[Equest-users] Secondary Loop Valve Type

Darryl Kasun via Equest-users equest-users at lists.onebuilding.org
Tue Aug 23 14:35:15 PDT 2016


Hi David,

The flow in the secondary loop definitely varies based on differential
pressure setpoints.  There are two way valves at reheat coils, reflected
ceiling plans, etc.  And I've entered this input (two-way valve) at the
thermal zone level.

I guess I'm confused at the circulation loop level.  In this window, there
is also an "valve type" input for the secondary loop.  I know the primary
loop is constant and the secondary loop is variable so I'm thinking this
input should be "two-way valve" again.  These two inputs seem redundant to
me...

On Tue, Aug 23, 2016 at 2:12 PM, David Berty <
dberty at baselineenergyconsulting.com> wrote:

> Darryl,
> A three-way valve will maintain constant total branch or loop flow by
> modulating the flow to either the coil or directly to the return line. A
> two-way valve will modulate open or closed to maintain a flow or
> temperature (usually leaving air temp), as it closes it will reduce the
> total loop or branch flow proportionally. 3 way valves are not generally an
> acceptable choice because they run counter to the desire to reduce flow to
> reduce energy consumption. These valves are usually at the coil but can be
> at the primary secondary interface they perform the same function in
> general at either location. Smaller systems that might lack sufficient
> diversity to ensure a minimum level of system flow sometimes use these
> valves to ensure that the pumps don't "dead-head".
>
> David Berty, P.E.
> Baseline Energy Consulting
> 317.220.9272
>
> On Aug 23, 2016 2:17 PM, "Darryl Kasun via Equest-users" <
> equest-users at lists.onebuilding.org> wrote:
>
>> Hi eQUESTers,
>>
>> For a secondary loop, there is an input for valve type - either three way
>> or two way.  Can anyone provide a schematic or quick explanation of the
>> difference between how these two valves control the flow from the primary?
>> Is this input assuming there is a valve at the secondary loop connection?
>> If there is a simply a tee at the secondary connection, can the valve head
>> input be zero?
>>
>> _______________________________________________
>> Equest-users mailing list
>> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
>> To unsubscribe from this mailing list send  a blank message to
>> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>>
>>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20160823/c4416c46/attachment-0005.htm>


More information about the Equest-users mailing list