[Equest-users] [Bldg-sim] 90.1-2007 App. G baseline fan power	question
    via Equest-users 
    equest-users at lists.onebuilding.org
       
    Tue Jul 12 06:17:29 PDT 2016
    
    
  
This is totally appropriate as far as 90.1/LEED guidance.
 
I have in the past also pursued a “simplified” approach wherein I dump all Pfan power onto the supply fan and make the associated return fan “powerless” (very tiny kW/CFM).  I’ve been clear in documentation and that approach made it through a few reviews without comment.  This might for some baseline systems have some relative effect on baseline auto-sizing capacities considering fan heat loads relative to cooling coils, but in the aggregate I’m not certain this should have any substantial / consistent energy performance impact between projects.
 
Food for thought ;-),
 
~Nick
 
 
Nick Caton, P.E.
  Senior Energy Engineer
  Energy and Sustainability Services
  North America Operations
  Schneider Electric
D  913.564.6361 
M  785.410.3317 
E  nicholas.caton at schneider-electric.com <mailto:nicholas.caton at schneider-electric.com> 
F  913.564.6380
15200 Santa Fe Trail Drive
Suite 204
Lenexa, KS 66219
United States
 
 
 
From: Bldg-sim [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Chris Jones via Bldg-sim
Sent: Monday, July 11, 2016 4:15 PM
To: Jim Dirkes
Cc: bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] 90.1-2007 App. G baseline fan power question
 
Thanks for your response Jim.
 
 
Christopher Jones, P. Eng.
Rowan Williams Davies & Irwin Inc.
Consulting Engineers & Scientists
901 King Street West, Suite 400, Toronto, Ontario, M5V 3H5
T: (519) 823-1311 ext 2052 
M: (416) 697-0056 
 
From: Jim Dirkes [mailto:jim at buildingperformanceteam.com] 
Sent: Monday, July 11, 2016 5:10 PM
To: Chris Jones
Cc: bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] 90.1-2007 App. G baseline fan power question
 
Nothing from GBCI on my projects.  My normal practice is to split the power roughly in proportion to pressure rise.
 
On Mon, Jul 11, 2016 at 5:03 PM, Chris Jones via Bldg-sim <bldg-sim at lists.onebuilding.org> wrote:
The App. G baseline is to have return or relief fans if the proposed case does. This would imply that the system fan power should be distributed between the supply and return fans in the baseline case but no direction is given in the Standard nor in the User’s Manual. My inclination would be to distribute the fan power in the baseline case using the same proportions as in the proposed case.
 
Has anyone had any experience with directions given by the GBCI in this regard?
 
 
Christopher Jones, P. Eng.
Rowan Williams Davies & Irwin Inc.
Consulting Engineers & Scientists
901 King Street West, Suite 400, Toronto, Ontario, M5V 3H5
T: (519) 823-1311 ext 2052 <tel:%28519%29%20823-1311%20ext%202052>  
M: (416) 697-0056 <tel:%28416%29%20697-0056>  
 
 
________________________________
RWDI - One of Canada's 50 Best Managed Companies - This communication is intended for the sole use of the party to whom it was addressed and may contain information that is privileged and/or confidential. Any other distribution, copying or disclosure is strictly prohibited. If you received this email in error, please notify us immediately by replying to this email and delete the message without retaining any hard or electronic copies of same. Outgoing emails are scanned for viruses, but no warranty is made to their absence in this email or attachments. If you require any information supplied by RWDI in a different format to facilitate accessibility, contact the sender of the email, email solutions at rwdi.com or call +1.519.823.1311 <tel:%2B1.519.823.1311> . 
________________________________
_______________________________________________
Bldg-sim mailing list
http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
To unsubscribe from this mailing list send  a blank message to BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
 
-- 
James V Dirkes II, PE, BEMP, LEED AP
CEO/President
The Building Performance Team Inc.
1631 Acacia Dr, GR, Mi 49504
Direct: 616.450.8653
jim at buildingperformanceteam.com
Website <http://buildingperformanceteam.com> l  LinkedIn <https://www.linkedin.com/pub/jim-dirkes/7/444/413>  | May 2016 ASHRAE Journal article on energy modeling <http://buildingperformanceteam.com/bpt-insights-blog/item/73-modeled-performance-isn-t-actual-performance> 
For breaking the natural law, there are natural penalties:
Those who live by knives die by them. 
Those who betray their friends lose them.
Those who abandon their children never know the sweetness of their kiss. 
Those who travel from bed to bed lose the capacity for trust. 
Those who torture their consciences are tortured by them in return. 
Those who refuse the one in whose Image they are made live as strangers to themselves.
 Guelph Move<http://emergency.rwdi.com/RWDI-Guelph-Move-Notice.gif> 
________________________________
RWDI - One of Canada's 50 Best Managed Companies - This communication is intended for the sole use of the party to whom it was addressed and may contain information that is privileged and/or confidential. Any other distribution, copying or disclosure is strictly prohibited. If you received this email in error, please notify us immediately by replying to this email and delete the message without retaining any hard or electronic copies of same. Outgoing emails are scanned for viruses, but no warranty is made to their absence in this email or attachments. If you require any information supplied by RWDI in a different format to facilitate accessibility, contact the sender of the email, email solutions at rwdi.com or call +1.519.823.1311. 
________________________________
______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
______________________________________________________________________
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20160712/2131ec19/attachment-0005.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 255 bytes
Desc: image001.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20160712/2131ec19/attachment-0010.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.png
Type: image/png
Size: 7893 bytes
Desc: image002.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20160712/2131ec19/attachment-0011.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.jpg
Type: image/jpeg
Size: 823 bytes
Desc: image003.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20160712/2131ec19/attachment-0002.jpg>
    
    
More information about the Equest-users
mailing list