[Equest-users] 4 Pipe FCU- Refrigerant lines (supply and return) instead of CHW lines
Jones, Christopher
Christopher.r.Jones at wspgroup.com
Wed Feb 3 05:19:27 PST 2016
PTAC may not serve your purposes if the project unit ventilators have economizers. PTAC does not include the option for economizer. The PSZ system will work fine in either case – with or without economizer. The DOE22Vol3 – Topics manual mentions using the PSZ system to represent school classroom unit ventilators. See page 225.
[cid:image003.png at 01D09C46.E75BA0D0]
Christopher Jones, P.Eng.
Senior Engineer
WSP Canada Inc.
2300 Yonge Street, Suite 2300
Toronto, ON M4P 1E4
T +1 416-644-4226
F +1 416-487-9766
C +1 416-697-0056
www.wspgroup.com<http://www.wspgroup.com/>
From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Julien Marrec
Sent: Wednesday, February 03, 2016 2:52 AM
To: Jayant Patil
Cc: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] 4 Pipe FCU- Refrigerant lines (supply and return) instead of CHW lines
Hi,
I think you can make do with a hot water PTAC, as long as you specify the performance of the DX cooling based on your outdoor+indoor unit for fan power.
Best,
Julien
Envoyé de mon iPhone
Le 2 févr. 2016 à 21:14, Jayant Patil <jppatil at gmail.com<mailto:jppatil at gmail.com>> a écrit :
Hi,
I am looking to model a custom built up unit ventilator for classroom building. The UV in classroom is basically a 4 pipe FCU system. The HW is supplied by natural gas boiler. Instead of CHW water lines, an outdoor split system (air condenser) is utilized to run the refrigerant (supply and return)lines to the UV.
In e-quest, if FC is used as system type, a CHW loop is required (which is not present in this case). Therefore, for a custom system like this, is it safe to model the air side system as "residential split unit" and HW loop for the heating side? Since the cooling is provided by a split system, I thought a RESYS2 system will be ok?
Has anybody encountered such type of system before to model in e -quest?
Thanks
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG<mailto:EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG>
________________________________
You are receiving this communication because you are listed as a current WSP contact. Should you have any questions regarding WSP’s electronic communications policy, please consult our Anti-Spam Commitment www.wspgroup.com/casl. For any concern or if you believe you should not be receiving this message, please forward this message to us at caslcompliance at wspgroup.com<mailto:caslcompliance at wspgroup.com> so that we can promptly address your request. This message is intended only for the use of the individual or entity to which it is addressed, and may contain information which is privileged, confidential, proprietary or exempt from disclosure under applicable law. If you are not the intended recipient or the person responsible for delivering the message to the intended recipient, you are strictly prohibited from disclosing, distributing, copying or in any way using this message. If you have received this communication in error, please notify the sender, and destroy and delete any copies you may have received.
WSP provides professional land surveying services through the following entities: WSP Surveys (AB) Limited Partnership and WSP Surveys (BC) Limited Partnership
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20160203/27ea93c3/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 6574 bytes
Desc: image001.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20160203/27ea93c3/attachment-0002.png>
More information about the Equest-users
mailing list