[Equest-users] PV-A report
    Rathna Shree via Equest-users 
    equest-users at lists.onebuilding.org
       
    Mon Aug  8 22:15:39 PDT 2016
    
    
  
Dear John,
This is a commercial Interior project under LEED. The project is occupying only 2 floors in a 8 floors building. Only for those two floors, internal loads and the air side HVAC varies between base and proposed case. Rest of the floors, building envelope and plant side is modeled identically between base and proposed case. I don't know how equest calculates secondary loop capacity and the flow. 
Regards,
Rathnashree
--------------------------------------------
On Mon, 8/8/16, John Aulbach <jra_sac at yahoo.com> wrote:
 Subject: Re: [Equest-users] PV-A report
 To: "Rathna Shree" <rathnashreep at yahoo.in>, "via Equest-users" <equest-users at lists.onebuilding.org>
 Date: Monday, 8 August, 2016, 2:42 PM
 
 Rathna:
 Did you
 make changes to your load in the Proposed (less lighting,
 improved HVAC control, VAV/VFD). For whatever reason, eQuest
 seems to change things based on a different load and load
 profile.
 But I will
 let other chime in as well.
 John R.
 Aulbach, PE 
 
     On Monday, August 8, 2016 2:52 AM, Rathna
 Shree via Equest-users
 <equest-users at lists.onebuilding.org> wrote:
   
 
  Dear
 All,
 I have
 modelled the central plant identical in base and proposed
 case as it is an existing one. I have provided the capacity,
 flow rate, power and efficiency values for all the pumps.
 This is an air cooled chiller.
 When i
 compared the PV-A report for both base and proposed case,
 the secondary chilled water loop capacity (Mbtu/hr) and loop
 flow (gpm) varies between base and proposed case. I am not
 able to make it identical even though i have not autosized
 anything.
 Please
 let me know if there is any way to make PV-A report
 identical to base and proposed case.
 Regards,Rathnashree