[Equest-users] Equest Custom building footprint error msg
Mayank Bhatnagar via Equest-users
equest-users at lists.onebuilding.org
Tue Dec 6 02:55:33 PST 2016
Hi Niraj,
There are number of possiblity why it is happening. However, I would
suggest to check your cad file for unused layers and size of the file.
Purge all unused layers and try again.
Hope this resolve your issue.
Regards,
Mayank Bhatnagar
On Tue, Dec 6, 2016 at 3:27 PM, Niraj Boodhoo via Equest-users <
equest-users at lists.onebuilding.org> wrote:
> Good morning everyone
>
>
>
> I am having a problem getting Equest to do my model. I have imported the
> CAD file correctly and have been able to do the building outline. However,
> as soon as I click the ‘DONE’ button, the software is giving me an error
> message and I have no other alternative than to quit the system, without
> the possibility to save anything.
>
>
>
> I have tried to run it on different computers, and the same thing is
> happening.
>
>
>
> My OS is Windows 8.1, 64 bit and in principle, it should be compatible
> with Equest.
>
>
>
> Any help would be greatly appreciated.
>
>
>
> Thanks
>
> Niraj
>
>
>
> *From:* Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] *On
> Behalf Of *Nicholas Caton via Equest-users
> *Sent:* 05 December 2016 22:58
> *To:* Bishop, Bill <bbishop at pathfinder-ea.com>; Fakeha Sehar <
> fakeha_s at yahoo.com>
> *Cc:* equest-users at lists.onebuilding.org
> *Subject:* Re: [Equest-users] HVAC description - HVAC Summary file
>
>
>
> Hello Fakeha,
>
>
>
> In addition to Bill’s suggestion to consider the HVAC Summary CSV output,
> here are a few options “out of the box” which may address your query. 2
> major options (following a simulation run), and 1 over-arching caution:
>
> 1. Air-side HVAC tab, highlight the system in question in the
> component tree, then click the “Summary” tab to review SYSTEM and ZONE
> capacities. Alternatively highlight the “Project” line at the top of the
> component tree to review each system in succession.
>
> 2. Look to the SV-A reports in the SIM output file
>
>
>
> *Caution:* If you are seeing zeroes for the system cooling/heating
> capacity in the SV-A reports, there’s a good chance you’re looking at one
> of the inherently zonal system types, such as PTAC or FC. Be mindful that
> irrespective of how many of those SYSTEMS you have defined for the model,
> they actually exist on a per-zone basis when trying to summarize
> capacities.
>
>
>
> For example: if I have a PTAC system assigned to 10 conditioned zones, and
> the resulting airside summary tab suggests I have 60 tons for that
> “system,” that really means the typical PTAC averages ~6 tons (and would
> normally be expected to vary around that figure). If auto-sized, those
> capacities are respective design conditions for each respective zone, and
> do not in sum necessarily represent the aggregate peak cooling demand for
> the building.
>
>
>
> If “zonal system types” is alone cause for a head-scratch, advising
> further reading in/around Volume 1: Basics > Air-side Components >
> Introduction > Another Way of Classifying Air Systems > Zonal vs. Central
> Systems.
>
>
>
> Hope this helps!
>
>
>
> ~Nick
>
>
>
>
>
> *Nick Caton, P.E., BEMP*
>
> Senior Energy Engineer
> Energy and Sustainability Services
> Schneider Electric
>
> D 913.564.6361
> M 785.410.3317
> E nicholas.caton at schneider-electric.com
> F 913.564.6380
>
> 15200 Santa Fe Trail Drive
> Suite 204
> Lenexa, KS 66219
> United States
>
> [image: cid:image001.png at 01D189AB.58634A10]
>
>
>
>
>
> *From:* Equest-users [mailto:equest-users-bounces at lists.onebuilding.org
> <equest-users-bounces at lists.onebuilding.org>] *On Behalf Of *Bishop, Bill
> via Equest-users
> *Sent:* Monday, December 05, 2016 12:48 PM
> *To:* Fakeha Sehar <fakeha_s at yahoo.com>
> *Cc:* equest-users at lists.onebuilding.org
> *Subject:* Re: [Equest-users] HVAC description - HVAC Summary file
>
>
>
> Hi Fakeha,
>
> The HVAC Summary file may have what you are looking for. See my previous
> post, inserted below, if this file is not currently generated by your
> eQUEST installation.
>
> Regards,
>
> ~Bill
>
>
>
> eQUEST can generate a handy HVAC Summary file (.csv) automatically when
> you simulate. You have to open the “eQUEST.INI” file and insert the line,
> “StoreResults_HVAC_Summary=1” as shown in the screen shot below. The
> eQUEST.INI file is in the eQUEST Data directory, in both 3.65 and 3.64,
> which can be found in Tools -> View File Locations -> View eQUEST Data
> Directory. Once you modify, and save the eQUEST.INI file, there will be a
> “YOUR_PROJECT_NAME – HVAC Summary.csv” file in the project folder after you
> open and simulate your project. I mostly use the Air-Side System Summaries
> portion of the file to help with automating fan power and EIR calculations
> for Baseline models.
>
>
>
>
>
> Regards,
>
> Bill
>
>
>
>
>
> *William Bishop, PE, BEMP, BEAP, CEM, LEED AP **|** Pathfinder Engineers
> & Architects LLP*
>
> *Senior Energy Engineer*
>
>
>
>
>
> 134 South Fitzhugh Street Rochester, NY 14608
>
> *T: (585) 698-1956* F: (585) 325-6005
>
> bbishop at pathfinder-ea.com <wbishop at pathfinder-ea.com>
> www.pathfinder-ea.com
>
> [image: http://png-5.findicons.com/files/icons/977/rrze/720/globe.png]Carbon
> Fee and Dividend - simple, effective, and market-based.
>
>
>
> *From:* Equest-users [mailto:equest-users-bounces at lists.onebuilding.org
> <equest-users-bounces at lists.onebuilding.org>] *On Behalf Of *Fakeha Sehar
> via Equest-users
> *Sent:* Monday, December 05, 2016 1:20 PM
> *To:* via Equest-users <equest-users at lists.onebuilding.org>
> *Subject:* [Equest-users] HVAC description
>
>
>
> Hi,
>
>
>
> I want to know how to get a concise summary of the HVAC equipment in my
> building. For example, system 1 supports 3 different spaces, the SIM file
> shows the capacity/flow rates individually for the three spaces. I want
> the overall system 1 capacity so that I can say that system 1 has lets say
> 5 ton AC.
>
>
>
> Regards
>
>
> ______________________________________________________________________
> This email has been scanned by the Symantec Email Security.cloud service.
> ______________________________________________________________________
> ------------------------------
>
> This message was scanned by Exchange Online Protection Services.
> ------------------------------
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20161206/5c496c01/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 255 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20161206/5c496c01/attachment-0008.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image006.png
Type: image/png
Size: 2841 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20161206/5c496c01/attachment-0009.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.png
Type: image/png
Size: 7893 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20161206/5c496c01/attachment-0010.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.jpg
Type: image/jpeg
Size: 32648 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20161206/5c496c01/attachment-0006.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image007.png
Type: image/png
Size: 132159 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20161206/5c496c01/attachment-0011.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image004.jpg
Type: image/jpeg
Size: 1240 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20161206/5c496c01/attachment-0007.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image005.jpg
Type: image/jpeg
Size: 1309 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20161206/5c496c01/attachment-0008.jpg>
More information about the Equest-users
mailing list