[Equest-users] Bypass mechanism for energy recovery during mild condition
Lapierre, Patrick
plapierre at bpa.ca
Fri Feb 5 06:04:32 PST 2016
For unoccupied hours, you can simply use a min-outside air schedule forcing your outdoor air ratio to 0 on unoccupied hours.
See the Outside air tab.
[cid:image001.jpg at 01D15FF4.388FEB70]
Patrick Lapierre_ing.
plapierre at bpa.ca
De : Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] De la part de Vishal Jagdale
Envoyé : 5 février 2016 09:02
À : equest-users at lists.onebuilding.org
Objet : [Equest-users] Bypass mechanism for energy recovery during mild condition
Hi,
One of my LEED project received a standard comment as:
Energy recovery is modeled for credit in the Proposed Case. Provide further information regarding the energy recovery efficiency, verify that outside air is modeled with zero flow in both the Baseline and Proposed Case during unoccupied periods when fans are cycled on to meet unoccupied setback temperatures unless health or safety regulations mandate an alternate minimum flow during unoccupied periods (in which case, the unoccupied outside air rates should be modeled identically in the Baseline and Proposed Case), and indicate the bypass mechanism used to bypass the energy recovery during mild conditions.
I need to know,what exactly i need to do in E-quest model.as<http://model.as> per my understanding,i need to Keep Fan operation on by putting the fixed set point temp. control with bypass mechanism.
But how exactly it will consider schedule for unoccupied hours.And how bypass mechanism will serve the purpose during mild condition?
Please guide to resolve this query.
[Inline image 1]
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20160205/2ef2474f/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 1728 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20160205/2ef2474f/attachment-0002.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.png
Type: image/png
Size: 84023 bytes
Desc: image002.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20160205/2ef2474f/attachment-0002.png>
More information about the Equest-users
mailing list