[Equest-users] Window U Value

via Equest-users equest-users at lists.onebuilding.org
Mon Aug 1 08:40:06 PDT 2016


Right:  LV-D accounts for both frame effects and outside air film.  In this case, Sefa mentioned setting frame widths to zero (knocking out that variable), so I tailored my reply to address mainly the film issue.  

 

 

Nick Caton, P.E.

  Senior Energy Engineer
  Energy and Sustainability Services
  North America Operations
  Schneider Electric

D  913.564.6361 
M  785.410.3317 
E  nicholas.caton at schneider-electric.com <mailto:nicholas.caton at schneider-electric.com> 
F  913.564.6380

15200 Santa Fe Trail Drive
Suite 204
Lenexa, KS 66219
United States

 

 

 

From: John Aulbach [mailto:jra_sac at yahoo.com] 
Sent: Monday, August 01, 2016 10:35 AM
To: Nicholas Caton; ssahin at mimtarch.com; equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Window U Value

 

I believe the lower U-value includes the frame. The original number is only center-of-glass.

 

John R. Aulbach, PE

 

On Monday, August 1, 2016 8:07 AM, via Equest-users <equest-users at lists.onebuilding.org> wrote:

 

Hello Sefa,

 

This is a timely question – I needed this as a reminder for a couple active projects!

 

Anytime the SIM reports are unintuitive/confusing – be sure you’re aware of the following resource: Help > Tutorials and Reference > Detailed Simulation Reports Summary

 

 

Here, there are a number of clarifying notes concerning report LV-D specifically.  To your case, if all frame widths are set to zero, then the difference between inputs and these outputs will be the OA film coefficient for a 7.5 mph (summer) windspeed:

 

See the table located here in the DOE-2 help files for further information/documentation: Volume 2: Dictionary > Envelope Components > GLASS-TYPE > GLASS-CONDUCTANCE (Table 11)

 

In summary, do not equate the GLASS-CONDUCTANCE input with the assembly U-value, when using simplified glass type inputs.  

 

If you want to effect U-0.9 for the entire assembly, enter 1.23 for glass conductance in simplified window properties inputs.  LV-D should then report 0.9 as the assembly U-value.

 

At one point – I performed a curve-fit to find the coefficients to interpolate the above-cited table and shared with the list – see the email thread and image copied below.  Until assembly U-value becomes an input option for Simplified glass type inputs (feature-request, developers!), you could also calculate/automate GLASS-CONDUCTANCE with the following expression, referencing a global parameter:

0.2535*#PA("ASSEMBLY-UVALUE")**3+0.101*#PA("ASSEMBLY-UVALUE")**2+1.0852*#PA("ASSEMBLY-UVALUE")-0.0117

 

~Nick

 



 

 

 

Nick Caton, P.E.

  Senior Energy Engineer
  Energy and Sustainability Services
  North America Operations
  Schneider Electric

D  913.564.6361 
M  785.410.3317 
E  nicholas.caton at schneider-electric.com <mailto:nicholas.caton at schneider-electric.com> 
F  913.564.6380

15200 Santa Fe Trail Drive
Suite 204
Lenexa, KS 66219
United States



 

 

 

-----Original Message-----
From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Sefa Sahin via Equest-users
Sent: Monday, August 01, 2016 8:47 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Window U Value

 

Dear All,

 

I am trying to model window with 0.9 U-value. When I use 0.9 U value on model, LV-D reports shows 0.709 U value (frame with = 0 ). What is the reason it ? Please find attached files.

 

Thanks for all replies,

 

Sefa Sahin

 

 

 

From: Nicholas Caton [mailto:ncaton at catonenergy.com] 
Sent: Tuesday, December 23, 2014 3:43 PM
To: Jones, Christopher; Omar ElRawy; equest
Subject: RE: [Equest-users] Exterior Air Film - glazing

 

Chris:

 

After backtracking to the old glossary… I’ve learned something today!  You are absolutely right, and thank you for pressing the point!

 

I had the mistaken impression the U-values prescribed by 90.1 were exclusive of air films, analogous to GLASS-CONDUCTANCE.  The LV-D reports, inclusive of the exterior air film (assuming a 7.5mph wind), actually ought match the prescribed gross assembly U-factor.  I’ll be updating some of my personal resources!

 

For anyone else interested, here shared are coefficients for a curve matching the DOE2 reference for converting between the two:

 

 

Omar,  I’ll leave it to you to decide how to proceed.  I have (successfully enough) addressed the exact same commentary multiple times by simply illustrating my inputs matched the prescribed values.  My heart was in the right place, but I (and perhaps my reviewers) did not realize the disconnect with the output reports was not simply a matter of an erroneous inclusion of air films.  I will be changing my ways moving forward, personally!

 

Kind regards, and happy holidays to everyone on the list!

 

~Nick

 

NICK CATON, P.E.
Owner

 

Caton Energy Consulting
  1150 N. 192nd St., #4-202

  Shoreline, WA 98133
  office:  785.410.3317

www.catonenergy.com

 

From: Jones, Christopher [mailto:cjones at halsall.com] 
Sent: Tuesday, December 23, 2014 5:33 AM
To: Nicholas Caton; Omar ElRawy; equest
Subject: RE: [Equest-users] Exterior Air Film - glazing

 

Nick,

Would you not agree that one should define the glazing Conductance in the eQuest input, not the glazing U-value?  That way the .sim file reported glazing U-value is closer to what is expected?  

 

Christopher Jones, P.Eng. 
Tel: 416.644.4226 • Toll Free: 1.888.425.7255 x 527

 

From: Nicholas Caton [mailto:ncaton at catonenergy.com] 
Sent: Monday, December 22, 2014 4:46 PM
To: Jones, Christopher; Omar ElRawy; equest
Subject: RE: [Equest-users] Exterior Air Film

 

The LV-D reports (and others touching on windows/constructions) do indeed include an exterior air film.  I don’t know of a way to change that.

 

A quick screengrab of your (correct) inputs and a one-line explanation of that fact is probably your most expedient path forward for a LEED review response.

 

~Nick

 

NICK CATON, P.E.
Owner

 

Caton Energy Consulting
  1150 N. 192nd St., #4-202

  Shoreline, WA 98133
  office:  785.410.3317

www.catonenergy.com

 

From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Jones, Christopher
Sent: Monday, December 22, 2014 8:23 AM
To: Omar ElRawy; equest
Subject: Re: [Equest-users] Exterior Air Film

 

For glazing, you have to enter the GLASS-CONDUCTANCE into eQuest, not the glazing U-value.  See page 65 in the DOE22Vol2-Dictionary reference manual available for download at doe2.com <http://doe2.com/> .

 

 

Christopher Jones, P.Eng. 
Tel: 416.644.4226 • Toll Free: 1.888.425.7255 x 527

 

From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Omar ElRawy
Sent: Monday, December 22, 2014 7:28 AM
To: equest
Subject: [Equest-users] Exterior Air Film

 

Dear all,

            I have a problem reporting baseline case for LEED submission, where the exterior walls and windows U-values in Report LV-D appears less than the ASHRAE G 90.1 values that I did enter to the model, and this is (as I think) because eQuest adds the exterior air-film effect to the assembly during the run. 

 

My question is that; can I disable this eQuest calculation to see my input directly in LV-D report or not?

Thanks,

Omar ElRawy, LEED AP BD+C
LEED Project Manager
EA Sustainable Building Consultants
http://www.ea-buildingconsultants.com/ <http://www.ea-buildingconsultants.com/> 

 


_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send  a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG




______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
______________________________________________________________________

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20160801/bc84b2cd/attachment-0005.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 255 bytes
Desc: image001.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20160801/bc84b2cd/attachment-0025.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.png
Type: image/png
Size: 7893 bytes
Desc: image002.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20160801/bc84b2cd/attachment-0026.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.png
Type: image/png
Size: 29188 bytes
Desc: image003.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20160801/bc84b2cd/attachment-0027.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image004.png
Type: image/png
Size: 67275 bytes
Desc: image004.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20160801/bc84b2cd/attachment-0028.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image005.jpg
Type: image/jpeg
Size: 46723 bytes
Desc: image005.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20160801/bc84b2cd/attachment-0002.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image006.png
Type: image/png
Size: 40883 bytes
Desc: image006.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20160801/bc84b2cd/attachment-0029.png>


More information about the Equest-users mailing list