I am not clear whether the supply fan volume is also too high or just
the return volume.
If supply volume:
- Check the SV-A to see if the altitude correction factor is 1.0. If
not, set your altitude to 0 on Project & Site -> Site Data.
- Check your system sizing ratio -- if you specify a supply flow and a
sizing ratio, the flow entered will be multiplied by the sizing ratio.
If just return volume -- you can specify a return fan volume on the flow
parameters tab of Air-Side HVAC -> Fans
On 11/02/2016 10:41 AM, shilpa surana wrote:
> Simulation Community,
>
> I have a question regarding the EMIT Baseline fan power calculator, a
> tool provided to the energy modelers by RMI. I have used the
> calculator to determine the baseline fan power. I have entered the
> supply airflow from the autosized baseline model, exhaust air flow as
> the outside air flow and the appropriate supply fan ratio and return
> fan ratio in the calculator. I used the inputs in kW/cfm provided by
> the calculator in the Baseline model. However, the SVA report is
> reporting higher return fan power as the model is auto sizing the
> return flows higher than what the EMIT tool is using for calculations.
> EMIT tool determines the return airflow by subtracting exhaust airflow
> from the supply airflow. As a result when I fill out the Section 1.4
> table inputs, the calculated total fan power from the software is
> higher than the Baseline allowance.
>
> Has anyone faced similar issues when calculating the baseline fan
> power allowances?
>
> Thanks,
>
> */Shilpa Surana/*
>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20160211/b97b8066/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: bfhhedai.png
Type: image/png
Size: 53964 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20160211/b97b8066/attachment-0002.png>
More information about the Equest-users
mailing list