[Equest-users] Modeled Interior Floors as Exterior Roofs
Darryl Kasun via Equest-users
equest-users at lists.onebuilding.org
Wed Jul 13 14:38:41 PDT 2016
Hi Jeff,
I think I'm on the same page as you now. Let me give a little information
about this project just so I can assure myself I'm modeling this correctly.
I have the design drawings/specs for a hospital which using as the inputs
for the eQUEST model. The majority of spaces are heated/cooled/ventilated
by central AHUs with VAVs c/w reheat coils along the perimeter. If I model
the zones without plenums, do I not run the risk of seeing unmet loads in
the perimeter zones as the reheat coils may not be large enough for say the
peak heating load for that zone?.
On Wed, Jul 13, 2016 at 2:24 PM, Haberl, Jeff <jhaberl at tamu.edu> wrote:
> Hello Darryl:
>
>
>
> Yes, the heating/cooling loads should be showing up in the SYSTEMS
> reports. However, it will be in a “lump” that does not allow you to
> separate out the individual components. You can switch it on/off by using
> the direct return option, but then this chops out those surfaces from
> participating in the simulation, depending on how you’ve linked up the
> plenums to the spaces in the next-to commands (or how the DOE2.2 robot does
> it).
>
>
>
> You can see the loads in the plenums, but it will not show up in the UNMET
> loads because there is no thermostat in the plenum…hence no UNMET loads.
>
>
>
> Jeff
>
>
>
> PS: That’s off the top of my head…the eQUEST manual might shed more light
> on this.
>
>
>
> 8=! 8=) :=) 8=) ;=) 8=) 8=( 8=) 8=() 8=) 8=| 8=) :=') 8=) 8=?
> Jeff S. Haberl, Ph.D.,P.E.inactive,FASHRAE,FIBPSA,......jhaberl at tamu.edu
> <........jhaberl at tamu.edu>
> Professor........................................................................Office
> Ph: 979-845-6507
> Department of Architecture............................................Lab
> Ph:979-845-6065
> Energy Systems Laboratory...........................................FAX:
> 979-862-2457
> Texas A&M
> University...................................................77843-3581
> College Station, Texas, USA, 77843..............................URL:
> www.esl.tamu.edu
> 8=/ 8=) :=) 8=) ;=) 8=) 8=() 8=) :=) 8=) 8=! 8=) 8=? 8=) 8=0
>
>
>
>
>
> *From:* Darryl Kasun [mailto:darryl.kasun at gmail.com]
> *Sent:* Wednesday, July 13, 2016 4:18 PM
> *To:* Haberl, Jeff <jhaberl at tamu.edu>
> *Subject:* Re: [Equest-users] Modeled Interior Floors as Exterior Roofs
>
>
>
> Hi Jeff,
>
>
>
> Thanks for the reply. A couple of comments:
>
>
>
> - The hospital does have plenums and the heat gains/losses thru the plenum
> exterior surfaces would affect the return air to whatever system is serving
> that space. Will the system not see this load? I suspect it does and thus
> other than not being able to see the peak load, is there any other downside
> to having plenums?
>
> - If I want the plenum loads to show up in the peak loads report by not
> creating plenums, I suspect I will see unmet loads in these plenum-less and
> thus larger zones as the designed equipment capacities will not be able to
> meet loads.
>
>
>
> Thanks again
>
> Darryl Kasun
>
>
>
> On Wed, Jul 13, 2016 at 2:04 PM, Haberl, Jeff <jhaberl at tamu.edu> wrote:
>
> Hello Darryl:
>
>
>
> It may be worse than you think.
>
>
>
> From the looks of the image it also appears that you have plenums in the
> building, which further complicates the simulation, and for reasons that
> are not always obvious. For example, in DOE-2 if you declare the return air
> path as having a plenum and then assign the walls, roof, floor, etc. to
> that plenum as the zone, then the heat gain/loss from that surface is
> assigned to the air that is returning from the zone on its way back to the
> HVAC system and therefore, it will not show up in the peak load in LOADS
> because it is a heat gain to the return air and not the zone. You can prove
> this to yourself using the SAMP1 file that comes with DOE-2.
>
>
>
> For example, in the SAMP1.INP file that comes with DOE-2, RUN 3A, there is
> a single story 5 zone model with a plenum. What you will notice when you
> run this model is there is no roof load in LOADS because the single story
> building has a plenum and the roof load has been assigned to the plenum as
> the zone. The load from the roof does show up when you assign a SYSTEM
> where it then appears as heat gain/loss from the return air.
>
>
>
> To “see” the load from the roof you have to remove the plenum and
> re-proportion the roof to the zone area. Then the roof shows up in the
> component loads in the LOADS peak load report.
>
>
>
> I suspect that deep inside the bowels of the model you showed below this
> is going on.
>
>
>
> Jeff
>
>
>
> 8=! 8=) :=) 8=) ;=) 8=) 8=( 8=) 8=() 8=) 8=| 8=) :=') 8=) 8=?
> Jeff S. Haberl, Ph.D.,P.E.inactive,FASHRAE,FIBPSA,......jhaberl at tamu.edu
> <........jhaberl at tamu.edu>
> Professor........................................................................Office
> Ph: 979-845-6507
> Department of Architecture............................................Lab
> Ph:979-845-6065
> Energy Systems Laboratory...........................................FAX:
> 979-862-2457
> Texas A&M
> University...................................................77843-3581
> College Station, Texas, USA, 77843..............................URL:
> www.esl.tamu.edu
> 8=/ 8=) :=) 8=) ;=) 8=) 8=() 8=) :=) 8=) 8=! 8=) 8=? 8=) 8=0
>
>
>
>
>
> *From:* Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] *On
> Behalf Of *Darryl Kasun via Equest-users
> *Sent:* Wednesday, July 13, 2016 2:42 PM
> *To:* equest-users at lists.onebuilding.org
> *Subject:* [Equest-users] Modeled Interior Floors as Exterior Roofs
>
>
>
> Hey everyone,
>
>
>
> The hospital I am working has different footprints for each level (see
> snapshot below). While going thru the bldg. envelope in detailed mode, I
> noticed that the surfaces separating interior floors are modeled as
> exterior roofs. Now it’s been a while since I’ve modeled using eQUEST but
> I’m sure these surfaces should be modeled as interior floors.
>
>
>
>
>
>
>
> So a couple questions:
>
>
>
> 1) What did I miss in the DD Wizard? One shell was made for each
> elevation, and for the each above grade floor, below is the input entered
> for the floor info. Is this where I made my mistake? Or do I need to
> model the shells with and without roofs separately?
>
>
>
>
>
> 2) Is there a fast way to change what’s needed without deleting each
> “interior roof” and replacing it with an interior floor or going back into
> the DD wizard? Pretty sure not but here’s hoping!
>
>
>
> Thanks everyone. Hope your mid-week is going well!!
>
>
>
> Darryl Kasun
>
>
>
>
>
>
>
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20160713/60c01126/attachment-0005.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.png
Type: image/png
Size: 48496 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20160713/60c01126/attachment-0010.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 70946 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20160713/60c01126/attachment-0011.png>
More information about the Equest-users
mailing list