[Equest-users] *****SPAM***** RE: How do you think about the no electricity Eco-Coolers from Bangladesh
Joe Huang via Equest-users
equest-users at lists.onebuilding.org
Wed Jul 20 12:38:46 PDT 2016
This reminds me of the hoopla about "Cold Fusion" 30 years ago. Gad, am I showing my age! :-( :-(
Joe
Joe Huang
White Box Technologies, Inc.
346 Rheem Blvd., Suite 205A
Moraga CA 94556
yjhuang at whiteboxtechnologies.com
http://weather.whiteboxtechnologies.com for simulation-ready weather data
(o) (925)388-0265
(c) (510)928-2683
"building energy simulations at your fingertips"
On 7/20/2016 5:28 AM, Chris Jones wrote:
>
> My observations are that the air does heat up when compressed then cooled when it
> decompresses. For example, if you have a large take of compressed air used to fill a
> small tank, the small tank heats up as it is filled and the large tank cools off as it
> does the filling of the small tank.
>
> That would lead me to believe that, in the end, the air would be roughly the same
> temperature after it went through the compression then decompression as it traveled
> through the bottles from outside to inside. The bottles might absorb some of the heat
> from the compressed air and then you would have a wall that is warmer than room. In the
> end, I don’t believe there would be much change in temperature in the room.
>
> **
>
> *Christopher Jones, P. Eng.*
>
> *Rowan Williams Davies & Irwin Inc.*
> /Consulting Engineers & Scientists/
> 901 King Street West, Suite 400, Toronto, Ontario, M5V 3H5
> *T:* (519) 823-1311 ext 2052
>
> *M:*(416) 697-0056
>
> *From:*Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] *On Behalf Of
> *Joe Huang via Equest-users
> *Sent:* Tuesday, July 19, 2016 8:54 PM
> *To:* equest-users at lists.onebuilding.org
> *Subject:* Re: [Equest-users] How do you think about the no electricity Eco-Coolers from
> Bangladesh
>
> I saw today the same technology also promoted on the CIBSE Bulletin Board even with a
> video "explaining" how it works (the plastic bottles supposedly "compresses and cools
> the air")
>
> (
> https://www.linkedin.com/groups/75555/75555-6160367729091100672?midToken=AQF3zdCi1vKWLA&trk=eml-b2_anet_digest_of_digests-hero-8-view%7Ediscussion&trkEmail=eml-b2_anet_digest_of_digests-hero-8-view%7Ediscussion-null-bc6m0%7Eiqtrhngl%7Eh3
> )
>
> To me, this seems more like wishful thinking. My comment posted on the CIBSE Bulletin
> Board was:
>
> I don't understand how this would work from a thermodynamic point of view. There has to
> be some air velocity to begin with, in which case I can see how the bottles might
> channel the air flow resulting in higher air velocities coming out of the bottle
> openings, but wouldn't the total amount of air flow be the same, or less than through
> the window opening with no obstruction? Also, someone explain to me how compressing the
> air will cool it?? I've always thought that compressing the air would heat it up,
> although in this case the effect would be extremely minimal either way.
>
> Joe
>
> Joe Huang
> White Box Technologies, Inc.
> 346 Rheem Blvd., Suite 205A
> Moraga CA 94556
> yjhuang at whiteboxtechnologies.com <mailto:yjhuang at whiteboxtechnologies.com>
> http://weather.whiteboxtechnologies.com for simulation-ready weather data
> (o) (925)388-0265
> (c) (510)928-2683
> "building energy simulations at your fingertips"
>
> On 7/14/2016 7:22 PM, 冷面寒枪 via Equest-users wrote:
>
> Recently,I read the news about the zero air cooler,which is made with re-purposed
> plastic bottles.And the new claims that it helps reduce indoor temperature by 5
> degrees centigrade.
>
> The making process is shown as following:
>
> I dout that very much.
>
> the Joule-Thomson Coefficient for air (mostly nitrogen) at 300K (27°C/80°F) is about
> 0.36K/bar. This means that at 300K a 1bar change in pressure equates to a 0.22K. The
> change in pressure required to get the 5°C (5K) reduction would therefore be:
>
> 5 / 0.22 = 22.7bar
>
> So I think it is impossible the temperature drop will be up to 5 degrees centigrade
> after the air through the bottle.
>
> What do you think?
>
> ------------------
>
> *Yongqing Zhao*
>
> *Changsha Green Building & Energy Saving Technology CO.,LTD**
> *NO.438,Shaoshan Road,Changsha,Hunan,China
> Telephone:13574805636
>
> Email:zhaoyongqing1987 at 126.com <mailto:Email:zhaoyongqing1987 at 126.com>
>
> 503271081 at qq.com <mailto:503271081 at qq.com>
>
>
>
>
> _______________________________________________
>
> Equest-users mailing list
>
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
>
> To unsubscribe from this mailing list send a blank message toEQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
> <mailto:EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG>
>
> Guelph Move
> ------------------------------------------------------------------------------------------
> RWDI - One of Canada's 50 Best Managed Companies - This communication is intended for
> the sole use of the party to whom it was addressed and may contain information that is
> privileged and/or confidential. Any other distribution, copying or disclosure is
> strictly prohibited. If you received this email in error, please notify us immediately
> by replying to this email and delete the message without retaining any hard or
> electronic copies of same. Outgoing emails are scanned for viruses, but no warranty is
> made to their absence in this email or attachments. If you require any information
> supplied by RWDI in a different format to facilitate accessibility, contact the sender
> of the email, email solutions at rwdi.com or call +1.519.823.1311.
> ------------------------------------------------------------------------------------------
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20160720/e2d6789c/attachment-0005.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 157349 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20160720/e2d6789c/attachment-0006.jpe>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 109500 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20160720/e2d6789c/attachment-0007.jpe>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 106626 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20160720/e2d6789c/attachment-0008.jpe>
More information about the Equest-users
mailing list