[Equest-users] FW: DOE2 Batch Processing Error
Drew Morrison
DMorrison at seventhwave.org
Fri Feb 5 13:36:46 PST 2016
Looks like there’s a solution.
At first, I tried copying the text replacing the text in the usrlib.dat folder in the …\doe22 directory with the text from the eQ_Lib.dat file in the …\eQuest 3-64 Data\DOE-2 folder. That didn’t change anything. Eventually I found out that the library entries triggering errors in the BDL file were not present in the BDLLIB.dat file. However, they were in the original userlib.dat file. I copied the library entries for the missing components (which were some construction materials, a water heater performance curve, and all the hourly report library entries) into the BDLLIB.dat file, and the simulation ran without a hitch:
[cid:image001.png at 01D1602A.7AA6CDE0]
I’m not sure what the DOE2 scripts are doing with the library files, since the same entries are missing in the eQuest folder’s BDLLIB file, and yet running the simulation in eQuest works perfectly. Since the simulation now executes from the command line successfully, the problem is solved for the moment, though I don’t feel any less confused about what’s going on. And unfortunately, the simulation doesn’t appear to run significantly faster, since the total elapsed time was still over 4 minutes.
Still, thanks for all your help and suggestions. Despite my ongoing confusion, I feel like I’ve learned a lot about what goes on behind the scenes in DOE2. And if anyone has any insights as to why appending missing library entries to the BDLLIB file fixed this run, I’d love to hear them.
Cheers,
Drew Morrison, Energy Engineer
Seventhwave
608.210.7151 seventhwave.org
From: Julien Marrec [mailto:julien.marrec at gmail.com]
Sent: Friday, February 05, 2016 3:11 PM
To: Drew Morrison <DMorrison at seventhwave.org>
Cc: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] FW: DOE2 Batch Processing Error
Very likely because you are using the doe library and not equest's
I posted something a while back with a modified bat script that allows you to choose your equest version.
Try and find it in the archive if you can't let me know and I'll find it next time I'm on a computer
Envoyé de mon iPhone
Le 5 févr. 2016 à 19:04, Drew Morrison <DMorrison at seventhwave.org<mailto:DMorrison at seventhwave.org>> a écrit :
Hi Everyone,
I’ve got an issue trying to run DOE-2.2 models from the command prompt using the batch processing script. The .inp file is rather large (about 47,000 lines) and I’m hoping to get the simulations to run a little faster by bypassing the eQuest interface. I’d like to thank Ben Brannon and Joe Huang for this thread (http://energy-models.com/forum/run-equest-file-command-line-doe2) which helped me get started.
I’m able to run the doe22.bat script, but I’m getting an error when the script runs DOEBDL. When I open up the BDL file, I get a series of errors in the exterior construction layers which say “Symbol Previously Undefined”, which seem to be in reference to the materials which compose the layers. However, the layers all come directly from the DOE-2 library files.
Is there some reference to the library files I need to establish or have missed? Right now I have the .inp file in C:\doe22, the same directory as the doe22.bat file. I’ve attached the .inp file I’m trying to process, and below are excerpts from my command line and the BDL file generated when I executed the script.
Thanks,
Drew
**** Command Line Screen Shot ****
<image001.png>
***** BDL File Error Text *****
* 235 * "H2Roof Cons Layers" = LAYERS
* 236 * MATERIAL = ( "Blt-Up Roof 3/8in (BR01)", "Polyurethane 1 1/2in",
*ERROR********************************************************** ====================== ******SYMBOL PREVIOUSLY UNDEFINED
* 237 * "Plywd 5/8in (PW04)", "H2Roof Cons Mat 4 (31.52)" )
* 238 * ..
* 1 * $LIBRARY-ENTRY Plywd 5/8in (PW04) MAT Plywood
* 2 * $Plywood, 5/8 Inch
* 3 * TYPE=PROPERTIES TH=0.0521 COND=0.0667 DENS=34.0 S-H=0.29 ..
*ERROR****************************************************************************************
*ERROR*****MATERIAL Layer position number 3 is incomplete or undefined
Drew Morrison, Energy Engineer
Seventhwave
608.210.7151 seventhwave.org<http://seventhwave.org>
<ComplicatedBldg.BDL>
<ComplicatedBldg.inp>
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG<mailto:EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20160205/c1e3e717/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 26057 bytes
Desc: image001.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20160205/c1e3e717/attachment-0002.png>
More information about the Equest-users
mailing list