[Equest-users] Min Allowable Supply Air Flow
    Chris Jones via Equest-users 
    equest-users at lists.onebuilding.org
       
    Thu Aug 25 07:00:47 PDT 2016
    
    
  
Hello Bill,
Was going to ask you the following question but then I searched through BDLdft.dat. Very clever.
>>>>>>>>>>>>>>>>>>>>>>>>>>>>>
I am wondering how you determined that the MIN-FLOW-RATIO keyword is unused in the ZONE for systems where it is used in the SYSTEM? I am assuming that #SV(#P(“TYPE”)) refers to the system type. System 28 is PVVT and MIN-FLOW-RATIO is used in the System, no default is specified.
Christopher Jones, P. Eng.
Rowan Williams Davies & Irwin Inc.
Consulting Engineers & Scientists
901 King Street West, Suite 400, Toronto, Ontario, M5V 3H5
T: (519) 823-1311 ext 2052
M: (416) 697-0056
From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Bishop, Bill via Equest-users
Sent: Thursday, August 25, 2016 9:04 AM
To: Darryl Kasun
Cc: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Min Allowable Supply Air Flow
Darryl,
There is no zone keyword for minimum ACH. But you can enter the zone design ACH (ZONE:AIR-CHANGES/HR) and set the minimum air changes as a percentage of this using ZONE:MIN-FLOW-RATIO. You can write a keyword expression that enters and calculates this based on other zone inputs if you wanted to. For example, the expression below modifies the default DOE-2 expression for MIN-FLOW-RATIO, adding a calculation step based on the zone input for AIR-CHANGES/HR. The sample calculation assumes you want a minimum ACH of 3, and calculates the MIN-FLOW-RATIO for any zones for which you enter a design ACH rate of 3 or more.
if (#P("MIN-CFM-RATIO") == unused)
    then unused
    else switch #SV(#P("TYPE"))
    case  2 : unused
    case 17 : unused
    case 19 : unused
    case 26 : unused
    case 27 : unused
    case 28 : unused
    case 29 : unused
    default : if (#RV(#P("MIN-CFM-RATIO")) == 0)
              then #P("MIN-CFM-RATIO")
              else if (#RV(#L("AIR-CHANGES/HR")) == 0
                .AND. #L("AIR-CHANGES/HR") >= 3) then
                3/#L("AIR-CHANGES/HR") else no_default endif
              endif
    endswitch
   endif
Regards,
~Bill
William Bishop, PE, BEMP, BEAP, CEM, LEED AP | Pathfinder Engineers & Architects LLP
Senior Energy Engineer
[cid:image002.jpg at 01D1FEB6.CD8910B0]  [cid:image004.jpg at 01D1FEB6.CD8910B0]
134 South Fitzhugh Street                 Rochester, NY 14608
T: (585) 698-1956                        F: (585) 325-6005
bbishop at pathfinder-ea.com<mailto:wbishop at pathfinder-ea.com>             www.pathfinder-ea.com<http://www.pathfinder-ea.com/>
[http://png-5.findicons.com/files/icons/977/rrze/720/globe.png]Carbon Fee and Dividend - simple, effective, and market-based.
From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Darryl Kasun via Equest-users
Sent: Wednesday, August 24, 2016 5:59 PM
To: equest <equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>>
Subject: [Equest-users] Min Allowable Supply Air Flow
Hello again eQUESTers,
For some zones, I want to set the min. allowable zone air supply flow rate to a certain ACH.  There is a zonal input for min. design air changes/hr but I think eQUEST will go below this flow if possible.  Sure I can calculate the minimum flow as cfm.ft2 or ratio but would like to not do this work if possible!
Is there a straight-up min. allowable ACH input for eQUEST?
________________________________
RWDI - One of Canada's 50 Best Managed Companies - This communication is intended for the sole use of the party to whom it was addressed and may contain information that is privileged and/or confidential. Any other distribution, copying or disclosure is strictly prohibited. If you received this email in error, please notify us immediately by replying to this email and delete the message without retaining any hard or electronic copies of same. Outgoing emails are scanned for viruses, but no warranty is made to their absence in this email or attachments. If you require any information supplied by RWDI in a different format to facilitate accessibility, contact the sender of the email, email solutions at rwdi.com or call +1.519.823.1311.
________________________________
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20160825/48fcd8d1/attachment-0005.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.jpg
Type: image/jpeg
Size: 1242 bytes
Desc: image002.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20160825/48fcd8d1/attachment-0010.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image004.jpg
Type: image/jpeg
Size: 1308 bytes
Desc: image004.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20160825/48fcd8d1/attachment-0011.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image006.png
Type: image/png
Size: 2844 bytes
Desc: image006.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20160825/48fcd8d1/attachment-0005.png>
    
    
More information about the Equest-users
mailing list