[Equest-users] WSHP System with PS-H Report Circulation Loop Overload

Nicholas Caton ncaton at catonenergy.com
Wed Jan 27 10:46:44 PST 2016


Hi Kathryn,



I can’t answer without digging in myself, but I *think* if you follow along
with the textual description of PLANT simulation in the DOE2 engineers
manual (I’d attach, but don’t have my library handy atm – it’s out there in
google!), leveraging your intimacy with the project-at-hand as a working
example, you might come up with a better understanding of exactly what that
“overload” figure is in isolation.  There’s a bulleted list somewhere in
there that explains the order in which various parts of your model are
considered before the remaining loop loads (for any loop type) are labeled
“overload.”



A separate shot in the dark from the hip:  It may be possible the reason
“net peak + overload peak =/= total peak” could have to do with one or more
heatpumps on the loop operating in the reverse direction during the peak
hour… maybe… or not… =)



~Nick



---------------------------------------------------------------------------------------------------------------------------------------------

*Nick Caton, P.E.*

  Senior Energy Engineer
  Energy and Sustainability Services
  North America Operations
  Schneider Electric

D  913.564.6361
M  785.410.3317
E  nicholas.caton at schneider-electric.com
F  913.564.6380

15200 Santa Fe Trail Drive
Suite 204
Lenexa, KS 66219
United States

[image: http://10.218.104.225:8090/Images/SE.comCapsule.png]
<http://www.schneider-electric.com/ww/en/>



*Please consider the environment before printing this e-mail







*From:* Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] *On
Behalf Of *Kathryn Kerns
*Sent:* Friday, January 22, 2016 2:10 PM
*To:* equest-users at lists.onebuilding.org
*Subject:* [Equest-users] WSHP System with PS-H Report Circulation Loop
Overload



Everyone, I made an energy model of a building being served by water source
heat pumps attached to a typical water loop with a fluid cooler and a
boiler. I let eQuest size all the equipment including the boiler and water
source heat pumps. The PS-H Water Loop report showed the following:











Notice that in January, the peak heating load is -991.9 kbtu/hr, the peak
net load is -576.1 kbtu/hr, and the peak over load is -355.6 kbtu/hr.
eQuest sized the water loop boiler to be -576.1 kbtu/hr. I believe these
numbers are correct and the boiler size is correct but I cannot find an
explanation in a document telling me how net load and over load is
calculated and what they mean. I can explain how eQuest develops the heat
load, but not the other two loads. I know a typical hot water coil system
has heat load peaks equal to net load peaks and the over loads are usually
zero. I am pretty sure the over load value is related to the heat pump COP,
but I would like to be able to point to a written piece of documentation
explaining this. Anybody know where to look?



Thanks.





P.S. the energy model ran successfully with less than 10 heating hours out
of throttling range.





*Kathryn Kerns*

*Systems Specialist*

*BCE* *Engineers, Inc.*

*| Ph: 253.922.0446 | Fx: 253.922.0896 |*
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20160127/3faa8f98/attachment-0005.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.gif
Type: image/gif
Size: 1822 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20160127/3faa8f98/attachment-0005.gif>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.png
Type: image/png
Size: 5423 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20160127/3faa8f98/attachment-0010.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image004.png
Type: image/png
Size: 36163 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20160127/3faa8f98/attachment-0011.png>


More information about the Equest-users mailing list