[Equest-users] [Bldg-sim] LEED project - maximum limit allowed to simplified wall	azimuth.
    Nicholas Caton via Equest-users 
    equest-users at lists.onebuilding.org
       
    Thu Dec 15 13:40:08 PST 2016
    
    
  
That’s the one – thanks Daric!
~Nick
[cid:image004.png at 01D256E9.553BB230]
Nick Caton, P.E., BEMP
  Senior Energy Engineer
  Energy and Sustainability Services
  Schneider Electric
D  913.564.6361
M  785.410.3317
E  nicholas.caton at schneider-electric.com<mailto:nicholas.caton at schneider-electric.com>
F  913.564.6380
15200 Santa Fe Trail Drive
Suite 204
Lenexa, KS 66219
United States
[cid:image001.png at 01D189AB.58634A10]
From: Daric Adair [mailto:Daric.Adair at hei-eng.com]
Sent: Thursday, December 15, 2016 3:30 PM
To: Nicholas Caton <Nicholas.Caton at schneider-electric.com>; Leonard Sciarra <leonard_sciarra at gensler.com>
Cc: equest-users <equest-users at lists.onebuilding.org>
Subject: RE: [Equest-users] [Bldg-sim] LEED project - maximum limit allowed to simplified wall azimuth.
Attached the presentation slides from reference ASHRAE Conference…..
This project/study had a round building. There is an appreciable improvement in going from 4 side to 8 sides, much (much) smaller improvement in 8 to 12…..but flat lines from there.
Thanks,
DARIC R. ADAIR  PE, C.E.M.
Henderson Engineers, Inc. | Mechanical Engineer, Energy Analyst
dir 913 742 5530  tel 913 742 5000  fax 913 742 5001  tx id #F-001236  email daric.adair at hei-eng.com  www.hei-eng.com<http://www.hei-eng.com/>
Licensed in KS. 
From: Nicholas Caton via Equest-users [mailto:equest-users at lists.onebuilding.org]
Sent: Thursday, December 15, 2016 12:18 PM
To: Leonard Sciarra <leonard_sciarra at gensler.com<mailto:leonard_sciarra at gensler.com>>; equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: Re: [Equest-users] [Bldg-sim] LEED project - maximum limit allowed to simplified wall azimuth.
Put another way:
If you have a perfectly circular floorplate, ASHRAE wants you to model an octagon, with respect to a minimum number of facets.
This specific query reminds me:  There was a pretty interesting thought-study presented at ASHRAE’s energy conference in 2015 where someone tested this logic, by asking the question (paraphrasing) “how few facets can we get away with and still accurately represent a perfect circle?”  I don’t recall exactly the answer but the results surprised me with how far you could go in simplifying the shape & still maintain relative accuracy.  I believe a 4 sided square (corrected geometrically for volume) in fact performed very closely to the baseline.
If you’re sincerely & specifically interested in modeling an octagon as a square, I think you’ll find that could actually be pretty accurate so long as you are correcting for conditioned volume / exposed area.  I’d seek out that actual paper/presentation while you’re at it ;-).
~Nick
[cid:image004.png at 01D256E9.553BB230]
Nick Caton, P.E., BEMP
  Senior Energy Engineer
  Energy and Sustainability Services
  Schneider Electric
D  913.564.6361
M  785.410.3317
E  nicholas.caton at schneider-electric.com<mailto:nicholas.caton at schneider-electric.com>
F  913.564.6380
15200 Santa Fe Trail Drive
Suite 204
Lenexa, KS 66219
United States
[cid:image001.png at 01D189AB.58634A10]
From: Bldg-sim [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Leonard Sciarra via Bldg-sim
Sent: Thursday, December 15, 2016 12:05 PM
To: bldg-sim at lists.onebuilding.org<mailto:bldg-sim at lists.onebuilding.org>
Subject: Re: [Bldg-sim] LEED project - maximum limit allowed to simplified wall azimuth.
Julian –
The text is written to include 45 degrees.  So if they are 45 degrees, then you can make it a square, although the exception was intended for curved surfaces.
Hope this helps.
Leonard Sciarra, AIA, ASHRAE, LEED ap+
Senior Associate
+1 312.577.6580 Direct
+1 312.456.0123 Main
+1 847.345.5619 Mobile
Gensler
11 East Madison Street
Suite 300
Chicago, Illinois 60602
USA
Gensler.com<http://www.gensler.com/> | Blog<http://www.gensleron.com/> | Facebook<http://www.facebook.com/GenslerDesign> | Twitter<http://www.twitter.com/GenslerOnCities> | YouTube<http://www.youtube.com/GenslerTV>
What’s ahead for design and our clients?
Find out here: Gensler Design Forecast 2016<http://www.gensler.com/doc/gensler-design-forecast-2016>
From: Bldg-sim [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of via Bldg-sim
Sent: Thursday, December 15, 2016 11:17 AM
To: bldg-sim at lists.onebuilding.org<mailto:bldg-sim at lists.onebuilding.org>
Subject: [Bldg-sim] LEED project - maximum limit allowed to simplified wall azimuth.
Hello,
Does anyone know how to interpret “no more than 45 degrees” of exception 5.b - table G3.1 (90.1-2007/2010/2013) ? :
5.  Building Envelope
All components of the building envelope in the proposed design shall be modeled as shown on architectural drawings or as built for existing building envelopes.
Exceptions:
b. Exterior surfaces whose azimuth orientation and tilt differ by no more than 45 degrees and are otherwise the same may be described as either a single surface or by using multipliers.
Because “no more than 45 degree” include 45 degree, does the exception still apply if the azimuth of two walls is exactly 45 degrees?
In other words, considering a LEED project, can a perfect octagonal building shape be modeled as a square building (as long as they have the same floor area and the 8 walls have a similar construction) ?
Thanks
Julien
____________________________________________________________________
Julien Dutel, ing., CEM, CMVP.
Direction des secteurs résidentiel, institutionnel et des affaires
Bureau de l'efficacité et de l'innovation énergétiques
Ministère de l'Énergie et des Ressources naturelles
5700, 4e Avenue Ouest, B-406
Québec (Québec)  G1H 6R1
Téléphone : 418 627-6379, poste 8060
Téléphone sans frais : 1 877 727-6655
Télécopieur : 418 643-5828
julien.dutel at mern.gouv.qc.ca<mailto:julien.dutel at mern.gouv.qc.ca>
mern.gouv.qc.ca
______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
______________________________________________________________________
________________________________
This email and any files transmitted with it are confidential and are intended solely for the use of the individual or entity to whom they are addressed. This communication represents the originator's personal views and opinions, which do not necessarily reflect those of Henderson Engineers, Inc. If you are not the original recipient or the person responsible for delivering the email to the intended recipient, be advised that you have received this email in error, and that any use, dissemination, forwarding, printing, or copying of this email is strictly prohibited. If you received this email in error, please immediately notify administrator at hei-eng.com<mailto:administrator at hei-eng.com>.
______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
______________________________________________________________________
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20161215/4fb548b4/attachment-0005.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image004.png
Type: image/png
Size: 255 bytes
Desc: image004.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20161215/4fb548b4/attachment-0010.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image005.png
Type: image/png
Size: 7893 bytes
Desc: image005.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20161215/4fb548b4/attachment-0011.png>
    
    
More information about the Equest-users
mailing list