[Equest-users] Purpose of a DESIGN-DAY CLIMATE input?
Nicholas Caton via Equest-users
equest-users at lists.onebuilding.org
Fri Dec 2 11:18:16 PST 2016
I think the “transition from doe2.1e” document may be congruous actually with Joe’s original suggestion… It does reinforce that we’re on the right track to consider CLIMATE as associated with determing solar pathing for design days.
I’ve gone digging into Fundamentals 2005 and, googling after citations therein to try and lock in on this “Climate/Latitude” binning for solar angles. Found nothing direct in the Handbook to clarify but it does appear this (older) “ASHRAE clear sky model” was in fact limited to the Northern hemisphere (which may lead to why there’s seemingly nothing presently in DESIGN-DAY inputs to directly inform North vs South hemispheres… it seems a distinct possibility eQUEST makes a separate check of weather file latitude or other solar inputs however to account for this).
I’ve come across many papers/names associated with evaluation and improvement of that clear sky model. The “midlatitude” term particularly pops up in a few such abstracts / summaries for papers I can’t readily access, so I suspect doe2.2 initially was following one such extension to the pre-2006 ASHRAE clear sky model.
~Nick
[cid:image001.png at 01D24BE7.A8631500]
Nick Caton, P.E., BEMP
Senior Energy Engineer
Energy and Sustainability Services
Schneider Electric
D 913.564.6361
M 785.410.3317
E nicholas.caton at schneider-electric.com<mailto:nicholas.caton at schneider-electric.com>
F 913.564.6380
15200 Santa Fe Trail Drive
Suite 204
Lenexa, KS 66219
United States
[cid:image001.png at 01D189AB.58634A10]
From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of zhaoyongqing1987 via Equest-users
Sent: Tuesday, November 29, 2016 7:54 PM
To: Daric Adair via Equest-users <equest-users at lists.onebuilding.org>
Subject: Re: [Equest-users] Purpose of a DESIGN-DAY CLIMATE input?
DOE2.2 help files indicates that CLEARNESS and CLOUD-TYPE are now replaced by CLIMATE and VISIBILIY. It seems that CLIMATE is used for determine the clearness of sky.
Volume 3: Topics<mailmaster://webui/pages/write/writemail_content.html> > Overview and Converting From 2.1E<mailmaster://webui/pages/write/writemail_content.html> > LOADS<mailmaster://webui/pages/write/writemail_content.html>
DOE-2.1E version:
HOT-CLEAR-SUMMER = DESIGN-DAY
DRYBULB-HI = 91 DRYBULB-LO = 71
HOUR-HI = 15 HOUR-LO = 7
DEWPT-HI = 65.5 DEWPT-LO = 60
DHOUR-HI = 16 DHOUR-LO = 8
WIND-SPEED = 7.5 WIND-DIR = 10
CLOUD-AMOUNT = 0 CLOUD-TYPE = 0
CLEARNESS = 1 GROUND-T = 61 ..
COLD-CLOUDY-WINTER = DESIGN-DAY
DRYBULB-HI = 6 DRYBULB-LO = -4
HOUR-HI = 15 HOUR-LO = 2
DEWPT-HI = 6 DEWPT-LO = -4
DHOUR-HI = 16 DHOUR-LO = 3
WIND-SPEED = 15 WIND-DIR = 14
CLOUD-AMOUNT = 5 CLOUD-TYPE = 2
CLEARNESS = 1 GROUND-T = 46 ..
Converted:
"Chicago CDD" = DESIGN-DAY
TYPE = COOLING
DRYBULB-HIGH = 91 DRYBULB-RANGE = 20
HOUR-HIGH = 15 HOUR-LOW = 7
WETBULB-AT-HIGH = 77
WIND-SPEED = 7.5 WIND-DIR = SW
CLOUD-AMOUNT = 0 CLIMATE = MIDLATITUDE
VISIBILITY = HIGH GROUND-T = 61
..
"Chicago HDD" = DESIGN-DAY
TYPE = HEATING
DRYBULB-HIGH = 6 DRYBULB-RANGE = 10
HOUR-HIGH = 15 HOUR-LOW = 2
WIND-SPEED = 15 WIND-DIR = NW
CLOUD-AMOUNT = 5 CLIMATE = MIDLATITUDE
VISIBILITY = LOW GROUND-T = 46
On 11/30/2016 07:04, David Griffin II via Equest-users <equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>> wrote:
Nick/Joe,
I have done some light research on the topic since DOE2.3 moves in the direction of utilizing DESIGN-DAY more rigorously; e.g. if you depend on the weather file for auto sizing in DOE2.3, your simulation takes twice as long. I would refer both of you to page 23 of the DOE2.3 Volume 6 “Design-Sizing Enhancements” where it appears the eQUEST team is attempting exactly what Joe previously mentioned.
Although I believe the CLIMATE input is still available in DOE2.3 it may be ignored by the new algorithm. Maybe Jeff H. can shed some light on this situation for us.
Sincerely,
[ARCH | NEXUS]<http://www.archnexus.com>
DAVID W. GRIFFIN II
BEMP
ENERGY ANALYST
2505 E Parleys Way
Salt Lake City, UT 84109
Office 801.924.5028
archnexus.com<http://www.archnexus.com>
[Twitter]<https://twitter.com/arch_nexus>[Facebook]<https://www.facebook.com/pages/Architectural-Nexus/179588705397563?ref=ts&fref=ts>[Youtube]<https://www.youtube.com/channel/UCYRPWKF-yp-AUiI8ia2XfKw?feature=mhee>[LinkedIn]<https://www.linkedin.com/company/architectural-nexus>
From: Joe Huang via Equest-users [mailto:equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>]
Sent: Tuesday, November 29, 2016 1:49 PM
To: equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: Re: [Equest-users] Purpose of a DESIGN-DAY CLIMATE input?
I think this is a case of DOE-2 still using an older procedure for the solar portion of the design day calculation. Prior to 2006, ASHRAE used a relatively crude ASHRAE Clear Sky Model to determine the hourly profile of solar radiation for the design day. That model assumes there are different sky conditions for different latitudes, etc. In 2006, ASHRAE TC 4.2 (Climatic Information) carried out a project to develop an entirely new ASHRAE Clear Sky Model that's a parameterization of a detailed solar model developed by Chris Gueymard.
It would be nice if DOE-2 incorporates the new ASHRAE Clear Sky Model, which isn't terribly hard, but would take work. Besides, I'm under the impression that the vast majority of DOE-2 users don't do design day calculations but rather let the program autosize the equipment anyway!
Joe
Joe Huang
White Box Technologies, Inc.
346 Rheem Blvd., Suite 205A
Moraga CA 94556
yjhuang at whiteboxtechnologies.com<mailto:yjhuang at whiteboxtechnologies.com>
http://weather.whiteboxtechnologies.com for simulation-ready weather data
(o) (925)388-0265
(c) (510)928-2683
"building energy simulations at your fingertips"
On 11/29/2016 9:43 AM, Nicholas Caton via Equest-users wrote:
I have a question concerning doe2/eQUEST DESIGN-DAYs.
One of the keywords for DESIGN-DAY confuses me: CLIMATE. I have not been able to find this documented in the current doe2 reference manual or 2.1A engineering manuals.
It appears the CLIMATE keyword can accept one of three inputs: “SUBARCTIC,” “MIDLATITUDE,” or “TROPICAL.” The default is MIDLATITUDE and does not appear to reference anything else.
[cid:image003.png at 01D24BE7.A8631500]
So I have a few questions:
1. What is this input used for? Does it help to determine solar angles during design day calculations? Does it affect how other DESIGN-DAY inputs are interpreted?
2. Since one of the options is named “MIDLATITUDE,” my best guess is this is trying to establish in a loose sense which slice of the globe the weather station is located at for solar angle purposes. From that guess, I googled the topic for a bit<http://www.lat34north.com/cities/CitiesLatitude.cfm> and came up with this framework:
a. SUBARCTIC latitudes are > 66.5 or < -66.5 (Inside the Arctic circles - experiences days of complete daylight/darkness)
b. TROPICAL is between -23.5 and 23.5 (Tropic of Capricorn/Cancer - experiences the sun traversing directly overhead)
c. MIDLATITUDE = everywhere else
3. I struggle however with the concept of a DESIGN-DAY input based on latitude, where
a. The latitude is already a part of the weather file required for every simulation… and pulling the exact latitude would be more accurate anyway (I confess here I have never studied solar pathing in great depth - the problem may be simpler than I realize?).
b. These bands alone don’t give you enough information to know when you’re in the lower hemisphere (where solar angles based on the day/month would be flipped)
c. This leads me to question whether there’s a (meaningful) difference in solar angles experienced for loads calculations when you use the weather file instead of DESIGN-DAY inputs.
d. Alternatively, maybe the latitude IS pulled from the weather file for solar angle purposes so I’m completely on the wrong path as to the purpose/intent for the CLIMATE input.
Can anyone set me straight on this topic?
~Nick
[cid:image001.png at 01D24BE7.A8631500]
Nick Caton, P.E., BEMP
Senior Energy Engineer
Energy and Sustainability Services
Schneider Electric
D 913.564.6361
M 785.410.3317
E nicholas.caton at schneider-electric.com<mailto:nicholas.caton at schneider-electric.com>
F 913.564.6380
15200 Santa Fe Trail Drive
Suite 204
Lenexa, KS 66219
United States
[cid:image001.png at 01D189AB.58634A10]
________________________________
This message was scanned by Exchange Online Protection Services.
________________________________
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG<mailto:EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG>
______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
______________________________________________________________________
________________________________
This message was scanned by Exchange Online Protection Services.
________________________________
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20161202/d2dab709/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 255 bytes
Desc: image001.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20161202/d2dab709/attachment-0006.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.png
Type: image/png
Size: 7893 bytes
Desc: image002.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20161202/d2dab709/attachment-0007.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.png
Type: image/png
Size: 34261 bytes
Desc: image003.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20161202/d2dab709/attachment-0008.png>
More information about the Equest-users
mailing list