CEM, LEED AP | Pathfinder Engineers & Architects LLP
Senior Energy Engineer
134 South Fitzhugh Street Rochester, NY 14608
T: (585) 698-1956 F: (585) 325-6005
bbishop at pathfinder-ea.com <mailto:wbishop at pathfinder-ea.com> www.pathfinder-ea.com <http://www.pathfinder-ea.com/>
Carbon Fee and Dividend - simple, effective, and market-based.
From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Chris Jones via Equest-users
Sent: Wednesday, July 27, 2016 8:32 AM
To: John Aulbach <jra_sac at yahoo.com>; equest-users at onebuilding.org
Subject: Re: [Equest-users] Chiller or boiler seasonal lockout
John,
I wasn’t able to achieve the seasonal control. I am not sure what the correct steps are. It seems like it should be fairly simple – one flag for LOOP-ON and another flag for LOOP-OFF but it doesn’t seem to work.
Christopher Jones, P. Eng.
Rowan Williams Davies & Irwin Inc.
Consulting Engineers & Scientists
901 King Street West, Suite 400, Toronto, Ontario, M5V 3H5
T: (519) 823-1311 ext 2052
M: (416) 697-0056
From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of John Aulbach via Equest-users
Sent: Tuesday, July 26, 2016 7:51 PM
To: equest-users at onebuilding.org
Subject: [Equest-users] Chiller or boiler seasonal lockout
I thought I had a correct example, but it appears the chiller I have is not shutting off during the winter season. What am i doing wrong (I can apply this also to boiler).
Thanks. It has been a long day.
John R. Aulbach, PE
________________________________
RWDI - One of Canada's 50 Best Managed Companies - This communication is intended for the sole use of the party to whom it was addressed and may contain information that is privileged and/or confidential. Any other distribution, copying or disclosure is strictly prohibited. If you received this email in error, please notify us immediately by replying to this email and delete the message without retaining any hard or electronic copies of same. Outgoing emails are scanned for viruses, but no warranty is made to their absence in this email or attachments. If you require any information supplied by RWDI in a different format to facilitate accessibility, contact the sender of the email, email solutions at rwdi.com or call +1.519.823.1311.
________________________________
______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
______________________________________________________________________
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20160727/9bc7b7a2/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 255 bytes
Desc: image004.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20160727/9bc7b7a2/attachment-0006.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 7893 bytes
Desc: image005.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20160727/9bc7b7a2/attachment-0007.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1256 bytes
Desc: image007.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20160727/9bc7b7a2/attachment-0004.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1322 bytes
Desc: image009.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20160727/9bc7b7a2/attachment-0005.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 2851 bytes
Desc: image011.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20160727/9bc7b7a2/attachment-0008.png>
More information about the Equest-users
mailing list