[Equest-users] Repost - how to simulate a revolving door
    zhouzarah 
    zarahzhou at hotmail.com
       
    Wed Feb 24 17:11:59 PST 2016
    
    
  
Thanks a lot, Julien! Now it seems to be much simpler with the breakdown method. I appreciate your help!
From: julien.marrec at gmail.com
Date: Wed, 24 Feb 2016 14:26:23 +0100
Subject: Re: [Equest-users] Repost - how to simulate a revolving door
To: zarahzhou at hotmail.com
CC: equest-users at lists.onebuilding.org
Zarah,
If you break it down, here's what a door is:
- Thermal losses through the glass and frame: for that you define a Uvalue for the door
- Infiltration when the door is closed
- Added Infiltration when the door is open
In your case, you could model added infiltration (schedule multiplier) for the 30min shift change.
Best,
Julien
--
Julien Marrec, EBCP, BPI MFBA
Energy&Sustainability Engineer
T: +33 6 95 14 42 13
LinkedIn (en) : www.linkedin.com/in/julienmarrec
LinkedIn (fr) : www.linkedin.com/in/julienmarrec/fr
2016-02-24 5:17 GMT+01:00 zhouzarah <zarahzhou at hotmail.com>:
Dear eQuesters,
Sorry for the repost! I do need your help about this due to time limit. If any one can give a hint, I really appreciate that!
My client requires to do a thermal simulation for a two-story atrium/staircase to check if the cooling system is required for it. The atrium has a revolving door, which revolves once every 30 minutes, and the swing door opens for 30 minutes every 8 hours for shift change. My question is how to simulate the revolving door and swing door in eQuest? I noticed that ASHRAE 90.1-2010 mentioned the infiltration from these two types of doors is 1.0 cfm/ft2 tested at a pressure of at least 1.57 pounds per square foot (psf), but I do not quite understand what this means and how to use this number in my model. If any one has an idea, please give the comments. Thank you so much!Best regards,Zarah  		 	   		  
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send  a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
 		 	   		  
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20160225/b8647e0c/attachment-0005.htm>
    
    
More information about the Equest-users
mailing list