[Equest-users] Modeling Avionics Cooling units
Julien MARREC via Equest-users
equest-users at lists.onebuilding.org
Mon Aug 15 23:27:39 PDT 2016
Hi,
Your best and fastest bet is to apply a schedule multiplier to your process load. You can the weather file to create a schedule that you'll import in eQuest.
Tools such as RMI's EMIT make it easy to export such schedules
Best,
Julien
Envoyé de mon iPhone
> Le 16 août 2016 à 00:13, "Gutschow, Ezra via Equest-users" <equest-users at lists.onebuilding.org> a écrit :
>
> I’m modeling an aircraft maintenance hangar that uses “avionics cooling units” to cool off the electronics in the planes when they are under maintenance. These units are large air cooled condensing units with high static pressure fans. Since this project is for LEED, I’m modeling it as a process load for both baseline and proposed. Is there a way to make the “misc load” as a global, temperature dependent parameter?
> I’m not inclined to model these as chillers, as this would be confusing during the LEED documention.
> Thanks,
>
> Ezra Gutschow, P.E., LEED AP
> Senior Engineer, Mechanical Engineering
> Certified Commissioning Professional
>
> Coffman Engineers, Inc.
> 800 F Street | Anchorage, AK 99501
> p 907.276.6664 | f 907.276.5042 www.coffman.com
>
> LASTING creativity | results | relationships
> Please consider the environment before printing this email.
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20160816/1d5e8ab3/attachment-0002.htm>
More information about the Equest-users
mailing list