[Equest-users] DOAS+DCV+ERV problems

jacob goodman jacobgoodman22 at gmail.com
Thu Feb 4 06:49:49 PST 2016


Dear Community,
I am working on a model of a 33 story building served by separate VAV 
system for core and perimeter zones. Core zones with VAV terminal units 
and perimeter with fan powered boxes. All areas are served by DOAS via 
the dummy zone/"OA from system" work around. I have added DCV return 
sensor to the non-DOAS systems only. These systems showed appropriate 
savings from this before I added the DOAS and seem ok after as well. The 
problem comes when I add the ERV to the two DOAS systems. I am using ERV 
settings and controls that are well tested and have worked in similar 
models. That is Enthalpy wheel, 56% Sen.&Lat. effectiveness, OA Exhaust 
DT at 5deg, fixed set point controls and 0.5inH2O pressure drop with 
premium fans.

The issues is that as soon as I activate on the ERV the heating energy 
drops by ~90% and cooling/pumps/fans triple or more. This creates 4,000+ 
unmet hours and overall building energy use is up 40%.

It seems like a massive heat load is being added to the system because 
of the ERV, but I cant see why or how. I checked fan kW sizing and that 
does not go up. Neither does supply air flow.

I would work on debugging this for as long as needed, but the deadline 
looms! Attached is the model for reference. Simply turn "Recover 
Exhaust?" to No to see the difference.
Jacob

-------------- next part --------------
INPUT ..


$ ---------------------------------------------------------
$              Abort, Diagnostics
$ ---------------------------------------------------------




$ ---------------------------------------------------------
$              Global Parameters
$ ---------------------------------------------------------



$ ---------------------------------------------------------
$              Title, Run Periods, Design Days, Holidays
$ ---------------------------------------------------------

TITLE           
   LINE-1           = *Comm very large 102815*
   ..

"Entire Year" = RUN-PERIOD-PD
   BEGIN-MONTH      = 1
   BEGIN-DAY        = 1
   BEGIN-YEAR       = 2015
   END-MONTH        = 12
   END-DAY          = 31
   END-YEAR         = 2015
   ..


"Standard US Holidays" = HOLIDAYS        
   LIBRARY-ENTRY "US"
   ..


$ ---------------------------------------------------------
$              Compliance Data
$ ---------------------------------------------------------



$ ---------------------------------------------------------
$              Site and Building Data
$ ---------------------------------------------------------

"Site Data" = SITE-PARAMETERS 
   ALTITUDE         = 15
   ..

"Building Data" = BUILD-PARAMETERS
   HOLIDAYS         = "Standard US Holidays"
   ..



$ ---------------------------------------------------------
$              Materials / Layers / Constructions
$ ---------------------------------------------------------

"EL1 EWall Cons Mat 2 (3)" = MATERIAL        
   TYPE             = RESISTANCE
   RESISTANCE       = 15.5
   ..
"EL1 Roof Cons Mat 4 (2.8)" = MATERIAL        
   TYPE             = RESISTANCE
   RESISTANCE       = 2.8
   ..
"EL1 IWall Cons Mat 2 (0.91)" = MATERIAL        
   TYPE             = RESISTANCE
   RESISTANCE       = 0.91
   ..
"EL1 UFMat (B.S1.U2.M1)" = MATERIAL        
   TYPE             = RESISTANCE
   RESISTANCE       = 100
   ..
"EL1 UWMat (B.S1.U2.M1)" = MATERIAL        
   TYPE             = RESISTANCE
   RESISTANCE       = 0.959175
   ..

"EL1 EWall Cons Layers" = LAYERS          
   MATERIAL         = ( "1/4in Spandrel Glass", "Bldg Paper Felt (BP01)", 
         "EL1 EWall Cons Mat 2 (3)", "GypBd 1/2in (GP01)" )
   ..
"EL1 Roof Cons Layers" = LAYERS          
   MATERIAL         = ( "Blt-Up Roof 3/8in (BR01)", "Polyisocyanurate 2in", 
         "Plywd 5/8in (PW04)", "EL1 Roof Cons Mat 4 (2.8)", 
         "AcousTile 1/2in (AC02)" )
   THICKNESS        = ( &D, 0.355 )
   ..
"EL1 Ceilg Cons Layers" = LAYERS          
   MATERIAL         = ( "AcousTile 1/2in (AC02)" )
   ..
"EL1 IWall Cons Layers" = LAYERS          
   MATERIAL         = ( "GypBd 1/2in (GP01)", "EL1 IWall Cons Mat 2 (0.91)", 
         "GypBd 1/2in (GP01)" )
   ..
"EL1 IFlr Cons Layers" = LAYERS          
   MATERIAL         = ( "Conc HW 140lb 4in (HF-C5)", "Carpet & No Pad" )
   ..
"EL1 UFLyrs (B.S1.U2)" = LAYERS          
   MATERIAL         = ( "EL1 UFMat (B.S1.U2.M1)", "Light Soil, Damp 12in", 
         "Conc HW 140lb 6in (HF-C13)", "Carpet & No Pad" )
   ..
"EL1 UWLyrs (B.S1.U2)" = LAYERS          
   MATERIAL         = ( "EL1 UWMat (B.S1.U2.M1)", "Light Soil, Damp 12in", 
         "Conc HW 140lb 12in (HF-C11)" )
   ..

"EL1 EWall Construction" = CONSTRUCTION    
   TYPE             = LAYERS
   ABSORPTANCE      = 0.6
   ROUGHNESS        = 6
   LAYERS           = "EL1 EWall Cons Layers"
   ..
"EL1 Roof Construction" = CONSTRUCTION    
   TYPE             = LAYERS
   ABSORPTANCE      = 0.3
   ROUGHNESS        = 1
   LAYERS           = "EL1 Roof Cons Layers"
   ..
"EL1 Ceilg Construction" = CONSTRUCTION    
   TYPE             = LAYERS
   LAYERS           = "EL1 Ceilg Cons Layers"
   ..
"EL1 IWall Construction" = CONSTRUCTION    
   TYPE             = LAYERS
   LAYERS           = "EL1 IWall Cons Layers"
   ..
"EL1 IFlr Construction" = CONSTRUCTION    
   TYPE             = LAYERS
   LAYERS           = "EL1 IFlr Cons Layers"
   ..
"EL1 UFCons (B.S1.U2)" = CONSTRUCTION    
   TYPE             = LAYERS
   LAYERS           = "EL1 UFLyrs (B.S1.U2)"
   ..
"EL1 UWCons (B.S1.U2)" = CONSTRUCTION    
   TYPE             = LAYERS
   LAYERS           = "EL1 UWLyrs (B.S1.U2)"
   ..


$ ---------------------------------------------------------
$              Glass Type Codes
$ ---------------------------------------------------------



$ ---------------------------------------------------------
$              Glass Types
$ ---------------------------------------------------------

"EL1 Window Type #1 GT" = GLASS-TYPE      
   TYPE             = SHADING-COEF
   SHADING-COEF     = 0.392
   GLASS-CONDUCT    = 0.19
   VIS-TRANS        = 0.632
   ..
"EL1 Door Type #1 GT" = GLASS-TYPE      
   TYPE             = GLASS-TYPE-CODE
   GLASS-TYPE-CODE  = "1001"
   ..


$ ---------------------------------------------------------
$              Window Layers
$ ---------------------------------------------------------



$ ---------------------------------------------------------
$              Lamps / Luminaries / Lighting Systems
$ ---------------------------------------------------------





$ ---------------------------------------------------------
$              Day Schedules
$ ---------------------------------------------------------

"EL1 Bldg Occup WD" = DAY-SCHEDULE-PD
   TYPE             = FRACTION
   VALUES           = ( 0, &D, &D, &D, &D, &D, 0.099, 0.702, 0.9, &D, &D, 
         0.504, &D, 0.9, &D, &D, 0.702, 0.297, 0.099, &D, &D, &D, 0 )
   ..
"EL1 Bldg Occup WEH" = DAY-SCHEDULE-PD
   TYPE             = FRACTION
   VALUES           = ( 0 )
   ..
"EL1 Bldg InsLt WD" = DAY-SCHEDULE-PD
   TYPE             = FRACTION
   VALUES           = ( 0.05, &D, &D, &D, &D, &D, 0.2965, 0.798, 0.85, &D, &D, 
         &D, &D, &D, &D, &D, 0.798, 0.5005, 0.2965, &D, 0.101, &D, 0.05 )
   ..
"EL1 Bldg InsLt WEH" = DAY-SCHEDULE-PD
   TYPE             = FRACTION
   VALUES           = ( 0.015 )
   ..
"EL1 Bldg InsLt HDD" = DAY-SCHEDULE-PD
   TYPE             = FRACTION
   VALUES           = ( 0 )
   ..
"EL1 Bldg Misc WD" = DAY-SCHEDULE-PD
   TYPE             = FRACTION
   VALUES           = ( 0.2, &D, &D, &D, &D, &D, 0.298, 0.802, 0.85, &D, &D, 
         &D, &D, &D, &D, &D, &D, 0.501, 0.298, &D, 0.2 )
   ..
"EL1 Bldg Misc WEH" = DAY-SCHEDULE-PD
   TYPE             = FRACTION
   VALUES           = ( 0.1 )
   ..
"EL1 Bldg Misc HDD" = DAY-SCHEDULE-PD
   TYPE             = FRACTION
   VALUES           = ( 0 )
   ..
"EL1 Bldg Proc WD" = DAY-SCHEDULE-PD
   TYPE             = FRACTION
   VALUES           = ( 0.25, &D, &D, &D, &D, &D, 0.45, &D, &D, &D, &D, &D, 
         &D, &D, &D, &D, &D, &D, 0.25 )
   ..
"EL1 Bldg Proc WEH" = DAY-SCHEDULE-PD
   TYPE             = FRACTION
   VALUES           = ( 0.039 )
   ..
"EL1 Bldg Proc HDD" = DAY-SCHEDULE-PD
   TYPE             = FRACTION
   VALUES           = ( 0 )
   ..
"DHW Eqp NRes WD" = DAY-SCHEDULE-PD
   TYPE             = FRACTION
   VALUES           = ( 0.05, &D, &D, &D, &D, &D, 0.101, 0.5005, &D, 0.9, &D, 
         &D, &D, &D, &D, 0.696, 0.5005, 0.2965, 0.203, &D, &D, 0.05 )
   ..
"DHW Eqp NRes WEH" = DAY-SCHEDULE-PD
   TYPE             = FRACTION
   VALUES           = ( 0.015 )
   ..
"DHW Eqp NRes HDD" = DAY-SCHEDULE-PD
   TYPE             = FRACTION
   VALUES           = ( 0 )
   ..
"ZG0-S1 (FC) P-Inf WD" = DAY-SCHEDULE-PD
   TYPE             = MULTIPLIER
   VALUES           = ( 1, &D, &D, &D, &D, 1.049, 1.25, &D, 0.944, 0.5, 1.25, 
         &D, &D, &D, 0.5, 0.944, 1.25, &D, 1.148, 1, &D, 1.049, &D, 1 )
   ..
"ZG0-S1 (FC) P-Inf WEH" = DAY-SCHEDULE-PD
   TYPE             = MULTIPLIER
   VALUES           = ( 1 )
   ..
"ZG0-S1 (FC) P-Inf HDD" = DAY-SCHEDULE-PD
   TYPE             = MULTIPLIER
   VALUES           = ( 1, &D, &D, &D, &D, &D, &D, 0.5, &D, &D, &D, &D, &D, 
         &D, &D, &D, &D, &D, 1 )
   ..
"ZG0-S1 (FC) C-Inf WD" = DAY-SCHEDULE-PD
   TYPE             = FRACTION
   VALUES           = ( 1, &D, &D, &D, &D, &D, &D, 0.5, &D, &D, &D, &D, &D, 
         &D, &D, &D, &D, &D, 1 )
   ..
"ZG0-S1 (FC) C-Inf WEH" = DAY-SCHEDULE-PD
   TYPE             = FRACTION
   VALUES           = ( 1 )
   ..
"S1 Sys1 (FC) Fan WD" = DAY-SCHEDULE-PD
   TYPE             = ON/OFF/FLAG
   VALUES           = ( 0, &D, &D, &D, &D, &D, &D, 1, &D, &D, &D, &D, &D, &D, 
         &D, &D, &D, &D, 0 )
   ..
"S1 Sys1 (FC) Fan WEH" = DAY-SCHEDULE-PD
   TYPE             = ON/OFF/FLAG
   VALUES           = ( 0 )
   ..
"S1 Sys1 (FC) MinOA WD" = DAY-SCHEDULE-PD
   TYPE             = FRAC/DESIGN
   VALUES           = ( 0, &D, &D, &D, &D, &D, &D, -999, &D, &D, &D, &D, &D, 
         &D, &D, &D, &D, &D, 0 )
   ..
"S1 Sys1 (FC) MinOA WEH" = DAY-SCHEDULE-PD
   TYPE             = FRAC/DESIGN
   VALUES           = ( 0 )
   ..
"S1 Sys1 (FC) Cool WD" = DAY-SCHEDULE-PD
   TYPE             = TEMPERATURE
   VALUES           = ( 82, &D, &D, &D, &D, &D, &D, 76, &D, &D, &D, &D, &D, 
         &D, &D, &D, &D, &D, 82 )
   ..
"S1 Sys1 (FC) Cool WEH" = DAY-SCHEDULE-PD
   TYPE             = TEMPERATURE
   VALUES           = ( 82 )
   ..
"S1 Sys1 (FC) Heat WD" = DAY-SCHEDULE-PD
   TYPE             = TEMPERATURE
   VALUES           = ( 68, &D, &D, &D, &D, &D, &D, 72, &D, &D, &D, &D, &D, 
         &D, &D, &D, &D, &D, 68 )
   ..
"S1 Sys1 (FC) Heat WEH" = DAY-SCHEDULE-PD
   TYPE             = TEMPERATURE
   VALUES           = ( 68 )
   ..
"Day Schedule RESET-TEMP CLG" = DAY-SCHEDULE-PD
   TYPE             = RESET-TEMP
   OUTSIDE-HI       = 80
   OUTSIDE-LO       = 60
   SUPPLY-HI        = 54
   SUPPLY-LO        = 44
   ..
"Schedule RESET-TEMP HTG WD" = DAY-SCHEDULE-PD
   TYPE             = RESET-TEMP
   OUTSIDE-HI       = 50
   OUTSIDE-LO       = 20
   SUPPLY-HI        = 125
   SUPPLY-LO        = 100
   ..
"SAR Day" = DAY-SCHEDULE-PD
   TYPE             = RESET-TEMP
   OUTSIDE-HI       = 80
   OUTSIDE-LO       = 60
   SUPPLY-HI        = 54
   SUPPLY-LO        = 44
   ..

$ ---------------------------------------------------------
$              Week Schedules
$ ---------------------------------------------------------

"EL1 Bldg Occup Wk" = WEEK-SCHEDULE-PD
   TYPE             = FRACTION
   DAY-SCHEDULES    = ( "EL1 Bldg Occup WD", &D, &D, &D, &D, 
         "EL1 Bldg Occup WEH", &D, &D, "EL1 Bldg Occup WEH" )
   ..
"EL1 Bldg InsLt Wk" = WEEK-SCHEDULE-PD
   TYPE             = FRACTION
   DAY-SCHEDULES    = ( "EL1 Bldg InsLt WD", &D, &D, &D, &D, 
         "EL1 Bldg InsLt WEH", &D, &D, "EL1 Bldg InsLt HDD" )
   ..
"EL1 Bldg Misc Wk" = WEEK-SCHEDULE-PD
   TYPE             = FRACTION
   DAY-SCHEDULES    = ( "EL1 Bldg Misc WD", &D, &D, &D, &D, 
         "EL1 Bldg Misc WEH", &D, &D, "EL1 Bldg Misc HDD" )
   ..
"EL1 Bldg Proc Wk" = WEEK-SCHEDULE-PD
   TYPE             = FRACTION
   DAY-SCHEDULES    = ( "EL1 Bldg Proc WD" )
   ..
"DHW Eqp NRes Wk" = WEEK-SCHEDULE-PD
   TYPE             = FRACTION
   DAY-SCHEDULES    = ( "DHW Eqp NRes WD", &D, &D, &D, &D, "DHW Eqp NRes WEH", 
         &D, &D, "DHW Eqp NRes HDD" )
   ..
"ZG0-S1 (FC) P-Inf Wk" = WEEK-SCHEDULE-PD
   TYPE             = MULTIPLIER
   DAY-SCHEDULES    = ( "ZG0-S1 (FC) P-Inf WD", &D, &D, &D, &D, 
         "ZG0-S1 (FC) P-Inf WEH", &D, &D, "ZG0-S1 (FC) P-Inf HDD" )
   ..
"ZG0-S1 (FC) C-Inf Wk" = WEEK-SCHEDULE-PD
   TYPE             = FRACTION
   DAY-SCHEDULES    = ( "ZG0-S1 (FC) C-Inf WD", &D, &D, &D, &D, 
         "ZG0-S1 (FC) C-Inf WEH" )
   ..
"S1 Sys1 (FC) Fan Wk" = WEEK-SCHEDULE-PD
   TYPE             = ON/OFF/FLAG
   DAY-SCHEDULES    = ( "S1 Sys1 (FC) Fan WD", &D, &D, &D, &D, 
         "S1 Sys1 (FC) Fan WEH" )
   ..
"S1 Sys1 (FC) MinOA Wk" = WEEK-SCHEDULE-PD
   TYPE             = FRAC/DESIGN
   DAY-SCHEDULES    = ( "S1 Sys1 (FC) MinOA WD", &D, &D, &D, &D, 
         "S1 Sys1 (FC) MinOA WEH" )
   ..
"S1 Sys1 (FC) Cool Wk" = WEEK-SCHEDULE-PD
   TYPE             = TEMPERATURE
   DAY-SCHEDULES    = ( "S1 Sys1 (FC) Cool WD", &D, &D, &D, &D, 
         "S1 Sys1 (FC) Cool WEH" )
   ..
"S1 Sys1 (FC) Heat Wk" = WEEK-SCHEDULE-PD
   TYPE             = TEMPERATURE
   DAY-SCHEDULES    = ( "S1 Sys1 (FC) Heat WD", &D, &D, &D, &D, 
         "S1 Sys1 (FC) Heat WEH" )
   ..
"Week Schedule RESET-TEMP CLG" = WEEK-SCHEDULE-PD
   TYPE             = RESET-TEMP
   DAY-SCHEDULES    = ( "Day Schedule RESET-TEMP CLG" )
   ..
"Schedule RESET-TEMP HTG Wk" = WEEK-SCHEDULE-PD
   TYPE             = RESET-TEMP
   DAY-SCHEDULES    = ( "Schedule RESET-TEMP HTG WD" )
   ..
"SAR Wk" = WEEK-SCHEDULE-PD
   TYPE             = RESET-TEMP
   DAY-SCHEDULES    = ( "SAR Day" )
   ..

$ ---------------------------------------------------------
$              Annual Schedules
$ ---------------------------------------------------------

"EL1 Bldg Occup Sch" = SCHEDULE-PD
   TYPE             = FRACTION
   MONTH            = ( 12 )
   DAY              = ( 31 )
   WEEK-SCHEDULES   = ( "EL1 Bldg Occup Wk" )
   ..
"EL1 Bldg InsLt Sch" = SCHEDULE-PD
   TYPE             = FRACTION
   MONTH            = ( 12 )
   DAY              = ( 31 )
   WEEK-SCHEDULES   = ( "EL1 Bldg InsLt Wk" )
   ..
"EL1 Bldg Misc Sch" = SCHEDULE-PD
   TYPE             = FRACTION
   MONTH            = ( 12 )
   DAY              = ( 31 )
   WEEK-SCHEDULES   = ( "EL1 Bldg Misc Wk" )
   ..
"Procedd Load Sch" = SCHEDULE-PD
   TYPE             = FRACTION
   MONTH            = ( 12 )
   DAY              = ( 31 )
   WEEK-SCHEDULES   = ( "EL1 Bldg Proc Wk" )
   ..
"DHW Eqp NRes Sch" = SCHEDULE-PD
   TYPE             = FRACTION
   MONTH            = ( 12 )
   DAY              = ( 31 )
   WEEK-SCHEDULES   = ( "DHW Eqp NRes Wk" )
   ..
"ZG0-S1 (FC) P-Inf Sch" = SCHEDULE-PD
   TYPE             = MULTIPLIER
   MONTH            = ( 12 )
   DAY              = ( 31 )
   WEEK-SCHEDULES   = ( "ZG0-S1 (FC) P-Inf Wk" )
   ..
"ZG0-S1 (FC) C-Inf Sch" = SCHEDULE-PD
   TYPE             = FRACTION
   MONTH            = ( 12 )
   DAY              = ( 31 )
   WEEK-SCHEDULES   = ( "ZG0-S1 (FC) C-Inf Wk" )
   ..
"S1 Sys1 (FC) Fan Sch" = SCHEDULE-PD
   TYPE             = ON/OFF/FLAG
   MONTH            = ( 12 )
   DAY              = ( 31 )
   WEEK-SCHEDULES   = ( "S1 Sys1 (FC) Fan Wk" )
   ..
"S1 Sys1 (FC) MinOA Sch" = SCHEDULE-PD
   TYPE             = FRAC/DESIGN
   MONTH            = ( 12 )
   DAY              = ( 31 )
   WEEK-SCHEDULES   = ( "S1 Sys1 (FC) MinOA Wk" )
   ..
"S1 Sys1 (FC) Cool Sch" = SCHEDULE-PD
   TYPE             = TEMPERATURE
   MONTH            = ( 12 )
   DAY              = ( 31 )
   WEEK-SCHEDULES   = ( "S1 Sys1 (FC) Cool Wk" )
   ..
"S1 Sys1 (FC) Heat Sch" = SCHEDULE-PD
   TYPE             = TEMPERATURE
   MONTH            = ( 12 )
   DAY              = ( 31 )
   WEEK-SCHEDULES   = ( "S1 Sys1 (FC) Heat Wk" )
   ..
"OFFICE ELEV" = SCHEDULE-PD
   LIBRARY-ENTRY "OFFICE ELEV"
   ..
"Schedule RESET-TEMP CLG" = SCHEDULE-PD
   TYPE             = RESET-TEMP
   MONTH            = ( 12 )
   DAY              = ( 31 )
   WEEK-SCHEDULES   = ( "Week Schedule RESET-TEMP CLG" )
   ..
"Schedule RESET-TEMP HTG" = SCHEDULE-PD
   TYPE             = RESET-TEMP
   MONTH            = ( 12 )
   DAY              = ( 31 )
   WEEK-SCHEDULES   = ( "Schedule RESET-TEMP HTG Wk" )
   ..
"Supply Air Reset Sch" = SCHEDULE-PD
   TYPE             = RESET-TEMP
   MONTH            = ( 12 )
   DAY              = ( 31 )
   WEEK-SCHEDULES   = ( "SAR Wk" )
   ..


$ ---------------------------------------------------------
$              Polygons
$ ---------------------------------------------------------

"EL1 Floor Polygon" = POLYGON         
   V1               = ( 0, 0 )
   V2               = ( 184, 0 )
   V3               = ( 184, 127.38 )
   V4               = ( 0, 127.38 )
   ..
"EL1 Space Polygon 1" = POLYGON         
   V1               = ( 0, 0 )
   V2               = ( 184, 0 )
   V3               = ( 169, 15 )
   V4               = ( 15, 15 )
   ..
"EL1 Space Polygon 2" = POLYGON         
   V1               = ( 0, 0 )
   V2               = ( 127.38, -0 )
   V3               = ( 112.38, 15 )
   V4               = ( 15, 15 )
   ..
"EL1 Space Polygon 3" = POLYGON         
   V1               = ( 0, 0 )
   V2               = ( 184, 0 )
   V3               = ( 169, 15 )
   V4               = ( 15, 15 )
   ..
"EL1 Space Polygon 4" = POLYGON         
   V1               = ( 0, 0 )
   V2               = ( 127.38, 0 )
   V3               = ( 112.38, 15 )
   V4               = ( 15, 15 )
   ..
"EL1 Space Polygon 5" = POLYGON         
   V1               = ( 0, 0 )
   V2               = ( 154, 0 )
   V3               = ( 154, 97.38 )
   V4               = ( 0, 97.38 )
   ..
"EL1 Space Polygon 1 - SMirro" = POLYGON         
   V1               = ( 0, 0 )
   V2               = ( 15, 15 )
   V3               = ( 15, 169 )
   V4               = ( 0, 184 )
   ..
"EL1 Space Polygon 2 - SMirro" = POLYGON         
   V1               = ( 0, 0 )
   V2               = ( 15, 15 )
   V3               = ( 15, 112.38 )
   V4               = ( -0, 127.38 )
   ..
"EL1 Space Polygon 5 - SMirro" = POLYGON         
   V1               = ( 0, 0 )
   V2               = ( 97.38, 0 )
   V3               = ( 97.38, 154 )
   V4               = ( 0, 154 )
   ..


$ ---------------------------------------------------------
$              Wall Parameters
$ ---------------------------------------------------------



$ ---------------------------------------------------------
$              Fixed and Building Shades
$ ---------------------------------------------------------




$ ---------------------------------------------------------
$              Misc Cost Related Objects
$ ---------------------------------------------------------



"Baseline Data" = BASELINE        
   ..


$ *********************************************************
$ **                                                     **
$ **      Floors / Spaces / Walls / Windows / Doors      **
$ **                                                     **
$ *********************************************************

"EL1 Below-Grade Flr" = FLOOR           
   Z                = -9
   AZIMUTH          = 360
   POLYGON          = "EL1 Floor Polygon"
   SHAPE            = POLYGON
   FLOOR-HEIGHT     = 9
   SPACE-HEIGHT     = 9
   C-DIAGRAM-DATA   = *Bldg Envelope & Loads 1 Diag Data*
   ..
"EL1 South Perim Spc (B.S1)" = SPACE           
   SHAPE            = POLYGON
   ZONE-TYPE        = CONDITIONED
   PEOPLE-SCHEDULE  = "EL1 Bldg Occup Sch"
   LIGHTING-SCHEDUL = ( "EL1 Bldg InsLt Sch" )
   EQUIP-SCHEDULE   = ( "EL1 Bldg Misc Sch", "Procedd Load Sch", &D, 
         "Procedd Load Sch", "Procedd Load Sch" )
   PEOPLE-HG-LAT    = 201.518
   PEOPLE-HG-SENS   = 248.971
   EQUIP-LATENT     = ( 0, 0, 0, 0, 0 )
   EQUIP-SENSIBLE   = ( 1, 1, 1, 1, 0 )
   LIGHTING-W/AREA  = ( 0.675 )
   EQUIPMENT-W/AREA = ( 1.05, 0, 0, 0, 0 )
   AREA/PERSON      = 193.477
   POLYGON          = "EL1 Space Polygon 1"
   LOCATION         = FLOOR-V1
   C-SUB-SRC-BTUH   = ( 0, 0, 0 )
   C-SUB-SRC-KW     = ( 0, 0, 0.2991 )
   C-ACTIVITY-DESC  = *Office (Open Plan) (60%)*
   ..
"EL1 NE Wall (B.S1.I1)" = INTERIOR-WALL   
   NEXT-TO          = "EL1 East Perim Spc (B.E2)"
   CONSTRUCTION     = "EL1 IWall Construction"
   LOCATION         = SPACE-V2
   ..
"EL1 North Wall (B.S1.I2)" = INTERIOR-WALL   
   NEXT-TO          = "EL1 Core Spc (B.C5)"
   CONSTRUCTION     = "EL1 IWall Construction"
   LOCATION         = SPACE-V3
   ..
"EL1 NW Wall (B.S1.I3)" = INTERIOR-WALL   
   NEXT-TO          = "EL1 West Perim Spc (B.W4)"
   CONSTRUCTION     = "EL1 IWall Construction"
   LOCATION         = SPACE-V4
   ..
"EL1 Ceiling (B.S1.I4)" = INTERIOR-WALL   
   NEXT-TO          = "EL1 South Perim Spc (G.S6)"
   CONSTRUCTION     = "EL1 Ceilg Construction"
   LOCATION         = TOP
   ..
"EL1 Flr (B.S1.U1)" = UNDERGROUND-WALL
   CONSTRUCTION     = "EL1 UFCons (B.S1.U2)"
   LOCATION         = BOTTOM
   ..
"EL1 South Wall (B.S1.U2)" = UNDERGROUND-WALL
   CONSTRUCTION     = "EL1 UWCons (B.S1.U2)"
   LOCATION         = SPACE-V1
   ..
"EL1 East Perim Spc (B.E2)" = SPACE           
   SHAPE            = POLYGON
   ZONE-TYPE        = CONDITIONED
   PEOPLE-SCHEDULE  = "EL1 Bldg Occup Sch"
   LIGHTING-SCHEDUL = ( "EL1 Bldg InsLt Sch" )
   EQUIP-SCHEDULE   = ( "EL1 Bldg Misc Sch", "Procedd Load Sch", 
         "Procedd Load Sch", "Procedd Load Sch", "Procedd Load Sch" )
   PEOPLE-HG-LAT    = 201.518
   PEOPLE-HG-SENS   = 248.971
   EQUIP-LATENT     = ( 0, 0, 0, 0, 0 )
   EQUIP-SENSIBLE   = ( 1, 1, 1, 1, 0 )
   LIGHTING-W/AREA  = ( 0.68 )
   EQUIPMENT-W/AREA = ( 1.05, 0, 0, 0, 0 )
   AREA/PERSON      = 193.477
   POLYGON          = "EL1 Space Polygon 2"
   LOCATION         = FLOOR-V2
   C-SUB-SRC-BTUH   = ( 0, 0, 0 )
   C-SUB-SRC-KW     = ( 0, 0, 0.2991 )
   C-ACTIVITY-DESC  = *Office (Open Plan) (60%)*
   ..
"EL1 NW Wall (B.E2.I5)" = INTERIOR-WALL   
   NEXT-TO          = "EL1 North Perim Spc (B.N3)"
   CONSTRUCTION     = "EL1 IWall Construction"
   LOCATION         = SPACE-V2
   ..
"EL1 West Wall (B.E2.I6)" = INTERIOR-WALL   
   NEXT-TO          = "EL1 Core Spc (B.C5)"
   CONSTRUCTION     = "EL1 IWall Construction"
   LOCATION         = SPACE-V3
   ..
"EL1 Ceiling (B.E2.I7)" = INTERIOR-WALL   
   NEXT-TO          = "EL1 East Perim Spc (G.E7)"
   CONSTRUCTION     = "EL1 Ceilg Construction"
   LOCATION         = TOP
   ..
"EL1 Flr (B.E2.U3)" = UNDERGROUND-WALL
   CONSTRUCTION     = "EL1 UFCons (B.S1.U2)"
   LOCATION         = BOTTOM
   ..
"EL1 East Wall (B.E2.U4)" = UNDERGROUND-WALL
   CONSTRUCTION     = "EL1 UWCons (B.S1.U2)"
   LOCATION         = SPACE-V1
   ..
"EL1 North Perim Spc (B.N3)" = SPACE           
   SHAPE            = POLYGON
   ZONE-TYPE        = CONDITIONED
   PEOPLE-SCHEDULE  = "EL1 Bldg Occup Sch"
   LIGHTING-SCHEDUL = ( "EL1 Bldg InsLt Sch" )
   EQUIP-SCHEDULE   = ( "EL1 Bldg Misc Sch", "Procedd Load Sch", 
         "Procedd Load Sch", "Procedd Load Sch", "Procedd Load Sch" )
   PEOPLE-HG-LAT    = 201.518
   PEOPLE-HG-SENS   = 248.971
   EQUIP-LATENT     = ( 0, 0, 0, 0, 0 )
   EQUIP-SENSIBLE   = ( 1, 1, 1, 1, 0 )
   LIGHTING-W/AREA  = ( 0.68 )
   EQUIPMENT-W/AREA = ( 1.05, 0, 0, 0, 0 )
   AREA/PERSON      = 193.477
   POLYGON          = "EL1 Space Polygon 3"
   LOCATION         = FLOOR-V3
   C-SUB-SRC-BTUH   = ( 0, 0, 0 )
   C-SUB-SRC-KW     = ( 0, 0, 0.2991 )
   C-ACTIVITY-DESC  = *Office (Open Plan) (60%)*
   ..
"EL1 SW Wall (B.N3.I8)" = INTERIOR-WALL   
   NEXT-TO          = "EL1 West Perim Spc (B.W4)"
   CONSTRUCTION     = "EL1 IWall Construction"
   LOCATION         = SPACE-V2
   ..
"EL1 South Wall (B.N3.I9)" = INTERIOR-WALL   
   NEXT-TO          = "EL1 Core Spc (B.C5)"
   CONSTRUCTION     = "EL1 IWall Construction"
   LOCATION         = SPACE-V3
   ..
"EL1 Ceiling (B.N3.I10)" = INTERIOR-WALL   
   NEXT-TO          = "EL1 North Perim Spc (G.N8)"
   CONSTRUCTION     = "EL1 Ceilg Construction"
   LOCATION         = TOP
   ..
"EL1 Flr (B.N3.U5)" = UNDERGROUND-WALL
   CONSTRUCTION     = "EL1 UFCons (B.S1.U2)"
   LOCATION         = BOTTOM
   ..
"EL1 North Wall (B.N3.U6)" = UNDERGROUND-WALL
   CONSTRUCTION     = "EL1 UWCons (B.S1.U2)"
   LOCATION         = SPACE-V1
   ..
"EL1 West Perim Spc (B.W4)" = SPACE           
   SHAPE            = POLYGON
   ZONE-TYPE        = CONDITIONED
   PEOPLE-SCHEDULE  = "EL1 Bldg Occup Sch"
   LIGHTING-SCHEDUL = ( "EL1 Bldg InsLt Sch" )
   EQUIP-SCHEDULE   = ( "EL1 Bldg Misc Sch", "Procedd Load Sch", 
         "Procedd Load Sch", "Procedd Load Sch", "Procedd Load Sch" )
   PEOPLE-HG-LAT    = 201.518
   PEOPLE-HG-SENS   = 248.971
   EQUIP-LATENT     = ( 0, 0, 0, 0, 0 )
   EQUIP-SENSIBLE   = ( 1, 1, 1, 1, 0 )
   LIGHTING-W/AREA  = ( 0.68 )
   EQUIPMENT-W/AREA = ( 1.05, 0, 0, 0, 0 )
   AREA/PERSON      = 193.477
   POLYGON          = "EL1 Space Polygon 4"
   LOCATION         = FLOOR-V4
   C-SUB-SRC-BTUH   = ( 0, 0, 0 )
   C-SUB-SRC-KW     = ( 0, 0, 0.2991 )
   C-ACTIVITY-DESC  = *Office (Open Plan) (60%)*
   ..
"EL1 East Wall (B.W4.I11)" = INTERIOR-WALL   
   NEXT-TO          = "EL1 Core Spc (B.C5)"
   CONSTRUCTION     = "EL1 IWall Construction"
   LOCATION         = SPACE-V3
   ..
"EL1 Ceiling (B.W4.I12)" = INTERIOR-WALL   
   NEXT-TO          = "EL1 West Perim Spc (G.W9)"
   CONSTRUCTION     = "EL1 Ceilg Construction"
   LOCATION         = TOP
   ..
"EL1 Flr (B.W4.U7)" = UNDERGROUND-WALL
   CONSTRUCTION     = "EL1 UFCons (B.S1.U2)"
   LOCATION         = BOTTOM
   ..
"EL1 West Wall (B.W4.U8)" = UNDERGROUND-WALL
   CONSTRUCTION     = "EL1 UWCons (B.S1.U2)"
   LOCATION         = SPACE-V1
   ..
"EL1 Core Spc (B.C5)" = SPACE           
   X                = 15
   Y                = 15
   SHAPE            = POLYGON
   ZONE-TYPE        = CONDITIONED
   PEOPLE-SCHEDULE  = "EL1 Bldg Occup Sch"
   LIGHTING-SCHEDUL = ( "EL1 Bldg InsLt Sch" )
   EQUIP-SCHEDULE   = ( "EL1 Bldg Misc Sch", "Procedd Load Sch", 
         "Procedd Load Sch", "Procedd Load Sch" )
   PEOPLE-HG-LAT    = 201.518
   PEOPLE-HG-SENS   = 248.971
   EQUIP-LATENT     = ( 0, 0, 0, 0, 0 )
   EQUIP-SENSIBLE   = ( 1, 1, 1, 1, 0 )
   LIGHTING-W/AREA  = ( 0.68 )
   EQUIPMENT-W/AREA = ( 1.05, 0, 0, 0, 0 )
   AREA/PERSON      = 193.477
   POLYGON          = "EL1 Space Polygon 5"
   C-SUB-SRC-BTUH   = ( 0, 0, 0 )
   C-SUB-SRC-KW     = ( 0, 0, 0.2991 )
   C-ACTIVITY-DESC  = *Office (Open Plan) (60%)*
   ..
"EL1 Ceiling (B.C5.I13)" = INTERIOR-WALL   
   NEXT-TO          = "EL1 Core Spc (G.C10)"
   CONSTRUCTION     = "EL1 Ceilg Construction"
   LOCATION         = TOP
   ..
"EL1 Flr (B.C5.U9)" = UNDERGROUND-WALL
   CONSTRUCTION     = "EL1 UFCons (B.S1.U2)"
   LOCATION         = BOTTOM
   ..
"Dummy Upper Stack" = SPACE           
   SHAPE            = BOX
   WIDTH            = 1
   DEPTH            = 1
   ..
"Dummy Lower Stack" = SPACE           
   SHAPE            = BOX
   WIDTH            = 1
   DEPTH            = 1
   ..
"EL1 Ground Flr" = FLOOR           
   AZIMUTH          = 360
   POLYGON          = "EL1 Floor Polygon"
   SHAPE            = POLYGON
   FLOOR-HEIGHT     = 9
   SPACE-HEIGHT     = 9
   C-DIAGRAM-DATA   = *Bldg Envelope & Loads 1 Diag Data*
   ..
"EL1 South Perim Spc (G.S6)" = SPACE           
   SHAPE            = POLYGON
   ZONE-TYPE        = CONDITIONED
   PEOPLE-SCHEDULE  = "EL1 Bldg Occup Sch"
   LIGHTING-SCHEDUL = ( "EL1 Bldg InsLt Sch" )
   EQUIP-SCHEDULE   = ( "EL1 Bldg Misc Sch", "Procedd Load Sch" )
   INF-SCHEDULE     = "ZG0-S1 (FC) P-Inf Sch"
   INF-METHOD       = AIR-CHANGE
   INF-FLOW/AREA    = 0.027
   PEOPLE-HG-LAT    = 250
   PEOPLE-HG-SENS   = 250
   EQUIP-LATENT     = ( 0 )
   EQUIP-SENSIBLE   = ( 1 )
   LIGHTING-W/AREA  = ( 0.68 )
   EQUIPMENT-W/AREA = ( 1.05, 0 )
   DAYLIGHTING      = YES
   LIGHT-REF-POINT1 = ( 65, 5 )
   AREA/PERSON      = 100
   POLYGON          = "EL1 Space Polygon 1"
   LOCATION         = FLOOR-V1
   C-SUB-SRC-BTUH   = ( 0, 0, 0 )
   C-SUB-SRC-KW     = ( 0, 0, 0 )
   C-ACTIVITY-DESC  = *Lobby (Reception/Waiting)*
   ..
"EL1 South Wall (G.S6.E1)" = EXTERIOR-WALL   
   CONSTRUCTION     = "EL1 EWall Construction"
   LOCATION         = SPACE-V1
   ..
"EL1 South Win (G.S6.E1.W1)" = WINDOW          
   GLASS-TYPE       = "EL1 Window Type #1 GT"
   FRAME-WIDTH      = 1
   X                = 14.375
   Y                = 0.5
   HEIGHT           = 8
   WIDTH            = 71.9583
   FRAME-CONDUCT    = 2.781
   ..
"EL1 South Win (G.S6.E1.W2)" = WINDOW          
   GLASS-TYPE       = "EL1 Window Type #1 GT"
   FRAME-WIDTH      = 1
   X                = 97.6667
   Y                = 0.5
   HEIGHT           = 8
   WIDTH            = 71.9583
   FRAME-CONDUCT    = 2.781
   ..
"EL1 South Door (G.S6.E1.D1)" = WINDOW          
   GLASS-TYPE       = "EL1 Door Type #1 GT"
   FRAME-WIDTH      = 1
   X                = 89.25
   Y                = 0.25
   HEIGHT           = 6.5
   WIDTH            = 5.5
   FRAME-CONDUCT    = 3.079
   ..
"EL1 Flr (G.S6.I14)" = INTERIOR-WALL   
   NEXT-TO          = "EL1 South Perim Spc (B.S1)"
   CONSTRUCTION     = "EL1 IFlr Construction"
   LOCATION         = BOTTOM
   ..
"EL1 NE Wall (G.S6.I15)" = INTERIOR-WALL   
   NEXT-TO          = "EL1 East Perim Spc (G.E7)"
   CONSTRUCTION     = "EL1 IWall Construction"
   LOCATION         = SPACE-V2
   ..
"EL1 North Wall (G.S6.I16)" = INTERIOR-WALL   
   NEXT-TO          = "EL1 Core Spc (G.C10)"
   CONSTRUCTION     = "EL1 IWall Construction"
   LOCATION         = SPACE-V3
   ..
"EL1 NW Wall (G.S6.I17)" = INTERIOR-WALL   
   NEXT-TO          = "EL1 West Perim Spc (G.W9)"
   CONSTRUCTION     = "EL1 IWall Construction"
   LOCATION         = SPACE-V4
   ..
"EL1 Ceiling (G.S6.I18)" = INTERIOR-WALL   
   NEXT-TO          = "EL1 South Perim Spc (M.S11)"
   CONSTRUCTION     = "EL1 Ceilg Construction"
   LOCATION         = TOP
   ..
"EL1 East Perim Spc (G.E7)" = SPACE           
   SHAPE            = POLYGON
   ZONE-TYPE        = CONDITIONED
   PEOPLE-SCHEDULE  = "EL1 Bldg Occup Sch"
   LIGHTING-SCHEDUL = ( "EL1 Bldg InsLt Sch" )
   EQUIP-SCHEDULE   = ( "EL1 Bldg Misc Sch", "Procedd Load Sch" )
   INF-SCHEDULE     = "ZG0-S1 (FC) P-Inf Sch"
   INF-METHOD       = AIR-CHANGE
   INF-FLOW/AREA    = 0.027
   PEOPLE-HG-LAT    = 250
   PEOPLE-HG-SENS   = 250
   EQUIP-LATENT     = ( 0 )
   EQUIP-SENSIBLE   = ( 1 )
   LIGHTING-W/AREA  = ( 0.68 )
   EQUIPMENT-W/AREA = ( 1.05, 0 )
   DAYLIGHTING      = YES
   LIGHT-REF-POINT1 = ( 65, 5 )
   AREA/PERSON      = 100
   POLYGON          = "EL1 Space Polygon 2"
   LOCATION         = FLOOR-V2
   C-SUB-SRC-BTUH   = ( 0, 0, 0 )
   C-SUB-SRC-KW     = ( 0, 0, 0 )
   C-ACTIVITY-DESC  = *Lobby (Reception/Waiting)*
   ..
"EL1 East Wall (G.E7.E2)" = EXTERIOR-WALL   
   CONSTRUCTION     = "EL1 EWall Construction"
   LOCATION         = SPACE-V1
   ..
"EL1 East Win (G.E7.E2.W1)" = WINDOW          
   GLASS-TYPE       = "EL1 Window Type #1 GT"
   FRAME-WIDTH      = 1
   X                = 9.95156
   Y                = 0.5
   HEIGHT           = 8
   WIDTH            = 48.0718
   FRAME-CONDUCT    = 2.781
   ..
"EL1 East Win (G.E7.E2.W2)" = WINDOW          
   GLASS-TYPE       = "EL1 Window Type #1 GT"
   FRAME-WIDTH      = 1
   X                = 69.3567
   Y                = 0.5
   HEIGHT           = 8
   WIDTH            = 48.0718
   FRAME-CONDUCT    = 2.781
   ..
"EL1 East Door (G.E7.E2.D1)" = WINDOW          
   GLASS-TYPE       = "EL1 Door Type #1 GT"
   FRAME-WIDTH      = 1
   X                = 60.94
   Y                = 0.25
   HEIGHT           = 6.5
   WIDTH            = 5.5
   FRAME-CONDUCT    = 3.079
   ..
"EL1 Flr (G.E7.I19)" = INTERIOR-WALL   
   NEXT-TO          = "EL1 East Perim Spc (B.E2)"
   CONSTRUCTION     = "EL1 IFlr Construction"
   LOCATION         = BOTTOM
   ..
"EL1 NW Wall (G.E7.I20)" = INTERIOR-WALL   
   NEXT-TO          = "EL1 North Perim Spc (G.N8)"
   CONSTRUCTION     = "EL1 IWall Construction"
   LOCATION         = SPACE-V2
   ..
"EL1 West Wall (G.E7.I21)" = INTERIOR-WALL   
   NEXT-TO          = "EL1 Core Spc (G.C10)"
   CONSTRUCTION     = "EL1 IWall Construction"
   LOCATION         = SPACE-V3
   ..
"EL1 Ceiling (G.E7.I22)" = INTERIOR-WALL   
   NEXT-TO          = "EL1 East Perim Spc (M.E12)"
   CONSTRUCTION     = "EL1 Ceilg Construction"
   LOCATION         = TOP
   ..
"EL1 North Perim Spc (G.N8)" = SPACE           
   SHAPE            = POLYGON
   ZONE-TYPE        = CONDITIONED
   PEOPLE-SCHEDULE  = "EL1 Bldg Occup Sch"
   LIGHTING-SCHEDUL = ( "EL1 Bldg InsLt Sch" )
   EQUIP-SCHEDULE   = ( "EL1 Bldg Misc Sch", "Procedd Load Sch" )
   INF-SCHEDULE     = "ZG0-S1 (FC) P-Inf Sch"
   INF-METHOD       = AIR-CHANGE
   INF-FLOW/AREA    = 0.027
   PEOPLE-HG-LAT    = 250
   PEOPLE-HG-SENS   = 250
   EQUIP-LATENT     = ( 0 )
   EQUIP-SENSIBLE   = ( 1 )
   LIGHTING-W/AREA  = ( 0.68 )
   EQUIPMENT-W/AREA = ( 1.05, 0 )
   DAYLIGHTING      = YES
   LIGHT-REF-POINT1 = ( 65, 5 )
   AREA/PERSON      = 100
   POLYGON          = "EL1 Space Polygon 3"
   LOCATION         = FLOOR-V3
   C-SUB-SRC-BTUH   = ( 0, 0, 0 )
   C-SUB-SRC-KW     = ( 0, 0, 0 )
   C-ACTIVITY-DESC  = *Lobby (Reception/Waiting)*
   ..
"EL1 North Wall (G.N8.E3)" = EXTERIOR-WALL   
   CONSTRUCTION     = "EL1 EWall Construction"
   LOCATION         = SPACE-V1
   ..
"EL1 North Win (G.N8.E3.W1)" = WINDOW          
   GLASS-TYPE       = "EL1 Window Type #1 GT"
   FRAME-WIDTH      = 1
   X                = 14.375
   Y                = 0.5
   HEIGHT           = 8
   WIDTH            = 71.9583
   FRAME-CONDUCT    = 2.781
   ..
"EL1 North Win (G.N8.E3.W2)" = WINDOW          
   GLASS-TYPE       = "EL1 Window Type #1 GT"
   FRAME-WIDTH      = 1
   X                = 97.6667
   Y                = 0.5
   HEIGHT           = 8
   WIDTH            = 71.9583
   FRAME-CONDUCT    = 2.781
   ..
"EL1 North Door (G.N8.E3.D1)" = WINDOW          
   GLASS-TYPE       = "EL1 Door Type #1 GT"
   FRAME-WIDTH      = 1
   X                = 89.25
   Y                = 0.25
   HEIGHT           = 6.5
   WIDTH            = 5.5
   FRAME-CONDUCT    = 3.079
   ..
"EL1 Flr (G.N8.I23)" = INTERIOR-WALL   
   NEXT-TO          = "EL1 North Perim Spc (B.N3)"
   CONSTRUCTION     = "EL1 IFlr Construction"
   LOCATION         = BOTTOM
   ..
"EL1 SW Wall (G.N8.I24)" = INTERIOR-WALL   
   NEXT-TO          = "EL1 West Perim Spc (G.W9)"
   CONSTRUCTION     = "EL1 IWall Construction"
   LOCATION         = SPACE-V2
   ..
"EL1 South Wall (G.N8.I25)" = INTERIOR-WALL   
   NEXT-TO          = "EL1 Core Spc (G.C10)"
   CONSTRUCTION     = "EL1 IWall Construction"
   LOCATION         = SPACE-V3
   ..
"EL1 Ceiling (G.N8.I26)" = INTERIOR-WALL   
   NEXT-TO          = "EL1 North Perim Spc (M.N13)"
   CONSTRUCTION     = "EL1 Ceilg Construction"
   LOCATION         = TOP
   ..
"EL1 West Perim Spc (G.W9)" = SPACE           
   SHAPE            = POLYGON
   ZONE-TYPE        = CONDITIONED
   PEOPLE-SCHEDULE  = "EL1 Bldg Occup Sch"
   LIGHTING-SCHEDUL = ( "EL1 Bldg InsLt Sch" )
   EQUIP-SCHEDULE   = ( "EL1 Bldg Misc Sch", "Procedd Load Sch" )
   INF-SCHEDULE     = "ZG0-S1 (FC) P-Inf Sch"
   INF-METHOD       = AIR-CHANGE
   INF-FLOW/AREA    = 0.027
   PEOPLE-HG-LAT    = 250
   PEOPLE-HG-SENS   = 250
   EQUIP-LATENT     = ( 0 )
   EQUIP-SENSIBLE   = ( 1 )
   LIGHTING-W/AREA  = ( 0.68 )
   EQUIPMENT-W/AREA = ( 1.05, 0 )
   DAYLIGHTING      = YES
   LIGHT-REF-POINT1 = ( 65, 5 )
   AREA/PERSON      = 100
   POLYGON          = "EL1 Space Polygon 4"
   LOCATION         = FLOOR-V4
   C-SUB-SRC-BTUH   = ( 0, 0, 0 )
   C-SUB-SRC-KW     = ( 0, 0, 0 )
   C-ACTIVITY-DESC  = *Lobby (Reception/Waiting)*
   ..
"EL1 West Wall (G.W9.E4)" = EXTERIOR-WALL   
   CONSTRUCTION     = "EL1 EWall Construction"
   LOCATION         = SPACE-V1
   ..
"EL1 West Win (G.W9.E4.W1)" = WINDOW          
   GLASS-TYPE       = "EL1 Window Type #1 GT"
   FRAME-WIDTH      = 1
   X                = 9.95156
   Y                = 0.5
   HEIGHT           = 8
   WIDTH            = 48.0718
   FRAME-CONDUCT    = 2.781
   ..
"EL1 West Win (G.W9.E4.W2)" = WINDOW          
   GLASS-TYPE       = "EL1 Window Type #1 GT"
   FRAME-WIDTH      = 1
   X                = 69.3567
   Y                = 0.5
   HEIGHT           = 8
   WIDTH            = 48.0718
   FRAME-CONDUCT    = 2.781
   ..
"EL1 West Door (G.W9.E4.D1)" = WINDOW          
   GLASS-TYPE       = "EL1 Door Type #1 GT"
   FRAME-WIDTH      = 1
   X                = 60.94
   Y                = 0.25
   HEIGHT           = 6.5
   WIDTH            = 5.5
   FRAME-CONDUCT    = 3.079
   ..
"EL1 Flr (G.W9.I27)" = INTERIOR-WALL   
   NEXT-TO          = "EL1 West Perim Spc (B.W4)"
   CONSTRUCTION     = "EL1 IFlr Construction"
   LOCATION         = BOTTOM
   ..
"EL1 East Wall (G.W9.I28)" = INTERIOR-WALL   
   NEXT-TO          = "EL1 Core Spc (G.C10)"
   CONSTRUCTION     = "EL1 IWall Construction"
   LOCATION         = SPACE-V3
   ..
"EL1 Ceiling (G.W9.I29)" = INTERIOR-WALL   
   NEXT-TO          = "EL1 West Perim Spc (M.W14)"
   CONSTRUCTION     = "EL1 Ceilg Construction"
   LOCATION         = TOP
   ..
"EL1 Core Spc (G.C10)" = SPACE           
   X                = 15
   Y                = 15
   SHAPE            = POLYGON
   ZONE-TYPE        = CONDITIONED
   PEOPLE-SCHEDULE  = "EL1 Bldg Occup Sch"
   LIGHTING-SCHEDUL = ( "EL1 Bldg InsLt Sch" )
   EQUIP-SCHEDULE   = ( "EL1 Bldg Misc Sch", "Procedd Load Sch" )
   INF-SCHEDULE     = "ZG0-S1 (FC) C-Inf Sch"
   INF-METHOD       = AIR-CHANGE
   INF-FLOW/AREA    = 0.009
   PEOPLE-HG-LAT    = 250
   PEOPLE-HG-SENS   = 250
   EQUIP-LATENT     = ( 0 )
   EQUIP-SENSIBLE   = ( 1 )
   LIGHTING-W/AREA  = ( 0.68 )
   EQUIPMENT-W/AREA = ( 1.05, 0 )
   AREA/PERSON      = 2000
   POLYGON          = "EL1 Space Polygon 5"
   C-SUB-SRC-BTUH   = ( 0, 0, 0 )
   C-SUB-SRC-KW     = ( 0, 0, 0 )
   C-ACTIVITY-DESC  = *Mechanical/Electrical Room*
   ..
"EL1 Flr (G.C10.I30)" = INTERIOR-WALL   
   NEXT-TO          = "EL1 Core Spc (B.C5)"
   CONSTRUCTION     = "EL1 IFlr Construction"
   LOCATION         = BOTTOM
   ..
"EL1 Ceiling (G.C10.I31)" = INTERIOR-WALL   
   NEXT-TO          = "EL1 Core Spc (M.C15)"
   CONSTRUCTION     = "EL1 Ceilg Construction"
   LOCATION         = TOP
   ..
"EL1 Above-Grade Flrs" = FLOOR           
   MULTIPLIER       = 15
   Z                = 9
   AZIMUTH          = 360
   POLYGON          = "EL1 Floor Polygon"
   SHAPE            = POLYGON
   FLOOR-HEIGHT     = 9
   SPACE-HEIGHT     = 9
   C-DIAGRAM-DATA   = *Bldg Envelope & Loads 1 Diag Data*
   ..
"EL1 South Perim Spc (M.S11)" = SPACE           
   SHAPE            = POLYGON
   ZONE-TYPE        = CONDITIONED
   PEOPLE-SCHEDULE  = "EL1 Bldg Occup Sch"
   LIGHTING-SCHEDUL = ( "EL1 Bldg InsLt Sch" )
   EQUIP-SCHEDULE   = ( "EL1 Bldg Misc Sch", "Procedd Load Sch", 
         "Procedd Load Sch", "Procedd Load Sch" )
   INF-SCHEDULE     = "ZG0-S1 (FC) P-Inf Sch"
   INF-METHOD       = AIR-CHANGE
   INF-FLOW/AREA    = 0.027
   PEOPLE-HG-LAT    = 198.58
   PEOPLE-HG-SENS   = 249.644
   EQUIP-LATENT     = ( 0, 0, 0, 0, 0 )
   EQUIP-SENSIBLE   = ( 1, 1, 1, 1, 0 )
   LIGHTING-W/AREA  = ( 0.68 )
   EQUIPMENT-W/AREA = ( 1.05, 0, 0, 0, 0 )
   DAYLIGHTING      = YES
   LIGHT-REF-POINT1 = ( 65, 5 )
   AREA/PERSON      = 187.486
   POLYGON          = "EL1 Space Polygon 1"
   LOCATION         = FLOOR-V1
   C-SUB-SRC-BTUH   = ( 0, 0, 0 )
   C-SUB-SRC-KW     = ( 0, 0, 0.4763 )
   C-ACTIVITY-DESC  = *Office (Executive/Private) (74%)*
   ..
"EL1 South Wall (M.S11.E5)" = EXTERIOR-WALL   
   CONSTRUCTION     = "EL1 EWall Construction"
   LOCATION         = SPACE-V1
   ..
"EL1 South Win (M.S11.E5.W1)" = WINDOW          
   GLASS-TYPE       = "EL1 Window Type #1 GT"
   FRAME-WIDTH      = 1
   X                = 14.375
   Y                = 0.5
   HEIGHT           = 8
   WIDTH            = 155.25
   FRAME-CONDUCT    = 2.781
   ..
"Exterior Wall 22" = EXTERIOR-WALL   
   CONSTRUCTION     = "EL1 EWall Construction"
   LOCATION         = SPACE-V1
   ..
"Window 25" = WINDOW          
   GLASS-TYPE       = "EL1 Window Type #1 GT"
   FRAME-WIDTH      = 1
   X                = 14.375
   Y                = 0.5
   HEIGHT           = 8
   WIDTH            = 155.25
   FRAME-CONDUCT    = 2.781
   ..
"EL1 Flr (M.S11.I32)" = INTERIOR-WALL   
   NEXT-TO          = "EL1 South Perim Spc (G.S6)"
   CONSTRUCTION     = "EL1 IFlr Construction"
   LOCATION         = BOTTOM
   ..
"EL1 NE Wall (M.S11.I33)" = INTERIOR-WALL   
   NEXT-TO          = "EL1 East Perim Spc (M.E12)"
   CONSTRUCTION     = "EL1 IWall Construction"
   LOCATION         = SPACE-V2
   ..
"EL1 North Wall (M.S11.I34)" = INTERIOR-WALL   
   NEXT-TO          = "EL1 Core Spc (M.C15)"
   CONSTRUCTION     = "EL1 IWall Construction"
   LOCATION         = SPACE-V3
   ..
"EL1 NW Wall (M.S11.I35)" = INTERIOR-WALL   
   NEXT-TO          = "EL1 West Perim Spc (M.W14)"
   CONSTRUCTION     = "EL1 IWall Construction"
   LOCATION         = SPACE-V4
   ..
"EL1 Ceiling (M.S11.I36)" = INTERIOR-WALL   
   NEXT-TO          = "EL1 South Perim Spc (T.S16)"
   CONSTRUCTION     = "EL1 Ceilg Construction"
   LOCATION         = TOP
   ..
"Interior Wall 81" = INTERIOR-WALL   
   NEXT-TO          = "EL1 South Perim Spc (G.S6)"
   CONSTRUCTION     = "EL1 IFlr Construction"
   LOCATION         = BOTTOM
   ..
"Interior Wall 82" = INTERIOR-WALL   
   NEXT-TO          = "EL1 East Perim Spc (M.E12)"
   CONSTRUCTION     = "EL1 IWall Construction"
   LOCATION         = SPACE-V2
   ..
"Interior Wall 83" = INTERIOR-WALL   
   NEXT-TO          = "EL1 Core Spc (M.C15)"
   CONSTRUCTION     = "EL1 IWall Construction"
   LOCATION         = SPACE-V3
   ..
"Interior Wall 84" = INTERIOR-WALL   
   NEXT-TO          = "EL1 West Perim Spc (M.W14)"
   CONSTRUCTION     = "EL1 IWall Construction"
   LOCATION         = SPACE-V4
   ..
"Interior Wall 85" = INTERIOR-WALL   
   NEXT-TO          = "EL1 South Perim Spc (T.S16)"
   CONSTRUCTION     = "EL1 Ceilg Construction"
   LOCATION         = TOP
   ..
"EL1 East Perim Spc (M.E12)" = SPACE           
   SHAPE            = POLYGON
   ZONE-TYPE        = CONDITIONED
   PEOPLE-SCHEDULE  = "EL1 Bldg Occup Sch"
   LIGHTING-SCHEDUL = ( "EL1 Bldg InsLt Sch" )
   EQUIP-SCHEDULE   = ( "EL1 Bldg Misc Sch", "Procedd Load Sch", 
         "Procedd Load Sch", "Procedd Load Sch" )
   INF-SCHEDULE     = "ZG0-S1 (FC) P-Inf Sch"
   INF-METHOD       = AIR-CHANGE
   INF-FLOW/AREA    = 0.027
   PEOPLE-HG-LAT    = 198.58
   PEOPLE-HG-SENS   = 249.644
   EQUIP-LATENT     = ( 0, 0, 0, 0, 0 )
   EQUIP-SENSIBLE   = ( 1, 1, 1, 1, 0 )
   LIGHTING-W/AREA  = ( 0.68 )
   EQUIPMENT-W/AREA = ( 1.05, 0, 0, 0, 0 )
   DAYLIGHTING      = YES
   LIGHT-REF-POINT1 = ( 65, 5 )
   AREA/PERSON      = 187.486
   POLYGON          = "EL1 Space Polygon 2"
   LOCATION         = FLOOR-V2
   C-SUB-SRC-BTUH   = ( 0, 0, 0 )
   C-SUB-SRC-KW     = ( 0, 0, 0.4763 )
   C-ACTIVITY-DESC  = *Office (Executive/Private) (74%)*
   ..
"EL1 East Wall (M.E12.E6)" = EXTERIOR-WALL   
   CONSTRUCTION     = "EL1 EWall Construction"
   LOCATION         = SPACE-V1
   ..
"EL1 East Win (M.E12.E6.W1)" = WINDOW          
   GLASS-TYPE       = "EL1 Window Type #1 GT"
   FRAME-WIDTH      = 1
   X                = 9.95156
   Y                = 0.5
   HEIGHT           = 8
   WIDTH            = 107.477
   FRAME-CONDUCT    = 2.781
   ..
"Exterior Wall 23" = EXTERIOR-WALL   
   CONSTRUCTION     = "EL1 EWall Construction"
   LOCATION         = SPACE-V1
   ..
"Window 26" = WINDOW          
   GLASS-TYPE       = "EL1 Window Type #1 GT"
   FRAME-WIDTH      = 1
   X                = 9.95156
   Y                = 0.5
   HEIGHT           = 8
   WIDTH            = 107.477
   FRAME-CONDUCT    = 2.781
   ..
"EL1 Flr (M.E12.I37)" = INTERIOR-WALL   
   NEXT-TO          = "EL1 East Perim Spc (G.E7)"
   CONSTRUCTION     = "EL1 IFlr Construction"
   LOCATION         = BOTTOM
   ..
"EL1 NW Wall (M.E12.I38)" = INTERIOR-WALL   
   NEXT-TO          = "EL1 North Perim Spc (M.N13)"
   CONSTRUCTION     = "EL1 IWall Construction"
   LOCATION         = SPACE-V2
   ..
"EL1 West Wall (M.E12.I39)" = INTERIOR-WALL   
   NEXT-TO          = "EL1 Core Spc (M.C15)"
   CONSTRUCTION     = "EL1 IWall Construction"
   LOCATION         = SPACE-V3
   ..
"EL1 Ceiling (M.E12.I40)" = INTERIOR-WALL   
   NEXT-TO          = "EL1 East Perim Spc (T.E17)"
   CONSTRUCTION     = "EL1 Ceilg Construction"
   LOCATION         = TOP
   ..
"Interior Wall 86" = INTERIOR-WALL   
   NEXT-TO          = "EL1 East Perim Spc (G.E7)"
   CONSTRUCTION     = "EL1 IFlr Construction"
   LOCATION         = BOTTOM
   ..
"Interior Wall 87" = INTERIOR-WALL   
   NEXT-TO          = "EL1 North Perim Spc (M.N13)"
   CONSTRUCTION     = "EL1 IWall Construction"
   LOCATION         = SPACE-V2
   ..
"Interior Wall 88" = INTERIOR-WALL   
   NEXT-TO          = "EL1 Core Spc (M.C15)"
   CONSTRUCTION     = "EL1 IWall Construction"
   LOCATION         = SPACE-V3
   ..
"Interior Wall 89" = INTERIOR-WALL   
   NEXT-TO          = "EL1 East Perim Spc (T.E17)"
   CONSTRUCTION     = "EL1 Ceilg Construction"
   LOCATION         = TOP
   ..
"EL1 North Perim Spc (M.N13)" = SPACE           
   SHAPE            = POLYGON
   ZONE-TYPE        = CONDITIONED
   PEOPLE-SCHEDULE  = "EL1 Bldg Occup Sch"
   LIGHTING-SCHEDUL = ( "EL1 Bldg InsLt Sch" )
   EQUIP-SCHEDULE   = ( "EL1 Bldg Misc Sch", "Procedd Load Sch", 
         "Procedd Load Sch", "Procedd Load Sch" )
   INF-SCHEDULE     = "ZG0-S1 (FC) P-Inf Sch"
   INF-METHOD       = AIR-CHANGE
   INF-FLOW/AREA    = 0.027
   PEOPLE-HG-LAT    = 198.58
   PEOPLE-HG-SENS   = 249.644
   EQUIP-LATENT     = ( 0, 0, 0, 0, 0 )
   EQUIP-SENSIBLE   = ( 1, 1, 1, 1, 0 )
   LIGHTING-W/AREA  = ( 0.68 )
   EQUIPMENT-W/AREA = ( 1.05, 0, 0, 0, 0 )
   DAYLIGHTING      = YES
   LIGHT-REF-POINT1 = ( 65, 5 )
   AREA/PERSON      = 187.486
   POLYGON          = "EL1 Space Polygon 3"
   LOCATION         = FLOOR-V3
   C-SUB-SRC-BTUH   = ( 0, 0, 0 )
   C-SUB-SRC-KW     = ( 0, 0, 0.4763 )
   C-ACTIVITY-DESC  = *Office (Executive/Private) (74%)*
   ..
"EL1 North Wall (M.N13.E7)" = EXTERIOR-WALL   
   CONSTRUCTION     = "EL1 EWall Construction"
   LOCATION         = SPACE-V1
   ..
"EL1 North Win (M.N13.E7.W1)" = WINDOW          
   GLASS-TYPE       = "EL1 Window Type #1 GT"
   FRAME-WIDTH      = 1
   X                = 14.375
   Y                = 0.5
   HEIGHT           = 8
   WIDTH            = 155.25
   FRAME-CONDUCT    = 2.781
   ..
"Exterior Wall 24" = EXTERIOR-WALL   
   CONSTRUCTION     = "EL1 EWall Construction"
   LOCATION         = SPACE-V1
   ..
"Window 27" = WINDOW          
   GLASS-TYPE       = "EL1 Window Type #1 GT"
   FRAME-WIDTH      = 1
   X                = 14.375
   Y                = 0.5
   HEIGHT           = 8
   WIDTH            = 155.25
   FRAME-CONDUCT    = 2.781
   ..
"EL1 Flr (M.N13.I41)" = INTERIOR-WALL   
   NEXT-TO          = "EL1 North Perim Spc (G.N8)"
   CONSTRUCTION     = "EL1 IFlr Construction"
   LOCATION         = BOTTOM
   ..
"EL1 SW Wall (M.N13.I42)" = INTERIOR-WALL   
   NEXT-TO          = "EL1 West Perim Spc (M.W14)"
   CONSTRUCTION     = "EL1 IWall Construction"
   LOCATION         = SPACE-V2
   ..
"EL1 South Wall (M.N13.I43)" = INTERIOR-WALL   
   NEXT-TO          = "EL1 Core Spc (M.C15)"
   CONSTRUCTION     = "EL1 IWall Construction"
   LOCATION         = SPACE-V3
   ..
"EL1 Ceiling (M.N13.I44)" = INTERIOR-WALL   
   NEXT-TO          = "EL1 North Perim Spc (T.N18)"
   CONSTRUCTION     = "EL1 Ceilg Construction"
   LOCATION         = TOP
   ..
"Interior Wall 90" = INTERIOR-WALL   
   NEXT-TO          = "EL1 North Perim Spc (G.N8)"
   CONSTRUCTION     = "EL1 IFlr Construction"
   LOCATION         = BOTTOM
   ..
"Interior Wall 91" = INTERIOR-WALL   
   NEXT-TO          = "EL1 West Perim Spc (M.W14)"
   CONSTRUCTION     = "EL1 IWall Construction"
   LOCATION         = SPACE-V2
   ..
"Interior Wall 92" = INTERIOR-WALL   
   NEXT-TO          = "EL1 Core Spc (M.C15)"
   CONSTRUCTION     = "EL1 IWall Construction"
   LOCATION         = SPACE-V3
   ..
"Interior Wall 93" = INTERIOR-WALL   
   NEXT-TO          = "EL1 North Perim Spc (T.N18)"
   CONSTRUCTION     = "EL1 Ceilg Construction"
   LOCATION         = TOP
   ..
"EL1 West Perim Spc (M.W14)" = SPACE           
   SHAPE            = POLYGON
   ZONE-TYPE        = CONDITIONED
   PEOPLE-SCHEDULE  = "EL1 Bldg Occup Sch"
   LIGHTING-SCHEDUL = ( "EL1 Bldg InsLt Sch" )
   EQUIP-SCHEDULE   = ( "EL1 Bldg Misc Sch", "Procedd Load Sch", 
         "Procedd Load Sch", "Procedd Load Sch" )
   INF-SCHEDULE     = "ZG0-S1 (FC) P-Inf Sch"
   INF-METHOD       = AIR-CHANGE
   INF-FLOW/AREA    = 0.027
   PEOPLE-HG-LAT    = 198.58
   PEOPLE-HG-SENS   = 249.644
   EQUIP-LATENT     = ( 0, 0, 0, 0, 0 )
   EQUIP-SENSIBLE   = ( 1, 1, 1, 1, 0 )
   LIGHTING-W/AREA  = ( 0.68 )
   EQUIPMENT-W/AREA = ( 1.05, 0, 0, 0, 0 )
   DAYLIGHTING      = YES
   LIGHT-REF-POINT1 = ( 65, 5 )
   AREA/PERSON      = 187.486
   POLYGON          = "EL1 Space Polygon 4"
   LOCATION         = FLOOR-V4
   C-SUB-SRC-BTUH   = ( 0, 0, 0 )
   C-SUB-SRC-KW     = ( 0, 0, 0.4763 )
   C-ACTIVITY-DESC  = *Office (Executive/Private) (74%)*
   ..
"EL1 West Wall (M.W14.E8)" = EXTERIOR-WALL   
   CONSTRUCTION     = "EL1 EWall Construction"
   LOCATION         = SPACE-V1
   ..
"EL1 West Win (M.W14.E8.W1)" = WINDOW          
   GLASS-TYPE       = "EL1 Window Type #1 GT"
   FRAME-WIDTH      = 1
   X                = 9.95156
   Y                = 0.5
   HEIGHT           = 8
   WIDTH            = 107.477
   FRAME-CONDUCT    = 2.781
   ..
"Exterior Wall 25" = EXTERIOR-WALL   
   CONSTRUCTION     = "EL1 EWall Construction"
   LOCATION         = SPACE-V1
   ..
"Window 28" = WINDOW          
   GLASS-TYPE       = "EL1 Window Type #1 GT"
   FRAME-WIDTH      = 1
   X                = 9.95156
   Y                = 0.5
   HEIGHT           = 8
   WIDTH            = 107.477
   FRAME-CONDUCT    = 2.781
   ..
"EL1 Flr (M.W14.I45)" = INTERIOR-WALL   
   NEXT-TO          = "EL1 West Perim Spc (G.W9)"
   CONSTRUCTION     = "EL1 IFlr Construction"
   LOCATION         = BOTTOM
   ..
"EL1 East Wall (M.W14.I46)" = INTERIOR-WALL   
   NEXT-TO          = "EL1 Core Spc (M.C15)"
   CONSTRUCTION     = "EL1 IWall Construction"
   LOCATION         = SPACE-V3
   ..
"EL1 Ceiling (M.W14.I47)" = INTERIOR-WALL   
   NEXT-TO          = "EL1 West Perim Spc (T.W19)"
   CONSTRUCTION     = "EL1 Ceilg Construction"
   LOCATION         = TOP
   ..
"Interior Wall 94" = INTERIOR-WALL   
   NEXT-TO          = "EL1 West Perim Spc (G.W9)"
   CONSTRUCTION     = "EL1 IFlr Construction"
   LOCATION         = BOTTOM
   ..
"Interior Wall 95" = INTERIOR-WALL   
   NEXT-TO          = "EL1 Core Spc (M.C15)"
   CONSTRUCTION     = "EL1 IWall Construction"
   LOCATION         = SPACE-V3
   ..
"Interior Wall 96" = INTERIOR-WALL   
   NEXT-TO          = "EL1 West Perim Spc (T.W19)"
   CONSTRUCTION     = "EL1 Ceilg Construction"
   LOCATION         = TOP
   ..
"EL1 Core Spc (M.C15)" = SPACE           
   X                = 15
   Y                = 15
   SHAPE            = POLYGON
   ZONE-TYPE        = CONDITIONED
   PEOPLE-SCHEDULE  = "EL1 Bldg Occup Sch"
   LIGHTING-SCHEDUL = ( "EL1 Bldg InsLt Sch" )
   EQUIP-SCHEDULE   = ( "EL1 Bldg Misc Sch", "Procedd Load Sch", 
         "Procedd Load Sch", "Procedd Load Sch" )
   INF-SCHEDULE     = "ZG0-S1 (FC) C-Inf Sch"
   INF-METHOD       = AIR-CHANGE
   INF-FLOW/AREA    = 0.009
   PEOPLE-HG-LAT    = 201.518
   PEOPLE-HG-SENS   = 248.971
   EQUIP-LATENT     = ( 0, 0, 0, 0, 0 )
   EQUIP-SENSIBLE   = ( 1, 1, 1, 1, 0 )
   LIGHTING-W/AREA  = ( 0.68 )
   EQUIPMENT-W/AREA = ( 1.05, 0, 0, 0, 0 )
   AREA/PERSON      = 193.477
   POLYGON          = "EL1 Space Polygon 5"
   C-SUB-SRC-BTUH   = ( 0, 0, 0 )
   C-SUB-SRC-KW     = ( 0, 0, 0.2991 )
   C-ACTIVITY-DESC  = *Office (Open Plan) (60%)*
   ..
"EL1 Flr (M.C15.I48)" = INTERIOR-WALL   
   NEXT-TO          = "EL1 Core Spc (G.C10)"
   CONSTRUCTION     = "EL1 IFlr Construction"
   LOCATION         = BOTTOM
   ..
"EL1 Ceiling (M.C15.I49)" = INTERIOR-WALL   
   NEXT-TO          = "EL1 Core Spc (T.C20)"
   CONSTRUCTION     = "EL1 Ceilg Construction"
   LOCATION         = TOP
   ..
"Interior Wall 97" = INTERIOR-WALL   
   NEXT-TO          = "EL1 Core Spc (G.C10)"
   CONSTRUCTION     = "EL1 IFlr Construction"
   LOCATION         = BOTTOM
   ..
"Interior Wall 98" = INTERIOR-WALL   
   NEXT-TO          = "EL1 Core Spc (T.C20)"
   CONSTRUCTION     = "EL1 Ceilg Construction"
   LOCATION         = TOP
   ..
"EL1 Top Abv-Grade Flr" = FLOOR           
   Z                = 279
   AZIMUTH          = 360
   POLYGON          = "EL1 Floor Polygon"
   SHAPE            = POLYGON
   FLOOR-HEIGHT     = 9
   SPACE-HEIGHT     = 9
   C-DIAGRAM-DATA   = *Bldg Envelope & Loads 1 Diag Data*
   ..
"EL1 South Perim Spc (T.S16)" = SPACE           
   SHAPE            = POLYGON
   ZONE-TYPE        = CONDITIONED
   PEOPLE-SCHEDULE  = "EL1 Bldg Occup Sch"
   LIGHTING-SCHEDUL = ( "EL1 Bldg InsLt Sch" )
   EQUIP-SCHEDULE   = ( "EL1 Bldg Misc Sch", "Procedd Load Sch", 
         "Procedd Load Sch", "Procedd Load Sch", "Procedd Load Sch" )
   INF-SCHEDULE     = "ZG0-S1 (FC) P-Inf Sch"
   INF-METHOD       = AIR-CHANGE
   INF-FLOW/AREA    = 0.027
   PEOPLE-HG-LAT    = 198.58
   PEOPLE-HG-SENS   = 249.644
   EQUIP-LATENT     = ( 0, 0, 0, 0, 0 )
   EQUIP-SENSIBLE   = ( 1, 1, 1, 1, 0 )
   LIGHTING-W/AREA  = ( 0.68 )
   EQUIPMENT-W/AREA = ( 1.05, 0, 0, 0, 0 )
   DAYLIGHTING      = YES
   LIGHT-REF-POINT1 = ( 65, 5 )
   AREA/PERSON      = 187.486
   POLYGON          = "EL1 Space Polygon 1"
   LOCATION         = FLOOR-V1
   C-SUB-SRC-BTUH   = ( 0, 0, 0 )
   C-SUB-SRC-KW     = ( 0, 0, 0.4763 )
   C-ACTIVITY-DESC  = *Office (Executive/Private) (74%)*
   ..
"EL1 South Wall (T.S16.E9)" = EXTERIOR-WALL   
   CONSTRUCTION     = "EL1 EWall Construction"
   LOCATION         = SPACE-V1
   ..
"EL1 South Win (T.S16.E9.W1)" = WINDOW          
   GLASS-TYPE       = "EL1 Window Type #1 GT"
   FRAME-WIDTH      = 1
   X                = 14.375
   Y                = 0.5
   HEIGHT           = 8
   WIDTH            = 155.25
   FRAME-CONDUCT    = 2.781
   ..
"EL1 Roof (T.S16.E10)" = EXTERIOR-WALL   
   CONSTRUCTION     = "EL1 Roof Construction"
   LOCATION         = TOP
   ..
"EL1 Flr (T.S16.I50)" = INTERIOR-WALL   
   NEXT-TO          = "EL1 South Perim Spc (M.S11)"
   CONSTRUCTION     = "EL1 IFlr Construction"
   LOCATION         = BOTTOM
   ..
"EL1 NE Wall (T.S16.I51)" = INTERIOR-WALL   
   NEXT-TO          = "EL1 East Perim Spc (T.E17)"
   CONSTRUCTION     = "EL1 IWall Construction"
   LOCATION         = SPACE-V2
   ..
"EL1 North Wall (T.S16.I52)" = INTERIOR-WALL   
   NEXT-TO          = "EL1 Core Spc (T.C20)"
   CONSTRUCTION     = "EL1 IWall Construction"
   LOCATION         = SPACE-V3
   ..
"EL1 NW Wall (T.S16.I53)" = INTERIOR-WALL   
   NEXT-TO          = "EL1 West Perim Spc (T.W19)"
   CONSTRUCTION     = "EL1 IWall Construction"
   LOCATION         = SPACE-V4
   ..
"EL1 East Perim Spc (T.E17)" = SPACE           
   SHAPE            = POLYGON
   ZONE-TYPE        = CONDITIONED
   PEOPLE-SCHEDULE  = "EL1 Bldg Occup Sch"
   LIGHTING-SCHEDUL = ( "EL1 Bldg InsLt Sch" )
   EQUIP-SCHEDULE   = ( "EL1 Bldg Misc Sch", "Procedd Load Sch", 
         "Procedd Load Sch", "Procedd Load Sch", "Procedd Load Sch" )
   INF-SCHEDULE     = "ZG0-S1 (FC) P-Inf Sch"
   INF-METHOD       = AIR-CHANGE
   INF-FLOW/AREA    = 0.027
   PEOPLE-HG-LAT    = 198.58
   PEOPLE-HG-SENS   = 249.644
   EQUIP-LATENT     = ( 0, 0, 0, 0, 0 )
   EQUIP-SENSIBLE   = ( 1, 1, 1, 1, 0 )
   LIGHTING-W/AREA  = ( 0.68 )
   EQUIPMENT-W/AREA = ( 1.05, 0, 0, 0, 0 )
   DAYLIGHTING      = YES
   LIGHT-REF-POINT1 = ( 65, 5 )
   AREA/PERSON      = 187.486
   POLYGON          = "EL1 Space Polygon 2"
   LOCATION         = FLOOR-V2
   C-SUB-SRC-BTUH   = ( 0, 0, 0 )
   C-SUB-SRC-KW     = ( 0, 0, 0.4763 )
   C-ACTIVITY-DESC  = *Office (Executive/Private) (74%)*
   ..
"EL1 East Wall (T.E17.E11)" = EXTERIOR-WALL   
   CONSTRUCTION     = "EL1 EWall Construction"
   LOCATION         = SPACE-V1
   ..
"EL1 East Win (T.E17.E11.W1)" = WINDOW          
   GLASS-TYPE       = "EL1 Window Type #1 GT"
   FRAME-WIDTH      = 1
   X                = 9.95156
   Y                = 0.5
   HEIGHT           = 8
   WIDTH            = 107.477
   FRAME-CONDUCT    = 2.781
   ..
"EL1 Roof (T.E17.E12)" = EXTERIOR-WALL   
   CONSTRUCTION     = "EL1 Roof Construction"
   LOCATION         = TOP
   ..
"EL1 Flr (T.E17.I54)" = INTERIOR-WALL   
   NEXT-TO          = "EL1 East Perim Spc (M.E12)"
   CONSTRUCTION     = "EL1 IFlr Construction"
   LOCATION         = BOTTOM
   ..
"EL1 NW Wall (T.E17.I55)" = INTERIOR-WALL   
   NEXT-TO          = "EL1 North Perim Spc (T.N18)"
   CONSTRUCTION     = "EL1 IWall Construction"
   LOCATION         = SPACE-V2
   ..
"EL1 West Wall (T.E17.I56)" = INTERIOR-WALL   
   NEXT-TO          = "EL1 Core Spc (T.C20)"
   CONSTRUCTION     = "EL1 IWall Construction"
   LOCATION         = SPACE-V3
   ..
"EL1 North Perim Spc (T.N18)" = SPACE           
   SHAPE            = POLYGON
   ZONE-TYPE        = CONDITIONED
   PEOPLE-SCHEDULE  = "EL1 Bldg Occup Sch"
   LIGHTING-SCHEDUL = ( "EL1 Bldg InsLt Sch" )
   EQUIP-SCHEDULE   = ( "EL1 Bldg Misc Sch", "Procedd Load Sch", 
         "Procedd Load Sch", "Procedd Load Sch", "Procedd Load Sch" )
   INF-SCHEDULE     = "ZG0-S1 (FC) P-Inf Sch"
   INF-METHOD       = AIR-CHANGE
   INF-FLOW/AREA    = 0.027
   PEOPLE-HG-LAT    = 198.58
   PEOPLE-HG-SENS   = 249.644
   EQUIP-LATENT     = ( 0, 0, 0, 0, 0 )
   EQUIP-SENSIBLE   = ( 1, 1, 1, 1, 0 )
   LIGHTING-W/AREA  = ( 0.68 )
   EQUIPMENT-W/AREA = ( 1.05, 0, 0, 0, 0 )
   DAYLIGHTING      = YES
   LIGHT-REF-POINT1 = ( 65, 5 )
   AREA/PERSON      = 187.486
   POLYGON          = "EL1 Space Polygon 3"
   LOCATION         = FLOOR-V3
   C-SUB-SRC-BTUH   = ( 0, 0, 0 )
   C-SUB-SRC-KW     = ( 0, 0, 0.4763 )
   C-ACTIVITY-DESC  = *Office (Executive/Private) (74%)*
   ..
"EL1 North Wall (T.N18.E13)" = EXTERIOR-WALL   
   CONSTRUCTION     = "EL1 EWall Construction"
   LOCATION         = SPACE-V1
   ..
"EL1 North Win (T.N18.E13.W1)" = WINDOW          
   GLASS-TYPE       = "EL1 Window Type #1 GT"
   FRAME-WIDTH      = 1
   X                = 14.375
   Y                = 0.5
   HEIGHT           = 8
   WIDTH            = 155.25
   FRAME-CONDUCT    = 2.781
   ..
"EL1 Roof (T.N18.E14)" = EXTERIOR-WALL   
   CONSTRUCTION     = "EL1 Roof Construction"
   LOCATION         = TOP
   ..
"EL1 Flr (T.N18.I57)" = INTERIOR-WALL   
   NEXT-TO          = "EL1 North Perim Spc (M.N13)"
   CONSTRUCTION     = "EL1 IFlr Construction"
   LOCATION         = BOTTOM
   ..
"EL1 SW Wall (T.N18.I58)" = INTERIOR-WALL   
   NEXT-TO          = "EL1 West Perim Spc (T.W19)"
   CONSTRUCTION     = "EL1 IWall Construction"
   LOCATION         = SPACE-V2
   ..
"EL1 South Wall (T.N18.I59)" = INTERIOR-WALL   
   NEXT-TO          = "EL1 Core Spc (T.C20)"
   CONSTRUCTION     = "EL1 IWall Construction"
   LOCATION         = SPACE-V3
   ..
"EL1 West Perim Spc (T.W19)" = SPACE           
   SHAPE            = POLYGON
   ZONE-TYPE        = CONDITIONED
   PEOPLE-SCHEDULE  = "EL1 Bldg Occup Sch"
   LIGHTING-SCHEDUL = ( "EL1 Bldg InsLt Sch" )
   EQUIP-SCHEDULE   = ( "EL1 Bldg Misc Sch", "Procedd Load Sch", 
         "Procedd Load Sch", "Procedd Load Sch", "Procedd Load Sch" )
   INF-SCHEDULE     = "ZG0-S1 (FC) P-Inf Sch"
   INF-METHOD       = AIR-CHANGE
   INF-FLOW/AREA    = 0.027
   PEOPLE-HG-LAT    = 198.58
   PEOPLE-HG-SENS   = 249.644
   EQUIP-LATENT     = ( 0, 0, 0, 0, 0 )
   EQUIP-SENSIBLE   = ( 1, 1, 1, 1, 0 )
   LIGHTING-W/AREA  = ( 0.68 )
   EQUIPMENT-W/AREA = ( 1.05, 0, 0, 0, 0 )
   DAYLIGHTING      = YES
   LIGHT-REF-POINT1 = ( 65, 5 )
   AREA/PERSON      = 187.486
   POLYGON          = "EL1 Space Polygon 4"
   LOCATION         = FLOOR-V4
   C-SUB-SRC-BTUH   = ( 0, 0, 0 )
   C-SUB-SRC-KW     = ( 0, 0, 0.4763 )
   C-ACTIVITY-DESC  = *Office (Executive/Private) (74%)*
   ..
"EL1 West Wall (T.W19.E15)" = EXTERIOR-WALL   
   CONSTRUCTION     = "EL1 EWall Construction"
   LOCATION         = SPACE-V1
   ..
"EL1 West Win (T.W19.E15.W1)" = WINDOW          
   GLASS-TYPE       = "EL1 Window Type #1 GT"
   FRAME-WIDTH      = 1
   X                = 9.95156
   Y                = 0.5
   HEIGHT           = 8
   WIDTH            = 107.477
   FRAME-CONDUCT    = 2.781
   ..
"EL1 Roof (T.W19.E16)" = EXTERIOR-WALL   
   CONSTRUCTION     = "EL1 Roof Construction"
   LOCATION         = TOP
   ..
"EL1 Flr (T.W19.I60)" = INTERIOR-WALL   
   NEXT-TO          = "EL1 West Perim Spc (M.W14)"
   CONSTRUCTION     = "EL1 IFlr Construction"
   LOCATION         = BOTTOM
   ..
"EL1 East Wall (T.W19.I61)" = INTERIOR-WALL   
   NEXT-TO          = "EL1 Core Spc (T.C20)"
   CONSTRUCTION     = "EL1 IWall Construction"
   LOCATION         = SPACE-V3
   ..
"EL1 Core Spc (T.C20)" = SPACE           
   X                = 15
   Y                = 15
   SHAPE            = POLYGON
   ZONE-TYPE        = CONDITIONED
   PEOPLE-SCHEDULE  = "EL1 Bldg Occup Sch"
   LIGHTING-SCHEDUL = ( "EL1 Bldg InsLt Sch" )
   EQUIP-SCHEDULE   = ( "EL1 Bldg Misc Sch", "Procedd Load Sch", 
         "Procedd Load Sch", "Procedd Load Sch", "Procedd Load Sch" )
   INF-SCHEDULE     = "ZG0-S1 (FC) C-Inf Sch"
   INF-METHOD       = AIR-CHANGE
   INF-FLOW/AREA    = 0.009
   PEOPLE-HG-LAT    = 201.518
   PEOPLE-HG-SENS   = 248.971
   EQUIP-LATENT     = ( 0, 0, 0, 0, 0 )
   EQUIP-SENSIBLE   = ( 1, 1, 1, 1, 0 )
   LIGHTING-W/AREA  = ( 0.68 )
   EQUIPMENT-W/AREA = ( 1.05, 17.5, 0, 0, 0 )
   AREA/PERSON      = 193.477
   POLYGON          = "EL1 Space Polygon 5"
   C-SUB-SRC-BTUH   = ( 0, 0, 0 )
   C-SUB-SRC-KW     = ( 0, 0, 0.2991 )
   C-ACTIVITY-DESC  = *Office (Open Plan) (60%)*
   ..
"EL1 Roof (T.C20.E17)" = EXTERIOR-WALL   
   CONSTRUCTION     = "EL1 Roof Construction"
   LOCATION         = TOP
   ..
"EL1 Flr (T.C20.I62)" = INTERIOR-WALL   
   NEXT-TO          = "EL1 Core Spc (M.C15)"
   CONSTRUCTION     = "EL1 IFlr Construction"
   LOCATION         = BOTTOM
   ..
"Mid Floors 2" = FLOOR           
   MULTIPLIER       = 15
   Z                = 90
   AZIMUTH          = 360
   POLYGON          = "EL1 Floor Polygon"
   SHAPE            = POLYGON
   FLOOR-HEIGHT     = 9
   SPACE-HEIGHT     = 9
   C-DIAGRAM-DATA   = *Bldg Envelope & Loads 1 Diag Data*
   ..
"Space 21" = SPACE           
   SHAPE            = POLYGON
   ZONE-TYPE        = CONDITIONED
   PEOPLE-SCHEDULE  = "EL1 Bldg Occup Sch"
   LIGHTING-SCHEDUL = ( "EL1 Bldg InsLt Sch" )
   EQUIP-SCHEDULE   = ( "EL1 Bldg Misc Sch", "Procedd Load Sch", 
         "Procedd Load Sch", "Procedd Load Sch", "Procedd Load Sch" )
   INF-SCHEDULE     = "ZG0-S1 (FC) P-Inf Sch"
   INF-METHOD       = AIR-CHANGE
   INF-FLOW/AREA    = 0.027
   PEOPLE-HG-LAT    = 198.58
   PEOPLE-HG-SENS   = 249.644
   EQUIP-LATENT     = ( 0, 0, 0, 0, 0 )
   EQUIP-SENSIBLE   = ( 1, 1, 1, 1, 0 )
   LIGHTING-W/AREA  = ( 0.68 )
   EQUIPMENT-W/AREA = ( 1.05, 0, 0, 0, 0 )
   DAYLIGHTING      = YES
   LIGHT-REF-POINT1 = ( 65, 5 )
   AREA/PERSON      = 187.486
   POLYGON          = "EL1 Space Polygon 1"
   LOCATION         = FLOOR-V1
   C-SUB-SRC-BTUH   = ( 0, 0, 0 )
   C-SUB-SRC-KW     = ( 0, 0, 0.4763 )
   C-ACTIVITY-DESC  = *Office (Executive/Private) (74%)*
   ..
"Exterior Wall 18" = EXTERIOR-WALL   
   CONSTRUCTION     = "EL1 EWall Construction"
   LOCATION         = SPACE-V1
   ..
"Window 21" = WINDOW          
   GLASS-TYPE       = "EL1 Window Type #1 GT"
   FRAME-WIDTH      = 1
   X                = 14.375
   Y                = 0.5
   HEIGHT           = 8
   WIDTH            = 155.25
   FRAME-CONDUCT    = 2.781
   ..
"Interior Wall 63" = INTERIOR-WALL   
   NEXT-TO          = "EL1 South Perim Spc (G.S6)"
   CONSTRUCTION     = "EL1 IFlr Construction"
   LOCATION         = BOTTOM
   ..
"Interior Wall 64" = INTERIOR-WALL   
   NEXT-TO          = "EL1 East Perim Spc (M.E12)"
   CONSTRUCTION     = "EL1 IWall Construction"
   LOCATION         = SPACE-V2
   ..
"Interior Wall 65" = INTERIOR-WALL   
   NEXT-TO          = "EL1 Core Spc (M.C15)"
   CONSTRUCTION     = "EL1 IWall Construction"
   LOCATION         = SPACE-V3
   ..
"Interior Wall 66" = INTERIOR-WALL   
   NEXT-TO          = "EL1 West Perim Spc (M.W14)"
   CONSTRUCTION     = "EL1 IWall Construction"
   LOCATION         = SPACE-V4
   ..
"Interior Wall 67" = INTERIOR-WALL   
   NEXT-TO          = "EL1 South Perim Spc (T.S16)"
   CONSTRUCTION     = "EL1 Ceilg Construction"
   LOCATION         = TOP
   ..
"Space 22" = SPACE           
   SHAPE            = POLYGON
   ZONE-TYPE        = CONDITIONED
   PEOPLE-SCHEDULE  = "EL1 Bldg Occup Sch"
   LIGHTING-SCHEDUL = ( "EL1 Bldg InsLt Sch" )
   EQUIP-SCHEDULE   = ( "EL1 Bldg Misc Sch", "Procedd Load Sch", 
         "Procedd Load Sch", "Procedd Load Sch", "Procedd Load Sch" )
   INF-SCHEDULE     = "ZG0-S1 (FC) P-Inf Sch"
   INF-METHOD       = AIR-CHANGE
   INF-FLOW/AREA    = 0.027
   PEOPLE-HG-LAT    = 198.58
   PEOPLE-HG-SENS   = 249.644
   EQUIP-LATENT     = ( 0, 0, 0, 0, 0 )
   EQUIP-SENSIBLE   = ( 1, 1, 1, 1, 0 )
   LIGHTING-W/AREA  = ( 0.68 )
   EQUIPMENT-W/AREA = ( 1.05, 0, 0, 0, 0 )
   DAYLIGHTING      = YES
   LIGHT-REF-POINT1 = ( 65, 5 )
   AREA/PERSON      = 187.486
   POLYGON          = "EL1 Space Polygon 2"
   LOCATION         = FLOOR-V2
   C-SUB-SRC-BTUH   = ( 0, 0, 0 )
   C-SUB-SRC-KW     = ( 0, 0, 0.4763 )
   C-ACTIVITY-DESC  = *Office (Executive/Private) (74%)*
   ..
"Exterior Wall 19" = EXTERIOR-WALL   
   CONSTRUCTION     = "EL1 EWall Construction"
   LOCATION         = SPACE-V1
   ..
"Window 22" = WINDOW          
   GLASS-TYPE       = "EL1 Window Type #1 GT"
   FRAME-WIDTH      = 1
   X                = 9.95156
   Y                = 0.5
   HEIGHT           = 8
   WIDTH            = 107.477
   FRAME-CONDUCT    = 2.781
   ..
"Interior Wall 68" = INTERIOR-WALL   
   NEXT-TO          = "EL1 East Perim Spc (G.E7)"
   CONSTRUCTION     = "EL1 IFlr Construction"
   LOCATION         = BOTTOM
   ..
"Interior Wall 69" = INTERIOR-WALL   
   NEXT-TO          = "EL1 North Perim Spc (M.N13)"
   CONSTRUCTION     = "EL1 IWall Construction"
   LOCATION         = SPACE-V2
   ..
"Interior Wall 70" = INTERIOR-WALL   
   NEXT-TO          = "EL1 Core Spc (M.C15)"
   CONSTRUCTION     = "EL1 IWall Construction"
   LOCATION         = SPACE-V3
   ..
"Interior Wall 71" = INTERIOR-WALL   
   NEXT-TO          = "EL1 East Perim Spc (T.E17)"
   CONSTRUCTION     = "EL1 Ceilg Construction"
   LOCATION         = TOP
   ..
"Space 23" = SPACE           
   SHAPE            = POLYGON
   ZONE-TYPE        = CONDITIONED
   PEOPLE-SCHEDULE  = "EL1 Bldg Occup Sch"
   LIGHTING-SCHEDUL = ( "EL1 Bldg InsLt Sch" )
   EQUIP-SCHEDULE   = ( "EL1 Bldg Misc Sch", "Procedd Load Sch", 
         "Procedd Load Sch", "Procedd Load Sch", "Procedd Load Sch" )
   INF-SCHEDULE     = "ZG0-S1 (FC) P-Inf Sch"
   INF-METHOD       = AIR-CHANGE
   INF-FLOW/AREA    = 0.027
   PEOPLE-HG-LAT    = 198.58
   PEOPLE-HG-SENS   = 249.644
   EQUIP-LATENT     = ( 0, 0, 0, 0, 0 )
   EQUIP-SENSIBLE   = ( 1, 1, 1, 1, 0 )
   LIGHTING-W/AREA  = ( 0.68 )
   EQUIPMENT-W/AREA = ( 1.05, 0, 0, 0, 0 )
   DAYLIGHTING      = YES
   LIGHT-REF-POINT1 = ( 65, 5 )
   AREA/PERSON      = 187.486
   POLYGON          = "EL1 Space Polygon 3"
   LOCATION         = FLOOR-V3
   C-SUB-SRC-BTUH   = ( 0, 0, 0 )
   C-SUB-SRC-KW     = ( 0, 0, 0.4763 )
   C-ACTIVITY-DESC  = *Office (Executive/Private) (74%)*
   ..
"Exterior Wall 20" = EXTERIOR-WALL   
   CONSTRUCTION     = "EL1 EWall Construction"
   LOCATION         = SPACE-V1
   ..
"Window 23" = WINDOW          
   GLASS-TYPE       = "EL1 Window Type #1 GT"
   FRAME-WIDTH      = 1
   X                = 14.375
   Y                = 0.5
   HEIGHT           = 8
   WIDTH            = 155.25
   FRAME-CONDUCT    = 2.781
   ..
"Interior Wall 72" = INTERIOR-WALL   
   NEXT-TO          = "EL1 North Perim Spc (G.N8)"
   CONSTRUCTION     = "EL1 IFlr Construction"
   LOCATION         = BOTTOM
   ..
"Interior Wall 73" = INTERIOR-WALL   
   NEXT-TO          = "EL1 West Perim Spc (M.W14)"
   CONSTRUCTION     = "EL1 IWall Construction"
   LOCATION         = SPACE-V2
   ..
"Interior Wall 74" = INTERIOR-WALL   
   NEXT-TO          = "EL1 Core Spc (M.C15)"
   CONSTRUCTION     = "EL1 IWall Construction"
   LOCATION         = SPACE-V3
   ..
"Interior Wall 75" = INTERIOR-WALL   
   NEXT-TO          = "EL1 North Perim Spc (T.N18)"
   CONSTRUCTION     = "EL1 Ceilg Construction"
   LOCATION         = TOP
   ..
"Space 24" = SPACE           
   SHAPE            = POLYGON
   ZONE-TYPE        = CONDITIONED
   PEOPLE-SCHEDULE  = "EL1 Bldg Occup Sch"
   LIGHTING-SCHEDUL = ( "EL1 Bldg InsLt Sch" )
   EQUIP-SCHEDULE   = ( "EL1 Bldg Misc Sch", "Procedd Load Sch", 
         "Procedd Load Sch", "Procedd Load Sch", "Procedd Load Sch" )
   INF-SCHEDULE     = "ZG0-S1 (FC) P-Inf Sch"
   INF-METHOD       = AIR-CHANGE
   INF-FLOW/AREA    = 0.027
   PEOPLE-HG-LAT    = 198.58
   PEOPLE-HG-SENS   = 249.644
   EQUIP-LATENT     = ( 0, 0, 0, 0, 0 )
   EQUIP-SENSIBLE   = ( 1, 1, 1, 1, 0 )
   LIGHTING-W/AREA  = ( 0.68 )
   EQUIPMENT-W/AREA = ( 1.05, 0, 0, 0, 0 )
   DAYLIGHTING      = YES
   LIGHT-REF-POINT1 = ( 65, 5 )
   AREA/PERSON      = 187.486
   POLYGON          = "EL1 Space Polygon 4"
   LOCATION         = FLOOR-V4
   C-SUB-SRC-BTUH   = ( 0, 0, 0 )
   C-SUB-SRC-KW     = ( 0, 0, 0.4763 )
   C-ACTIVITY-DESC  = *Office (Executive/Private) (74%)*
   ..
"Exterior Wall 21" = EXTERIOR-WALL   
   CONSTRUCTION     = "EL1 EWall Construction"
   LOCATION         = SPACE-V1
   ..
"Window 24" = WINDOW          
   GLASS-TYPE       = "EL1 Window Type #1 GT"
   FRAME-WIDTH      = 1
   X                = 9.95156
   Y                = 0.5
   HEIGHT           = 8
   WIDTH            = 107.477
   FRAME-CONDUCT    = 2.781
   ..
"Interior Wall 76" = INTERIOR-WALL   
   NEXT-TO          = "EL1 West Perim Spc (G.W9)"
   CONSTRUCTION     = "EL1 IFlr Construction"
   LOCATION         = BOTTOM
   ..
"Interior Wall 77" = INTERIOR-WALL   
   NEXT-TO          = "EL1 Core Spc (M.C15)"
   CONSTRUCTION     = "EL1 IWall Construction"
   LOCATION         = SPACE-V3
   ..
"Interior Wall 78" = INTERIOR-WALL   
   NEXT-TO          = "EL1 West Perim Spc (T.W19)"
   CONSTRUCTION     = "EL1 Ceilg Construction"
   LOCATION         = TOP
   ..
"Space 25" = SPACE           
   X                = 15
   Y                = 15
   SHAPE            = POLYGON
   ZONE-TYPE        = CONDITIONED
   PEOPLE-SCHEDULE  = "EL1 Bldg Occup Sch"
   LIGHTING-SCHEDUL = ( "EL1 Bldg InsLt Sch" )
   EQUIP-SCHEDULE   = ( "EL1 Bldg Misc Sch", "Procedd Load Sch", 
         "Procedd Load Sch", "Procedd Load Sch", "Procedd Load Sch" )
   INF-SCHEDULE     = "ZG0-S1 (FC) C-Inf Sch"
   INF-METHOD       = AIR-CHANGE
   INF-FLOW/AREA    = 0.009
   PEOPLE-HG-LAT    = 201.518
   PEOPLE-HG-SENS   = 248.971
   EQUIP-LATENT     = ( 0, 0, 0, 0, 0 )
   EQUIP-SENSIBLE   = ( 1, 1, 1, 1, 0 )
   LIGHTING-W/AREA  = ( 0.68 )
   EQUIPMENT-W/AREA = ( 1.05, 0, 0, 0, 0 )
   AREA/PERSON      = 193.477
   POLYGON          = "EL1 Space Polygon 5"
   C-SUB-SRC-BTUH   = ( 0, 0, 0 )
   C-SUB-SRC-KW     = ( 0, 0, 0.2991 )
   C-ACTIVITY-DESC  = *Office (Open Plan) (60%)*
   ..
"Interior Wall 79" = INTERIOR-WALL   
   NEXT-TO          = "EL1 Core Spc (G.C10)"
   CONSTRUCTION     = "EL1 IFlr Construction"
   LOCATION         = BOTTOM
   ..
"Interior Wall 80" = INTERIOR-WALL   
   NEXT-TO          = "EL1 Core Spc (T.C20)"
   CONSTRUCTION     = "EL1 Ceilg Construction"
   LOCATION         = TOP
   ..


$ *********************************************************
$ **                                                     **
$ **                Performance Curves                   **
$ **                                                     **
$ *********************************************************

"Static Pressure Reset Sch" = CURVE-FIT       
   TYPE             = CUBIC
   INPUT-TYPE       = COEFFICIENTS
   COEFFICIENTS     = ( 0.0278279, 0.0265832, -0.0870687, 1.03092 )
   ..

$ *********************************************************
$ **                                                     **
$ **              Electric & Fuel Meters                 **
$ **                                                     **
$ *********************************************************

$ ---------------------------------------------------------
$              Electric Meters
$ ---------------------------------------------------------

"EM1" = ELEC-METER      
   TYPE             = UTILITY
   EXTERIOR-POWER   = ( 110 )
   EXTERIOR-SCH     = ( "OFFICE ELEV" )
   EXTERIOR-EU      = ( TASK-LIGHTS )
   ..


$ ---------------------------------------------------------
$              Fuel Meters
$ ---------------------------------------------------------



$ ---------------------------------------------------------
$              Master Meters
$ ---------------------------------------------------------

"MASTER-METERS 1" = MASTER-METERS   
   MSTR-ELEC-METER  = "EM1"
   MSTR-FUEL-METER  = "FM1"
   ..


$ *********************************************************
$ **                                                     **
$ **      HVAC Circulation Loops / Plant Equipment       **
$ **                                                     **
$ *********************************************************

$ ---------------------------------------------------------
$              Pumps
$ ---------------------------------------------------------

"CHW Loop Pump" = PUMP            
   NUMBER           = 1
   MOTOR-CLASS      = PREMIUM
   CAP-CTRL         = VAR-SPEED-PUMP
   ..
"HW Loop Pump" = PUMP            
   NUMBER           = 1
   MOTOR-CLASS      = PREMIUM
   PUMP-KW          = 0.01
   CAP-CTRL         = VAR-SPEED-PUMP
   ..
"CW Loop Pump" = PUMP            
   MOTOR-CLASS      = PREMIUM
   CAP-CTRL         = VAR-SPEED-PUMP
   ..
"Chlr1a (ElCentHerm) Pump" = PUMP            
   MOTOR-CLASS      = HI-EFF
   ..
"Chlr1b (ElCentHerm) Pump" = PUMP            
   MOTOR-CLASS      = HI-EFF
   ..
"IT sub loop pump" = PUMP            
   MOTOR-CLASS      = HI-EFF
   ..


$ ---------------------------------------------------------
$              Heat Exchangers
$ ---------------------------------------------------------



$ ---------------------------------------------------------
$              Circulation Loops
$ ---------------------------------------------------------

"Chilled Water Loop" = CIRCULATION-LOOP
   TYPE             = CHW
   LOOP-DESIGN-DT   = 12
   LOOP-OPERATION   = STANDBY
   DESIGN-COOL-T    = 42
   COOL-SETPT-CTRL  = OA-RESET
   COOL-RESET-SCH   = "Schedule RESET-TEMP CLG"
   LOOP-PUMP        = "CHW Loop Pump"
   ..
"Hot Water Loop" = CIRCULATION-LOOP
   TYPE             = HW
   LOOP-DESIGN-DT   = 50
   LOOP-OPERATION   = STANDBY
   DESIGN-HEAT-T    = 220
   HEAT-SETPT-CTRL  = OA-RESET
   HEAT-RESET-SCH   = "Schedule RESET-TEMP HTG"
   LOOP-PUMP        = "HW Loop Pump"
   ..
"Condenser Water Loop" = CIRCULATION-LOOP
   TYPE             = CW
   LOOP-DESIGN-DT   = 10
   PIPE-HEAD        = 21.6
   COOL-SETPT-CTRL  = FIXED
   COOL-SETPT-T     = 80
   LOOP-SETPT-RNG   = 10
   LOOP-PUMP        = "CW Loop Pump"
   ..
"DHW Plant 1 Loop (1)" = CIRCULATION-LOOP
   TYPE             = DHW
   DESIGN-HEAT-T    = 135
   PROCESS-FLOW     = ( 7.38464 )
   PROCESS-SCH      = ( "DHW Eqp NRes Sch" )
   PROCESS-T        = ( 135 )
   ..
"IT room Chilled water loop" = CIRCULATION-LOOP
   TYPE             = CHW
   SUBTYPE          = SECONDARY
   PRIMARY-LOOP     = "Chilled Water Loop"
   LOOP-PUMP        = "IT sub loop pump"
   ..


$ ---------------------------------------------------------
$              Chillers
$ ---------------------------------------------------------

"Chiller1a (ElCentHerm)" = CHILLER         
   TYPE             = ELEC-OPEN-CENT
   CAPACITY         = 13
   VARIABLE-SPEED   = YES
   ELEC-INPUT-RATIO = 0.1538
   CHW-LOOP         = "Chilled Water Loop"
   CHW-PUMP         = "Chlr1a (ElCentHerm) Pump"
   CONDENSER-TYPE   = WATER-COOLED
   CW-LOOP          = "Condenser Water Loop"
   ..
"Chiller1b (ElCentHerm)" = CHILLER         
   TYPE             = ELEC-OPEN-CENT
   CAPACITY         = 13
   VARIABLE-SPEED   = YES
   ELEC-INPUT-RATIO = 0.1538
   CHW-LOOP         = "Chilled Water Loop"
   CHW-PUMP         = "Chlr1b (ElCentHerm) Pump"
   CONDENSER-TYPE   = WATER-COOLED
   CW-LOOP          = "Condenser Water Loop"
   ..


$ ---------------------------------------------------------
$              Boilers
$ ---------------------------------------------------------



$ ---------------------------------------------------------
$              Domestic Water Heaters
$ ---------------------------------------------------------



$ ---------------------------------------------------------
$              Heat Rejection
$ ---------------------------------------------------------

"Open Tower" = HEAT-REJECTION  
   TYPE             = OPEN-TWR
   NUMBER-OF-CELLS  = 2
   ELEC-INPUT-RATIO = 0.022
   CAPACITY-CTRL    = VARIABLE-SPEED-FAN
   CW-LOOP          = "Condenser Water Loop"
   ..


$ ---------------------------------------------------------
$              Tower Free Cooling
$ ---------------------------------------------------------



$ ---------------------------------------------------------
$              Photovoltaic Modules
$ ---------------------------------------------------------



$ ---------------------------------------------------------
$              Electric Generators
$ ---------------------------------------------------------



$ ---------------------------------------------------------
$              Thermal Storage
$ ---------------------------------------------------------



$ ---------------------------------------------------------
$              Ground Loop Heat Exchangers
$ ---------------------------------------------------------



$ ---------------------------------------------------------
$              Compliance DHW (residential dwelling units)
$ ---------------------------------------------------------



$ *********************************************************
$ **                                                     **
$ **            Steam & Chilled Water Meters             **
$ **                                                     **
$ *********************************************************

$ ---------------------------------------------------------
$              Steam Meters
$ ---------------------------------------------------------

"Steam Meter 1" = STEAM-METER     
   CIRCULATION-LOOP = "Hot Water Loop"
   ..
"Steam Meter 2" = STEAM-METER     
   CIRCULATION-LOOP = "DHW Plant 1 Loop (1)"
   ..


$ ---------------------------------------------------------
$              Chilled Water Meters
$ ---------------------------------------------------------



$ *********************************************************
$ **                                                     **
$ **               HVAC Systems / Zones                  **
$ **                                                     **
$ *********************************************************

"DOAS sys Upper Stack" = SYSTEM          
   TYPE             = VAVS
   HEAT-SOURCE      = HOT-WATER
   BASEBOARD-SOURCE = HOT-WATER
   SIZING-RATIO     = 1.15
   MAX-SUPPLY-T     = 125
   MIN-SUPPLY-T     = 55
   COOL-CONTROL     = WARMEST
   ECONO-LIMIT-T    = 65
   COOL-MAX-RESET-T = 60
   OA-CONTROL       = FIXED
   RECOVER-EXHAUST  = YES
   FAN-SCHEDULE     = "S1 Sys1 (FC) Fan Sch"
   FAN-CONTROL      = FAN-EIR-FPLR
   SUPPLY-KW/FLOW   = 0.000703
   RETURN-KW/FLOW   = 0.000346
   NIGHT-CYCLE-CTRL = CYCLE-ON-ANY
   FAN-EIR-FPLR     = "Static Pressure Reset Sch"
   RETURN-CAP-RATIO = 0.9
   REHEAT-DELTA-T   = 35
   MIN-FLOW/AREA    = 0.4
   HW-VALVE-TYPE    = TWO-WAY
   HW-LOOP          = "Hot Water Loop"
   CHW-VALVE-TYPE   = TWO-WAY
   CHW-LOOP         = "Chilled Water Loop"
   BBRD-LOOP        = "Hot Water Loop"
   COOL-CTRL-RANGE  = 5
   ERV-RECOVER-TYPE = ENTHALPY-WHEEL
   ERV-SENSIBLE-EFF = 0.56
   ERV-LATENT-EFF   = 0.56
   ERV-RUN-CTRL     = OA-EXHAUST-DT
   ERV-TEMP-CTRL    = FIXED-SETPT
   OA-HEAT-SETPT-T  = 70
   OA-COOL-SETPT-T  = 55
   ERV-CAP-CTRL     = BYPASS-OA
   ERV-FAN-EFF      = 0.77
   ERV-MOTOR-CLASS  = PREMIUM
   ERV-OA-STATIC    = 0.5
   ERV-EXH-STATIC   = 0.5
   ..
"Dummy Zn Upper Stack" = ZONE            
   TYPE             = CONDITIONED
   SPACE            = "Dummy Upper Stack"
   ..
"DOAS sys lower stack" = SYSTEM          
   TYPE             = VAVS
   HEAT-SOURCE      = HOT-WATER
   BASEBOARD-SOURCE = HOT-WATER
   SIZING-RATIO     = 1.15
   MAX-SUPPLY-T     = 125
   MIN-SUPPLY-T     = 55
   COOL-CONTROL     = WARMEST
   ECONO-LIMIT-T    = 65
   COOL-MAX-RESET-T = 60
   OA-CONTROL       = FIXED
   RECOVER-EXHAUST  = YES
   FAN-SCHEDULE     = "S1 Sys1 (FC) Fan Sch"
   FAN-CONTROL      = FAN-EIR-FPLR
   SUPPLY-KW/FLOW   = 0.000714
   RETURN-KW/FLOW   = 0.000352
   NIGHT-CYCLE-CTRL = CYCLE-ON-ANY
   FAN-EIR-FPLR     = "Static Pressure Reset Sch"
   RETURN-CAP-RATIO = 0.9
   REHEAT-DELTA-T   = 35
   MIN-FLOW/AREA    = 0.4
   HW-VALVE-TYPE    = TWO-WAY
   HW-LOOP          = "Hot Water Loop"
   CHW-VALVE-TYPE   = TWO-WAY
   CHW-LOOP         = "Chilled Water Loop"
   BBRD-LOOP        = "Hot Water Loop"
   COOL-CTRL-RANGE  = 5
   ERV-RECOVER-TYPE = ENTHALPY-WHEEL
   ERV-SENSIBLE-EFF = 0.56
   ERV-LATENT-EFF   = 0.56
   ERV-RUN-CTRL     = OA-EXHAUST-DT
   ERV-TEMP-CTRL    = FIXED-SETPT
   OA-HEAT-SETPT-T  = 70
   OA-COOL-SETPT-T  = 55
   ERV-CAP-CTRL     = BYPASS-OA
   ERV-FAN-EFF      = 0.77
   ERV-MOTOR-CLASS  = PREMIUM
   ERV-OA-STATIC    = 0.5
   ERV-EXH-STATIC   = 0.5
   ..
"Dummy Zn Lower Stack" = ZONE            
   TYPE             = CONDITIONED
   SPACE            = "Dummy Lower Stack"
   ..
"Lower stack core VAV" = SYSTEM          
   TYPE             = VAVS
   HEAT-SOURCE      = HOT-WATER
   BASEBOARD-SOURCE = HOT-WATER
   SIZING-RATIO     = 1.15
   MAX-SUPPLY-T     = 125
   MIN-SUPPLY-T     = 55
   COOL-CONTROL     = WARMEST
   ECONO-LIMIT-T    = 65
   MIN-OA-METHOD    = DCV-RETURN-SENSOR
   COOL-MAX-RESET-T = 60
   OA-CONTROL       = FIXED
   FAN-SCHEDULE     = "S1 Sys1 (FC) Fan Sch"
   FAN-CONTROL      = FAN-EIR-FPLR
   SUPPLY-KW/FLOW   = 0.000961
   RETURN-KW/FLOW   = 0.0004
   NIGHT-CYCLE-CTRL = CYCLE-ON-ANY
   FAN-EIR-FPLR     = "Static Pressure Reset Sch"
   RETURN-CAP-RATIO = 0.9
   REHEAT-DELTA-T   = 35
   MIN-FLOW/AREA    = 0.4
   HW-VALVE-TYPE    = TWO-WAY
   HW-LOOP          = "Hot Water Loop"
   CHW-VALVE-TYPE   = TWO-WAY
   CHW-LOOP         = "Chilled Water Loop"
   BBRD-LOOP        = "Hot Water Loop"
   COOL-CTRL-RANGE  = 5
   OA-FROM-SYSTEM   = "DOAS sys lower stack"
   ..
"EL1 Core Zn (M.C15)" = ZONE            
   TYPE             = CONDITIONED
   FLOW/AREA        = 0.5
   OA-FLOW/PER      = 57.25
   MIN-FLOW/AREA    = 0.4
   DESIGN-HEAT-T    = 72
   HEAT-TEMP-SCH    = "S1 Sys1 (FC) Heat Sch"
   DESIGN-COOL-T    = 76
   COOL-TEMP-SCH    = "S1 Sys1 (FC) Cool Sch"
   THROTTLING-RANGE = 4
   SIZING-OPTION    = ADJUST-LOADS
   SPACE            = "EL1 Core Spc (M.C15)"
   ..
"Upper stack core VAV" = SYSTEM          
   TYPE             = VAVS
   HEAT-SOURCE      = HOT-WATER
   BASEBOARD-SOURCE = HOT-WATER
   SIZING-RATIO     = 1.15
   MAX-SUPPLY-T     = 125
   MIN-SUPPLY-T     = 55
   COOL-CONTROL     = WARMEST
   ECONO-LIMIT-T    = 65
   MIN-OA-METHOD    = DCV-RETURN-SENSOR
   COOL-MAX-RESET-T = 60
   OA-CONTROL       = FIXED
   FAN-SCHEDULE     = "S1 Sys1 (FC) Fan Sch"
   FAN-CONTROL      = FAN-EIR-FPLR
   SUPPLY-EFF       = 0.33
   SUPPLY-KW/FLOW   = 0.000961
   RETURN-KW/FLOW   = 0.0004
   NIGHT-CYCLE-CTRL = CYCLE-ON-ANY
   FAN-EIR-FPLR     = "Static Pressure Reset Sch"
   RETURN-CAP-RATIO = 0.9
   REHEAT-DELTA-T   = 35
   MIN-FLOW/AREA    = 0.4
   HW-VALVE-TYPE    = TWO-WAY
   HW-LOOP          = "Hot Water Loop"
   CHW-VALVE-TYPE   = TWO-WAY
   CHW-LOOP         = "Chilled Water Loop"
   BBRD-LOOP        = "Hot Water Loop"
   COOL-CTRL-RANGE  = 5
   OA-FROM-SYSTEM   = "DOAS sys Upper Stack"
   ..
"Thermal Zone 25" = ZONE            
   TYPE             = CONDITIONED
   FLOW/AREA        = 0.5
   OA-FLOW/PER      = 57.25
   MIN-FLOW/AREA    = 0.4
   DESIGN-HEAT-T    = 72
   HEAT-TEMP-SCH    = "S1 Sys1 (FC) Heat Sch"
   DESIGN-COOL-T    = 76
   COOL-TEMP-SCH    = "S1 Sys1 (FC) Cool Sch"
   THROTTLING-RANGE = 4
   SIZING-OPTION    = ADJUST-LOADS
   SPACE            = "Space 25"
   ..
"Basement AHU VAV" = SYSTEM          
   TYPE             = VAVS
   HEAT-SOURCE      = HOT-WATER
   BASEBOARD-SOURCE = HOT-WATER
   SIZING-RATIO     = 1.15
   MAX-SUPPLY-T     = 125
   MIN-SUPPLY-T     = 55
   COOL-CONTROL     = WARMEST
   ECONO-LIMIT-T    = 65
   MIN-OA-METHOD    = DCV-RETURN-SENSOR
   COOL-MAX-RESET-T = 60
   OA-CONTROL       = FIXED
   FAN-SCHEDULE     = "S1 Sys1 (FC) Fan Sch"
   FAN-CONTROL      = FAN-EIR-FPLR
   SUPPLY-KW/FLOW   = 0.000961
   RETURN-KW/FLOW   = 0.0004
   MIN-FAN-RATIO    = 0.4
   NIGHT-CYCLE-CTRL = CYCLE-ON-ANY
   FAN-EIR-FPLR     = "Static Pressure Reset Sch"
   RETURN-CAP-RATIO = 0.9
   REHEAT-DELTA-T   = 35
   MIN-FLOW/AREA    = 0.4
   HW-VALVE-TYPE    = TWO-WAY
   HW-LOOP          = "Hot Water Loop"
   CHW-VALVE-TYPE   = TWO-WAY
   CHW-LOOP         = "Chilled Water Loop"
   BBRD-LOOP        = "Hot Water Loop"
   COOL-CTRL-RANGE  = 5
   OA-FROM-SYSTEM   = "DOAS sys lower stack"
   ..
"EL1 Core Zn (B.C5)" = ZONE            
   TYPE             = CONDITIONED
   FLOW/AREA        = 0.5
   OA-FLOW/PER      = 57.25
   MIN-FLOW/AREA    = 0.4
   DESIGN-HEAT-T    = 72
   HEAT-TEMP-SCH    = "S1 Sys1 (FC) Heat Sch"
   DESIGN-COOL-T    = 76
   COOL-TEMP-SCH    = "S1 Sys1 (FC) Cool Sch"
   THROTTLING-RANGE = 4
   SIZING-OPTION    = ADJUST-LOADS
   SPACE            = "EL1 Core Spc (B.C5)"
   ..
"EL1 South Perim Zn (B.S1)" = ZONE            
   TYPE             = CONDITIONED
   FLOW/AREA        = 0.5
   OA-FLOW/PER      = 57.25
   MIN-FLOW/AREA    = 0.4
   DESIGN-HEAT-T    = 72
   HEAT-TEMP-SCH    = "S1 Sys1 (FC) Heat Sch"
   DESIGN-COOL-T    = 76
   COOL-TEMP-SCH    = "S1 Sys1 (FC) Cool Sch"
   THROTTLING-RANGE = 4
   SIZING-OPTION    = ADJUST-LOADS
   SPACE            = "EL1 South Perim Spc (B.S1)"
   ..
"EL1 East Perim Zn (B.E2)" = ZONE            
   TYPE             = CONDITIONED
   FLOW/AREA        = 0.5
   OA-FLOW/PER      = 57.25
   MIN-FLOW/AREA    = 0.4
   DESIGN-HEAT-T    = 72
   HEAT-TEMP-SCH    = "S1 Sys1 (FC) Heat Sch"
   DESIGN-COOL-T    = 76
   COOL-TEMP-SCH    = "S1 Sys1 (FC) Cool Sch"
   THROTTLING-RANGE = 4
   SIZING-OPTION    = ADJUST-LOADS
   SPACE            = "EL1 East Perim Spc (B.E2)"
   ..
"EL1 North Perim Zn (B.N3)" = ZONE            
   TYPE             = CONDITIONED
   FLOW/AREA        = 0.5
   OA-FLOW/PER      = 57.25
   MIN-FLOW/AREA    = 0.4
   DESIGN-HEAT-T    = 72
   HEAT-TEMP-SCH    = "S1 Sys1 (FC) Heat Sch"
   DESIGN-COOL-T    = 76
   COOL-TEMP-SCH    = "S1 Sys1 (FC) Cool Sch"
   THROTTLING-RANGE = 4
   SIZING-OPTION    = ADJUST-LOADS
   SPACE            = "EL1 North Perim Spc (B.N3)"
   ..
"EL1 West Perim Zn (B.W4)" = ZONE            
   TYPE             = UNCONDITIONED
   DESIGN-HEAT-T    = 72
   DESIGN-COOL-T    = 76
   SIZING-OPTION    = ADJUST-LOADS
   SPACE            = "EL1 West Perim Spc (B.W4)"
   ..
"Lobby AHU VAV" = SYSTEM          
   TYPE             = VAVS
   HEAT-SOURCE      = HOT-WATER
   BASEBOARD-SOURCE = HOT-WATER
   SIZING-RATIO     = 1.15
   MAX-SUPPLY-T     = 125
   MIN-SUPPLY-T     = 55
   COOL-CONTROL     = WARMEST
   ECONO-LIMIT-T    = 65
   MIN-OA-METHOD    = DCV-RETURN-SENSOR
   COOL-MAX-RESET-T = 60
   SUPPLY-FLOW      = 17579
   OA-CONTROL       = FIXED
   FAN-SCHEDULE     = "S1 Sys1 (FC) Fan Sch"
   FAN-CONTROL      = FAN-EIR-FPLR
   SUPPLY-KW/FLOW   = 0.000961
   RETURN-KW/FLOW   = 0.0004
   MIN-FAN-RATIO    = 0.4
   NIGHT-CYCLE-CTRL = CYCLE-ON-ANY
   FAN-EIR-FPLR     = "Static Pressure Reset Sch"
   RETURN-CAP-RATIO = 0.9
   REHEAT-DELTA-T   = 35
   MIN-FLOW/AREA    = 0.4
   HW-VALVE-TYPE    = TWO-WAY
   HW-LOOP          = "Hot Water Loop"
   CHW-VALVE-TYPE   = TWO-WAY
   CHW-LOOP         = "Chilled Water Loop"
   BBRD-LOOP        = "Hot Water Loop"
   COOL-CTRL-RANGE  = 5
   OA-FROM-SYSTEM   = "DOAS sys Upper Stack"
   ..
"EL1 Core Zn (G.C10)" = ZONE            
   TYPE             = CONDITIONED
   FLOW/AREA        = 0.5
   OA-FLOW/PER      = 57.25
   MIN-FLOW/AREA    = 0.4
   DESIGN-HEAT-T    = 72
   HEAT-TEMP-SCH    = "S1 Sys1 (FC) Heat Sch"
   DESIGN-COOL-T    = 76
   COOL-TEMP-SCH    = "S1 Sys1 (FC) Cool Sch"
   THROTTLING-RANGE = 4
   SIZING-OPTION    = ADJUST-LOADS
   SPACE            = "EL1 Core Spc (G.C10)"
   ..
"EL1 South Perim Zn (G.S6)" = ZONE            
   TYPE             = CONDITIONED
   BASEBOARD-RATING = -68445
   FLOW/AREA        = 0.5
   OA-FLOW/PER      = 57.25
   MIN-FLOW/AREA    = 0.4
   DESIGN-HEAT-T    = 72
   HEAT-TEMP-SCH    = "S1 Sys1 (FC) Heat Sch"
   DESIGN-COOL-T    = 76
   COOL-TEMP-SCH    = "S1 Sys1 (FC) Cool Sch"
   BASEBOARD-CTRL   = THERMOSTATIC
   THROTTLING-RANGE = 4
   SIZING-OPTION    = ADJUST-LOADS
   SPACE            = "EL1 South Perim Spc (G.S6)"
   ..
"EL1 East Perim Zn (G.E7)" = ZONE            
   TYPE             = CONDITIONED
   BASEBOARD-RATING = -45514
   FLOW/AREA        = 0.5
   OA-FLOW/PER      = 57.25
   MIN-FLOW/AREA    = 0.4
   DESIGN-HEAT-T    = 72
   HEAT-TEMP-SCH    = "S1 Sys1 (FC) Heat Sch"
   DESIGN-COOL-T    = 76
   COOL-TEMP-SCH    = "S1 Sys1 (FC) Cool Sch"
   BASEBOARD-CTRL   = THERMOSTATIC
   THROTTLING-RANGE = 4
   SIZING-OPTION    = ADJUST-LOADS
   SPACE            = "EL1 East Perim Spc (G.E7)"
   ..
"EL1 North Perim Zn (G.N8)" = ZONE            
   TYPE             = CONDITIONED
   BASEBOARD-RATING = -68445
   FLOW/AREA        = 0.5
   OA-FLOW/PER      = 57.25
   MIN-FLOW/AREA    = 0.4
   DESIGN-HEAT-T    = 72
   HEAT-TEMP-SCH    = "S1 Sys1 (FC) Heat Sch"
   DESIGN-COOL-T    = 76
   COOL-TEMP-SCH    = "S1 Sys1 (FC) Cool Sch"
   BASEBOARD-CTRL   = THERMOSTATIC
   THROTTLING-RANGE = 4
   SIZING-OPTION    = ADJUST-LOADS
   SPACE            = "EL1 North Perim Spc (G.N8)"
   ..
"EL1 West Perim Zn (G.W9)" = ZONE            
   TYPE             = CONDITIONED
   BASEBOARD-RATING = -45514
   FLOW/AREA        = 0.5
   OA-FLOW/PER      = 57.25
   MIN-FLOW/AREA    = 0.4
   DESIGN-HEAT-T    = 72
   HEAT-TEMP-SCH    = "S1 Sys1 (FC) Heat Sch"
   DESIGN-COOL-T    = 76
   COOL-TEMP-SCH    = "S1 Sys1 (FC) Cool Sch"
   BASEBOARD-CTRL   = THERMOSTATIC
   THROTTLING-RANGE = 4
   SIZING-OPTION    = ADJUST-LOADS
   SPACE            = "EL1 West Perim Spc (G.W9)"
   ..
"IT room system" = SYSTEM          
   TYPE             = VAVS
   HEAT-SOURCE      = HOT-WATER
   BASEBOARD-SOURCE = HOT-WATER
   SIZING-RATIO     = 1.15
   MAX-SUPPLY-T     = 125
   MIN-SUPPLY-T     = 55
   COOL-CONTROL     = WARMEST
   ECONO-LIMIT-T    = 65
   MIN-OA-METHOD    = DCV-RETURN-SENSOR
   COOL-MAX-RESET-T = 60
   OA-CONTROL       = FIXED
   FAN-SCHEDULE     = "S1 Sys1 (FC) Fan Sch"
   FAN-CONTROL      = FAN-EIR-FPLR
   SUPPLY-EFF       = 0.33
   SUPPLY-KW/FLOW   = 0.000961
   RETURN-KW/FLOW   = 0.0004
   MIN-FAN-RATIO    = 1
   NIGHT-CYCLE-CTRL = CYCLE-ON-ANY
   FAN-EIR-FPLR     = "Static Pressure Reset Sch"
   RETURN-CAP-RATIO = 0.9
   REHEAT-DELTA-T   = 35
   MIN-FLOW-RATIO   = 1
   HMIN-FLOW-RATIO  = 1
   HW-VALVE-TYPE    = TWO-WAY
   HW-LOOP          = "Hot Water Loop"
   CHW-VALVE-TYPE   = TWO-WAY
   CHW-LOOP         = "IT room Chilled water loop"
   BBRD-LOOP        = "Hot Water Loop"
   COOL-CTRL-RANGE  = 5
   OA-FROM-SYSTEM   = "DOAS sys Upper Stack"
   ..
"EL1 Core Zn (T.C20)" = ZONE            
   TYPE             = CONDITIONED
   FLOW/AREA        = 0.5
   OA-FLOW/PER      = 57.25
   DESIGN-HEAT-T    = 72
   HEAT-TEMP-SCH    = "S1 Sys1 (FC) Heat Sch"
   DESIGN-COOL-T    = 76
   COOL-TEMP-SCH    = "S1 Sys1 (FC) Cool Sch"
   THROTTLING-RANGE = 4
   SIZING-OPTION    = ADJUST-LOADS
   SPACE            = "EL1 Core Spc (T.C20)"
   ..
"Lower stack perim VAV" = SYSTEM          
   TYPE             = VAVS
   HEAT-SOURCE      = HOT-WATER
   BASEBOARD-SOURCE = HOT-WATER
   SIZING-RATIO     = 1.15
   MAX-SUPPLY-T     = 125
   MIN-SUPPLY-T     = 55
   COOL-CONTROL     = WARMEST
   ECONO-LIMIT-T    = 65
   MIN-OA-METHOD    = DCV-RETURN-SENSOR
   COOL-MAX-RESET-T = 60
   OA-CONTROL       = FIXED
   FAN-SCHEDULE     = "S1 Sys1 (FC) Fan Sch"
   FAN-CONTROL      = FAN-EIR-FPLR
   SUPPLY-KW/FLOW   = 0.000961
   RETURN-KW/FLOW   = 0.0004
   NIGHT-CYCLE-CTRL = CYCLE-ON-ANY
   FAN-EIR-FPLR     = "Static Pressure Reset Sch"
   RETURN-CAP-RATIO = 0.9
   REHEAT-DELTA-T   = 35
   MIN-FLOW/AREA    = 0.4
   HW-VALVE-TYPE    = TWO-WAY
   HW-LOOP          = "Hot Water Loop"
   CHW-VALVE-TYPE   = TWO-WAY
   CHW-LOOP         = "Chilled Water Loop"
   BBRD-LOOP        = "Hot Water Loop"
   COOL-CTRL-RANGE  = 5
   OA-FROM-SYSTEM   = "DOAS sys lower stack"
   ..
"EL1 South Perim Zn (M.S11)" = ZONE            
   TYPE             = CONDITIONED
   BASEBOARD-RATING = -68445
   FLOW/AREA        = 0.5
   OA-FLOW/PER      = 57.25
   DESIGN-HEAT-T    = 69
   HEAT-TEMP-SCH    = "S1 Sys1 (FC) Heat Sch"
   DESIGN-COOL-T    = 75
   COOL-TEMP-SCH    = "S1 Sys1 (FC) Cool Sch"
   BASEBOARD-CTRL   = THERMOSTATIC
   THROTTLING-RANGE = 4
   SIZING-OPTION    = ADJUST-LOADS
   SPACE            = "EL1 South Perim Spc (M.S11)"
   ..
"EL1 East Perim Zn (M.E12)" = ZONE            
   TYPE             = CONDITIONED
   BASEBOARD-RATING = -45514
   FLOW/AREA        = 0.5
   OA-FLOW/PER      = 57.25
   DESIGN-HEAT-T    = 69
   HEAT-TEMP-SCH    = "S1 Sys1 (FC) Heat Sch"
   DESIGN-COOL-T    = 75
   COOL-TEMP-SCH    = "S1 Sys1 (FC) Cool Sch"
   BASEBOARD-CTRL   = THERMOSTATIC
   THROTTLING-RANGE = 4
   SIZING-OPTION    = ADJUST-LOADS
   SPACE            = "EL1 East Perim Spc (M.E12)"
   ..
"EL1 West Perim Zn (M.W14)" = ZONE            
   TYPE             = CONDITIONED
   BASEBOARD-RATING = -45514
   FLOW/AREA        = 0.5
   OA-FLOW/PER      = 57.25
   DESIGN-HEAT-T    = 69
   HEAT-TEMP-SCH    = "S1 Sys1 (FC) Heat Sch"
   DESIGN-COOL-T    = 75
   COOL-TEMP-SCH    = "S1 Sys1 (FC) Cool Sch"
   BASEBOARD-CTRL   = THERMOSTATIC
   THROTTLING-RANGE = 4
   SIZING-OPTION    = ADJUST-LOADS
   SPACE            = "EL1 West Perim Spc (M.W14)"
   ..
"EL1 North Perim Zn (M.N13)" = ZONE            
   TYPE             = CONDITIONED
   BASEBOARD-RATING = -68445
   FLOW/AREA        = 0.5
   OA-FLOW/PER      = 57.25
   DESIGN-HEAT-T    = 69
   HEAT-TEMP-SCH    = "S1 Sys1 (FC) Heat Sch"
   DESIGN-COOL-T    = 75
   COOL-TEMP-SCH    = "S1 Sys1 (FC) Cool Sch"
   BASEBOARD-CTRL   = THERMOSTATIC
   THROTTLING-RANGE = 4
   SIZING-OPTION    = ADJUST-LOADS
   SPACE            = "EL1 North Perim Spc (M.N13)"
   ..
"Upper stack VAV" = SYSTEM          
   TYPE             = VAVS
   HEAT-SOURCE      = HOT-WATER
   BASEBOARD-SOURCE = HOT-WATER
   SIZING-RATIO     = 1.15
   MAX-SUPPLY-T     = 125
   MIN-SUPPLY-T     = 55
   COOL-CONTROL     = WARMEST
   ECONO-LIMIT-T    = 65
   MIN-OA-METHOD    = DCV-RETURN-SENSOR
   COOL-MAX-RESET-T = 60
   OA-CONTROL       = FIXED
   FAN-SCHEDULE     = "S1 Sys1 (FC) Fan Sch"
   FAN-CONTROL      = FAN-EIR-FPLR
   SUPPLY-EFF       = 0.33
   SUPPLY-KW/FLOW   = 0.000961
   RETURN-KW/FLOW   = 0.0004
   NIGHT-CYCLE-CTRL = CYCLE-ON-ANY
   FAN-EIR-FPLR     = "Static Pressure Reset Sch"
   RETURN-CAP-RATIO = 0.9
   REHEAT-DELTA-T   = 35
   MIN-FLOW/AREA    = 0.4
   HW-VALVE-TYPE    = TWO-WAY
   HW-LOOP          = "Hot Water Loop"
   CHW-VALVE-TYPE   = TWO-WAY
   CHW-LOOP         = "Chilled Water Loop"
   BBRD-LOOP        = "Hot Water Loop"
   COOL-CTRL-RANGE  = 5
   OA-FROM-SYSTEM   = "DOAS sys Upper Stack"
   ..
"Thermal Zone 22" = ZONE            
   TYPE             = CONDITIONED
   BASEBOARD-RATING = -45514
   FLOW/AREA        = 0.5
   OA-FLOW/PER      = 57.25
   DESIGN-HEAT-T    = 69
   HEAT-TEMP-SCH    = "S1 Sys1 (FC) Heat Sch"
   DESIGN-COOL-T    = 75
   COOL-TEMP-SCH    = "S1 Sys1 (FC) Cool Sch"
   BASEBOARD-CTRL   = THERMOSTATIC
   THROTTLING-RANGE = 4
   SIZING-OPTION    = ADJUST-LOADS
   SPACE            = "Space 22"
   ..
"EL1 South Perim Zn (T.S16)" = ZONE            
   TYPE             = CONDITIONED
   BASEBOARD-RATING = -68445
   FLOW/AREA        = 0.5
   OA-FLOW/PER      = 57.25
   DESIGN-HEAT-T    = 69
   HEAT-TEMP-SCH    = "S1 Sys1 (FC) Heat Sch"
   DESIGN-COOL-T    = 75
   COOL-TEMP-SCH    = "S1 Sys1 (FC) Cool Sch"
   BASEBOARD-CTRL   = THERMOSTATIC
   THROTTLING-RANGE = 4
   SIZING-OPTION    = ADJUST-LOADS
   SPACE            = "EL1 South Perim Spc (T.S16)"
   ..
"EL1 East Perim Zn (T.E17)" = ZONE            
   TYPE             = CONDITIONED
   BASEBOARD-RATING = -45514
   FLOW/AREA        = 0.5
   OA-FLOW/PER      = 57.25
   DESIGN-HEAT-T    = 69
   HEAT-TEMP-SCH    = "S1 Sys1 (FC) Heat Sch"
   DESIGN-COOL-T    = 75
   COOL-TEMP-SCH    = "S1 Sys1 (FC) Cool Sch"
   BASEBOARD-CTRL   = THERMOSTATIC
   THROTTLING-RANGE = 4
   SIZING-OPTION    = ADJUST-LOADS
   SPACE            = "EL1 East Perim Spc (T.E17)"
   ..
"EL1 North Perim Zn (T.N18)" = ZONE            
   TYPE             = CONDITIONED
   BASEBOARD-RATING = -68445
   FLOW/AREA        = 0.5
   OA-FLOW/PER      = 57.25
   DESIGN-HEAT-T    = 69
   HEAT-TEMP-SCH    = "S1 Sys1 (FC) Heat Sch"
   DESIGN-COOL-T    = 75
   COOL-TEMP-SCH    = "S1 Sys1 (FC) Cool Sch"
   BASEBOARD-CTRL   = THERMOSTATIC
   THROTTLING-RANGE = 4
   SIZING-OPTION    = ADJUST-LOADS
   SPACE            = "EL1 North Perim Spc (T.N18)"
   ..
"EL1 West Perim Zn (T.W19)" = ZONE            
   TYPE             = CONDITIONED
   BASEBOARD-RATING = -45514
   FLOW/AREA        = 0.5
   OA-FLOW/PER      = 57.25
   DESIGN-HEAT-T    = 69
   HEAT-TEMP-SCH    = "S1 Sys1 (FC) Heat Sch"
   DESIGN-COOL-T    = 75
   COOL-TEMP-SCH    = "S1 Sys1 (FC) Cool Sch"
   BASEBOARD-CTRL   = THERMOSTATIC
   THROTTLING-RANGE = 4
   SIZING-OPTION    = ADJUST-LOADS
   SPACE            = "EL1 West Perim Spc (T.W19)"
   ..
"Thermal Zone 21" = ZONE            
   TYPE             = CONDITIONED
   BASEBOARD-RATING = -68445
   FLOW/AREA        = 0.5
   OA-FLOW/PER      = 57.25
   DESIGN-HEAT-T    = 69
   HEAT-TEMP-SCH    = "S1 Sys1 (FC) Heat Sch"
   DESIGN-COOL-T    = 75
   COOL-TEMP-SCH    = "S1 Sys1 (FC) Cool Sch"
   BASEBOARD-CTRL   = THERMOSTATIC
   THROTTLING-RANGE = 4
   SIZING-OPTION    = ADJUST-LOADS
   SPACE            = "Space 21"
   ..
"Thermal Zone 23" = ZONE            
   TYPE             = CONDITIONED
   BASEBOARD-RATING = -68445
   FLOW/AREA        = 0.5
   OA-FLOW/PER      = 57.25
   DESIGN-HEAT-T    = 69
   HEAT-TEMP-SCH    = "S1 Sys1 (FC) Heat Sch"
   DESIGN-COOL-T    = 75
   COOL-TEMP-SCH    = "S1 Sys1 (FC) Cool Sch"
   BASEBOARD-CTRL   = THERMOSTATIC
   THROTTLING-RANGE = 4
   SIZING-OPTION    = ADJUST-LOADS
   SPACE            = "Space 23"
   ..
"Thermal Zone 24" = ZONE            
   TYPE             = CONDITIONED
   BASEBOARD-RATING = -45514
   FLOW/AREA        = 0.5
   OA-FLOW/PER      = 57.25
   DESIGN-HEAT-T    = 69
   HEAT-TEMP-SCH    = "S1 Sys1 (FC) Heat Sch"
   DESIGN-COOL-T    = 75
   COOL-TEMP-SCH    = "S1 Sys1 (FC) Cool Sch"
   BASEBOARD-CTRL   = THERMOSTATIC
   THROTTLING-RANGE = 4
   SIZING-OPTION    = ADJUST-LOADS
   SPACE            = "Space 24"
   ..


$ *********************************************************
$ **                                                     **
$ **                Metering & Misc HVAC                 **
$ **                                                     **
$ *********************************************************

$ ---------------------------------------------------------
$              Equipment Controls
$ ---------------------------------------------------------



$ ---------------------------------------------------------
$              Load Management
$ ---------------------------------------------------------



$ *********************************************************
$ **                                                     **
$ **                    Utility Rates                    **
$ **                                                     **
$ *********************************************************

$ ---------------------------------------------------------
$              Ratchets
$ ---------------------------------------------------------



$ ---------------------------------------------------------
$              Block Charges
$ ---------------------------------------------------------



$ ---------------------------------------------------------
$              Utility Rates
$ ---------------------------------------------------------

"ConEd LgGen SC-9 Non-TOU LT Elec" = UTILITY-RATE    
   LIBRARY-ENTRY "ConEd LgGen SC-9 Non-TOU LT Elec"
   ..
"ConEd Gen SC-2 Heating Gas" = UTILITY-RATE    
   LIBRARY-ENTRY "ConEd Gen SC-2 Heating Gas"
   ..


$ *********************************************************
$ **                                                     **
$ **                 Output Reporting                    **
$ **                                                     **
$ *********************************************************

$ ---------------------------------------------------------
$              Loads Non-Hourly Reporting
$ ---------------------------------------------------------

LOADS-REPORT    
   VERIFICATION     = ( ALL-VERIFICATION )
   SUMMARY          = ( ALL-SUMMARY )
   ..


$ ---------------------------------------------------------
$              Systems Non-Hourly Reporting
$ ---------------------------------------------------------

SYSTEMS-REPORT  
   VERIFICATION     = ( ALL-VERIFICATION )
   SUMMARY          = ( ALL-SUMMARY )
   ..


$ ---------------------------------------------------------
$              Plant Non-Hourly Reporting
$ ---------------------------------------------------------

PLANT-REPORT    
   VERIFICATION     = ( ALL-VERIFICATION )
   SUMMARY          = ( ALL-SUMMARY )
   ..


$ ---------------------------------------------------------
$              Economics Non-Hourly Reporting
$ ---------------------------------------------------------

ECONOMICS-REPORT
   VERIFICATION     = ( ALL-VERIFICATION )
   SUMMARY          = ( ALL-SUMMARY )
   ..


$ ---------------------------------------------------------
$              Hourly Reporting
$ ---------------------------------------------------------


"Hourly Report" = HOURLY-REPORT   
   LIBRARY-ENTRY "Hourly Report"
   ..


$ ---------------------------------------------------------
$              THE END
$ ---------------------------------------------------------

END ..
COMPUTE ..
STOP ..
-------------- next part --------------
Proj   "Comm very large"  
   ProgramVersion = "eQUEST 3.64.7130"
   BDBaseVersion = 24
   ProductCode = "eQUEST"
   WeatherFile = "TMY2\NEW-YONY.bin"
   CreateDate = 1441396740
   ModDate = 1454597365
   RunDate = 1454597268
   LibraryFile = "eQ_Lib.dat"
   ActiveMode = 0
   InputModule = 4
   UseCameraData = 1
   ClippingRange = ( 342.729, 1139.49 )
   FocalPoint = ( 92, 63.75, 135.029 )
   Position = ( 706.419, 363.423, 258.822 )
   ViewUpVector = ( 0, 0, 1 )
   ViewAngle = 30
   InterfaceMode = 1
   AllowWizard = 1
   NotProjFile = "Comm very large"
   InputUnitsType = "English"
   OutputUnitsType = "English"
   PreviousName = "Comm very large"
   DetailedModelEdits = 1
   ProjTreeType[2] = 1
   ProjTreeType[3] = 1
   ProjTreeType[4] = 1
   ProjTreeType[5] = 1
   ProjTreeType[6] = 1
   ProjTreeID[2] = 10410001
   ProjTreeID[3] = 10080009
   ProjTreeID[4] = 10770001
   ProjTreeID[5] = 10480001
   ProjTreeID[6] = 10750000
   ProjTreeLabel[2] = "EL1 Ground Flr"
   ProjTreeLabel[3] = "EL1 North Perim Spc (G.N8)"
   ProjTreeLabel[4] = "Steam Meter 2"
   ProjTreeLabel[5] = "DOAS sys lower stack"
   ProjTreeLabel[6] = "EM1"
   ..

MainWiz   "Comm very large"  
   ProductCode = "eQUEST"
   WizardType = "Design Development"
   DebugID = 0
   AllowCustWinDoor = 1
   ScreenIDArrIdx = 6
   ScreenIDArrID = 250
   Coverage = "All eQUEST Locations"
   State = "New York"
   Location = "New York"
   GasUtility = "ConEd (NY)"
   BldgType = "Office Bldg, High-Rise"
   ..

ShellWiz   "Bldg Envelope & Loads 1"  
   ModelEnduse[2] = 0
   ModelEnduse[3] = 0
   ModelEnduse[4] = 0
   ModelEnduse[11] = 1
   ScreenIDArrIdx = 2
   ScreenIDArrID = 30
   BldgType = "Office Bldg, High-Rise"
   GrossArea = 750000
   FlrsAboveGrade = 32
   FlrsBelowGrade = 1
   X[1] = 184
   Y[1] = 127.38
   FlrToFlr = 9
   FlrToCeiling = 9
   NumMCZnGrps = 0
   UseFloorMults = 1
   DiagLink = "Bldg Envelope & Loads 1 Diag Data"
   RoofBrdInsType = "2 in. polyisocyanurate (R-14)"
   VertExtBrdInsType = "- no ext board insulation -"
   VertExtSecInsType = "R-13 batt"
   VertUndConsType = "12 in. Concrete"
   PerimInfMethod = "ACH (air changes per hour)"
   CoreInfMethod = "ACH (air changes per hour)"
   PerimInfil = 0.6
   CoreInfil = 0.4
   ZoningCurrent = 1
   AdiabaticCurrent = 1
   ZoneGroupsOK = 1
   DfltZnGrpName = ( "EL1 Underground Areas", "EL1 Ground Floor Core", 
                     "EL1 Ground Floor Perimeter", 
                     "EL1 Typical Floor(s) Core", 
                     "EL1 Typical Floor(s) Perimeter", 
                     "EL1 Top Floor Core", "EL1 Top Floor Perimeter" )
   CustomRoofZoning = -1
   LastFootprint = 1
   LastX[1] = 184
   LastY[1] = 127.38
   GTCCategory[1] = "- specify properties -"
   GTCCategory[2] = "- select another -"
   WindowHeight[1] = 8
   WinSillHeight[1] = 0.5
   PercentGlass1[1] = 75
   PercentGlass2[1] = 75
   PercentGlass3[1] = 75
   PercentGlass4[1] = 75
   GP_ProductType[1] = "Fixed Window"
   GP_GasFill[1] = "Air"
   GP_LowECoating[1] = "none"
   GP_Ufactor[1] = 0.79
   GP_SHGC[1] = 0.68
   GP_BDLVisualTrans[1] = 0.67
   SkyZonesCurrent = 1
   SkyltZones[1] = 1
   SkyltZones[2] = 1
   SkyltZones[3] = 1
   SkyltZones[4] = 1
   SkyltZones[5] = 1
   SkyPosCurrent = 1
   DayZonesCurrent = ( 1, 1, 1 )
   DayltZones[1] = 1
   DayltZones[2] = 1
   DayltZones[3] = 1
   DayltZones[4] = 1
   DayltZones[5] = 0
   DayltZones[201] = 1
   DayltZones[202] = 1
   DayltZones[203] = 1
   DayltZones[204] = 1
   DayltZones[205] = 0
   DayltZones[401] = 1
   DayltZones[402] = 1
   DayltZones[403] = 1
   DayltZones[404] = 1
   DayltZones[405] = 0
   WinDoorCurrent = 1
   DetailsCurrent = ( 1, 1, 1 )
   BDLNumDayltCtrls[1] = 0
   BDLNumDayltCtrls[2] = 0
   BDLNumDayltCtrls[3] = 0
   BDLNumDayltCtrls[4] = 0
   BDLNumDayltCtrls[5] = 0
   BDLNumDayltCtrls[201] = 0
   BDLNumDayltCtrls[202] = 0
   BDLNumDayltCtrls[203] = 0
   BDLNumDayltCtrls[204] = 0
   BDLNumDayltCtrls[205] = 0
   BDLNumDayltCtrls[401] = 0
   BDLNumDayltCtrls[402] = 0
   BDLNumDayltCtrls[403] = 0
   BDLNumDayltCtrls[404] = 0
   BDLNumDayltCtrls[405] = 0
   OccShape[1] = "EL1 Occup Profile (S1)"
   ILShape[1] = "EL1 InsLtg Profile (S1)"
   ILElecIntens[1] = 1.2
   ILElecIntens[2] = 1.2
   ILElecIntens[3] = 1.2
   ILElecIntens[4] = 1.2
   ILElecIntens[5] = 1.2
   ILElecIntens[6] = 1.2
   ILElecIntens[7] = 1.2
   ILElecIntens[8] = 1.2
   ELDayShapes = ( "EL1 ExtLtg DayShape (Jan)", 
                   "EL1 ExtLtg DayShape (Feb)", 
                   "EL1 ExtLtg DayShape (Mar)", 
                   "EL1 ExtLtg DayShape (Apr)", 
                   "EL1 ExtLtg DayShape (May)", 
                   "EL1 ExtLtg DayShape (Jun)", 
                   "EL1 ExtLtg DayShape (Jul)", 
                   "EL1 ExtLtg DayShape (Aug)", 
                   "EL1 ExtLtg DayShape (Sep)", 
                   "EL1 ExtLtg DayShape (Oct)", 
                   "EL1 ExtLtg DayShape (Nov)", 
                   "EL1 ExtLtg DayShape (Dec)" )
   OEShape[1] = "EL1 OffEq Profile (S1)"
   CEShape[1] = "EL1 CookEq Profile (S1)"
   MiscShape[1] = "EL1 Misc Profile (S1)"
   MiscDivEIntens[1] = 1.5
   MiscDivEIntens[2] = 1.5
   MiscDivEIntens[3] = 1.5
   MiscDivEIntens[4] = 1.5
   MiscDivEIntens[5] = 1.5
   MiscDivEIntens[6] = 1.5
   MiscDivEIntens[7] = 1.5
   MiscDivEIntens[8] = 1.5
   DHWShape[1] = "EL1 DHW Profile (S1)"
   PrcShape[1] = "EL1 Process Profile (S1)"
   PrcBTULoadType = "Process Load"
   PrcDivEIntens[1] = 0
   DaylitAreaCurrent = ( 1, 1, 1 )
   RoofZoneErrorCode = 4
   ..

ShapeWiz   "EL1 InsLtg Profile (S1)"  
   ..

DayShape   "EL1 ExtLtg DayShape (Jan)"  
   ..

DayShape   "EL1 ExtLtg DayShape (Feb)"  
   ..

DayShape   "EL1 ExtLtg DayShape (Mar)"  
   ..

DayShape   "EL1 ExtLtg DayShape (Apr)"  
   ..

DayShape   "EL1 ExtLtg DayShape (May)"  
   ..

DayShape   "EL1 ExtLtg DayShape (Jun)"  
   ..

DayShape   "EL1 ExtLtg DayShape (Jul)"  
   ..

DayShape   "EL1 ExtLtg DayShape (Aug)"  
   ..

DayShape   "EL1 ExtLtg DayShape (Sep)"  
   ..

DayShape   "EL1 ExtLtg DayShape (Oct)"  
   ..

DayShape   "EL1 ExtLtg DayShape (Nov)"  
   ..

DayShape   "EL1 ExtLtg DayShape (Dec)"  
   ..

ShapeWiz   "EL1 OffEq Profile (S1)"  
   ..

ShapeWiz   "EL1 Misc Profile (S1)"  
   ..

ShapeWiz   "EL1 DHW Profile (S1)"  
   ..

ShapeWiz   "EL1 Occup Profile (S1)"  
   ..

ShapeWiz   "EL1 Process Profile (S1)"  
   ..

ShapeWiz   "EL1 CookEq Profile (S1)"  
   ..

ZnGrpWiz   "EL1 Underground Areas"  
   ShortName = "Undgnd"
   ..

ZnGrpWiz   "EL1 Ground Floor Core"  
   ShortName = "GndCor"
   ..

ZnGrpWiz   "EL1 Ground Floor Perimeter"  
   ShortName = "GndPrm"
   ..

ZnGrpWiz   "EL1 Typical Floor(s) Core"  
   ShortName = "TypCor"
   ..

ZnGrpWiz   "EL1 Typical Floor(s) Perimeter"  
   ShortName = "TypPrm"
   ..

ZnGrpWiz   "EL1 Top Floor Core"  
   ShortName = "TopCor"
   ..

ZnGrpWiz   "EL1 Top Floor Perimeter"  
   ShortName = "TopPrm"
   ..

DiagData   "Bldg Envelope & Loads 1 Diag Data"  
   ..

HVACWiz   "HVAC System 1"  
   ScreenIDArrIdx = 0
   ScreenIDArrID = 112
   CoolSource[1] = "Chilled Water Coils"
   HVACSysType[1] = "4-Pipe Fan Coils with HW Heat"
   BBDHeatSource[1] = "Hot Water"
   SFanPower[1] = 1
   SFanFlowOption[1] = "Auto-size"
   MinAllowedAirflow[1] = 1
   FanNightCycleOpt[1] = "Cycle Fans (no OA at night + economizer)"
   SystemPerWhat[1] = "System per Floor"
   ..

DXCWWiz   "Water-Cooled DX System"  
   ..

WSECWWiz   "Wtr-Side Econo System"  
   ..

WLHPWiz   "WSHP System"  
   ..

GSHPWiz   "GSHP System"  
   ..

PrimWiz   "Primary HVAC Plant"  
   CHWScrnIDArrIdx = 0
   CHWScrnIDArrID = 190
   HWScrnIDArrIdx = 0
   HWScrnIDArrID = 220
   CHWSysPumpConfig = "Both System and Chiller Pumps"
   CHWSysOperation = "Standby"
   ChlrPumpEff[1] = "Standard"
   WCondFanMotorEff = "Standard"
   HWSysPumpConfig = "Both System and Boiler Pumps"
   BoilerType[1] = "HW Boiler (Natural Draft)"
   BoilerCombEff[1] = 70
   ..

DHWWiz   "DHW Plant 1"  
   ScreenIDArrIdx = 0
   DHWEfficiency = 0.7
   ..

FacetColor   "By Wall Type"  
   FacetType = "Walls"
   ColorOption = "By Wall Type"
   ..

FacetColor   "By Construction"  
   FacetType = "Walls"
   ColorOption = "By Construction"
   ..

FacetColor   "Uniform"  
   FacetType = "Windows"
   ColorOption = "Uniform"
   ..

FacetColor   "By Glass Type"  
   FacetType = "Windows"
   ColorOption = "By Glass Type"
   ..

Light3D   "Light3D - Default"  
   Type = "Default"
   ..

Light3D   "Light3D - User1"  
   Type = "User Defined 1"
   ..

Light3D   "Light3D - User2"  
   Type = "User Defined 2"
   ..

Light3D   "Light3D - User3"  
   Type = "User Defined 3"
   ..

Light3D   "Light3D - User4"  
   Type = "User Defined 4"
   ..

Light3D   "Light3D - User5"  
   Type = "User Defined 5"
   ..


END_OF_FILE


More information about the Equest-users mailing list