[Equest-users] Window U Value
John Aulbach via Equest-users
equest-users at lists.onebuilding.org
Mon Aug 1 08:35:09 PDT 2016
I believe the lower U-value includes the frame. The original number is only center-of-glass.
John R. Aulbach, PE
On Monday, August 1, 2016 8:07 AM, via Equest-users <equest-users at lists.onebuilding.org> wrote:
<!--#yiv1093014853 _filtered #yiv1093014853 {font-family:"Cambria Math";panose-1:2 4 5 3 5 4 6 3 2 4;} _filtered #yiv1093014853 {font-family:Calibri;panose-1:2 15 5 2 2 2 4 3 2 4;} _filtered #yiv1093014853 {font-family:Tahoma;panose-1:2 11 6 4 3 5 4 4 2 4;} _filtered #yiv1093014853 {font-family:Consolas;panose-1:2 11 6 9 2 2 4 3 2 4;} _filtered #yiv1093014853 {font-family:Verdana;panose-1:2 11 6 4 3 5 4 4 2 4;} _filtered #yiv1093014853 {font-family:"Franklin Gothic Book";}#yiv1093014853 #yiv1093014853 p.yiv1093014853MsoNormal, #yiv1093014853 li.yiv1093014853MsoNormal, #yiv1093014853 div.yiv1093014853MsoNormal {margin:0in;margin-bottom:.0001pt;font-size:11.0pt;font-family:"Calibri", "sans-serif";}#yiv1093014853 a:link, #yiv1093014853 span.yiv1093014853MsoHyperlink {color:blue;text-decoration:underline;}#yiv1093014853 a:visited, #yiv1093014853 span.yiv1093014853MsoHyperlinkFollowed {color:purple;text-decoration:underline;}#yiv1093014853 p.yiv1093014853MsoPlainText, #yiv1093014853 li.yiv1093014853MsoPlainText, #yiv1093014853 div.yiv1093014853MsoPlainText {margin:0in;margin-bottom:.0001pt;font-size:10.5pt;font-family:Consolas;}#yiv1093014853 p.yiv1093014853MsoAcetate, #yiv1093014853 li.yiv1093014853MsoAcetate, #yiv1093014853 div.yiv1093014853MsoAcetate {margin:0in;margin-bottom:.0001pt;font-size:8.0pt;font-family:"Tahoma", "sans-serif";}#yiv1093014853 span.yiv1093014853EmailStyle17 {font-family:"Calibri", "sans-serif";color:windowtext;}#yiv1093014853 span.yiv1093014853BalloonTextChar {font-family:"Tahoma", "sans-serif";}#yiv1093014853 span.yiv1093014853PlainTextChar {font-family:Consolas;}#yiv1093014853 .yiv1093014853MsoChpDefault {} _filtered #yiv1093014853 {margin:1.0in 1.0in 1.0in 1.0in;}#yiv1093014853 div.yiv1093014853WordSection1 {}-->Hello Sefa, This is a timely question – I needed this as a reminder for a couple active projects! Anytime the SIM reports are unintuitive/confusing – be sure you’re aware of the following resource: Help > Tutorials and Reference > Detailed Simulation Reports Summary Here, there are a number of clarifying notes concerning report LV-D specifically. To your case, if all frame widths are set to zero, then the difference between inputs and these outputs will be the OA film coefficient for a 7.5 mph (summer) windspeed:See the table located here in the DOE-2 help files for further information/documentation: Volume 2: Dictionary > Envelope Components > GLASS-TYPE > GLASS-CONDUCTANCE (Table 11)In summary, do not equate the GLASS-CONDUCTANCE input with the assembly U-value, when using simplified glass type inputs. If you want to effect U-0.9 for the entire assembly, enter 1.23 for glass conductance in simplified window properties inputs. LV-D should then report 0.9 as the assembly U-value. At one point – I performed a curve-fit to find the coefficients to interpolate the above-cited table and shared with the list – see the email thread and image copied below. Until assembly U-value becomes an input option for Simplified glass type inputs (feature-request, developers!), you could also calculate/automate GLASS-CONDUCTANCE with the following expression, referencing a global parameter:0.2535*#PA("ASSEMBLY-UVALUE")**3+0.101*#PA("ASSEMBLY-UVALUE")**2+1.0852*#PA("ASSEMBLY-UVALUE")-0.0117 ~Nick Nick Caton, P.E.
| Senior Energy Engineer
Energy and Sustainability Services
North America Operations
Schneider Electric | D 913.564.6361
M 785.410.3317
E nicholas.caton at schneider-electric.com
F 913.564.6380 | 15200 Santa Fe Trail Drive
Suite 204
Lenexa, KS 66219
United States |
| |
-----Original Message-----
From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Sefa Sahin via Equest-users
Sent: Monday, August 01, 2016 8:47 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Window U Value Dear All, I am trying to model window with 0.9 U-value. When I use 0.9 U value on model, LV-D reports shows 0.709 U value (frame with = 0 ). What is the reason it ? Please find attached files. Thanks for all replies, Sefa Sahin From: Nicholas Caton [mailto:ncaton at catonenergy.com]
Sent: Tuesday, December 23, 2014 3:43 PM
To: Jones, Christopher; Omar ElRawy; equest
Subject: RE: [Equest-users] Exterior Air Film - glazing Chris: After backtracking to the old glossary… I’ve learned something today! You are absolutely right, and thank you for pressing the point! I had the mistaken impression the U-values prescribed by 90.1 were exclusive of air films, analogous to GLASS-CONDUCTANCE. The LV-D reports, inclusive of the exterior air film (assuming a 7.5mph wind), actually ought match the prescribed gross assembly U-factor. I’ll be updating some of my personal resources! For anyone else interested, here shared are coefficients for a curve matching the DOE2 reference for converting between the two: Omar, I’ll leave it to you to decide how to proceed. I have (successfully enough) addressed the exact same commentary multiple times by simply illustrating my inputs matched the prescribed values. My heart was in the right place, but I (and perhaps my reviewers) did not realize the disconnect with the output reports was not simply a matter of an erroneous inclusion of air films. I will be changing my ways moving forward, personally! Kind regards, and happy holidays to everyone on the list! ~Nick NICK CATON, P.E.
Owner Caton Energy Consulting
1150 N. 192nd St., #4-202 Shoreline, WA 98133
office: 785.410.3317www.catonenergy.com From: Jones, Christopher [mailto:cjones at halsall.com]
Sent: Tuesday, December 23, 2014 5:33 AM
To: Nicholas Caton; Omar ElRawy; equest
Subject: RE: [Equest-users] Exterior Air Film - glazing Nick,Would you not agree that one should define the glazing Conductance in the eQuest input, not the glazing U-value? That way the .sim file reported glazing U-value is closer to what is expected? Christopher Jones, P.Eng.
Tel: 416.644.4226 • Toll Free: 1.888.425.7255 x 527 From: Nicholas Caton [mailto:ncaton at catonenergy.com]
Sent: Monday, December 22, 2014 4:46 PM
To: Jones, Christopher; Omar ElRawy; equest
Subject: RE: [Equest-users] Exterior Air Film The LV-D reports (and others touching on windows/constructions) do indeed include an exterior air film. I don’t know of a way to change that. A quick screengrab of your (correct) inputs and a one-line explanation of that fact is probably your most expedient path forward for a LEED review response. ~Nick NICK CATON, P.E.
Owner Caton Energy Consulting
1150 N. 192nd St., #4-202 Shoreline, WA 98133
office: 785.410.3317www.catonenergy.com From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Jones, Christopher
Sent: Monday, December 22, 2014 8:23 AM
To: Omar ElRawy; equest
Subject: Re: [Equest-users] Exterior Air Film For glazing, you have to enter the GLASS-CONDUCTANCE into eQuest, not the glazing U-value. See page 65 in the DOE22Vol2-Dictionary reference manual available for download at doe2.com. Christopher Jones, P.Eng.
Tel: 416.644.4226 • Toll Free: 1.888.425.7255 x 527 From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Omar ElRawy
Sent: Monday, December 22, 2014 7:28 AM
To: equest
Subject: [Equest-users] Exterior Air Film Dear all, I have a problem reporting baseline case for LEED submission, where the exterior walls and windows U-values in Report LV-D appears less than the ASHRAE G 90.1 values that I did enter to the model, and this is (as I think) because eQuest adds the exterior air-film effect to the assembly during the run. My question is that; can I disable this eQuest calculation to see my input directly in LV-D report or not?
Thanks,Omar ElRawy, LEED AP BD+C
LEED Project Manager
EA Sustainable Building Consultants
http://www.ea-buildingconsultants.com/
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20160801/083566c1/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 7893 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20160801/083566c1/attachment-0010.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 255 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20160801/083566c1/attachment-0011.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 46723 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20160801/083566c1/attachment-0002.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 40883 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20160801/083566c1/attachment-0012.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 67275 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20160801/083566c1/attachment-0013.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 29188 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20160801/083566c1/attachment-0014.png>
More information about the Equest-users
mailing list