[Equest-users] PSZ Dehumidification reheat?
Michael Campbell via Equest-users
equest-users at lists.onebuilding.org
Tue Apr 26 05:35:44 PDT 2016
Thanks for the input Bill. This is actually very similar to how I have my
system set up right now. My issue is that if I have ZONE-HEAT-SOURCE as
electric with 18F DT I will get the same exact results as if I have
ZONE-HEAT-SOURCE as "Not Installed." My PSZ DOAS is only attached to my
dummy space... could this be why?
On Mon, Apr 25, 2016 at 5:23 PM, Bishop, Bill <bbishop at pathfinder-ea.com>
wrote:
> Hi Mike,
>
> With a PSZ, your ZONE-HEAT-SOURCE will only get applied at your subzones
> (non-control zone(s)). The heat pump will operate to satisfy both the
> control zone thermostat and the humidity requirement based on the RH of the
> return air. For a DOAS heat pump PSZ serving multiple zones, the supply air
> temperature at the control zone will vary considerably on a sub-hourly
> basis as the heat pump cycles between cooling and heating mode to prevent
> overcooling the zone, but reheat can be used to keep the SAT to the
> subzones relatively constant. Give this input a try to get you close to
> your description:
>
> *"DOAS me no questions" = SYSTEM *
>
> * TYPE = PSZ*
>
> * HEAT-SOURCE = HEAT-PUMP*
>
> * ZONE-HEAT-SOURCE = ELECTRIC*
>
> * MAX-SUPPLY-T = 73*
>
> * MIN-SUPPLY-T = 55*
>
> * MAX-HUMIDITY = 60*
>
> * REHEAT-DELTA-T = 18*
>
>
>
> Regards,
>
> ~Bill
>
>
>
> *William Bishop, PE, BEMP, BEAP, CEM, LEED AP **|** Pathfinder Engineers
> & Architects LLP*
>
> *Senior Energy Engineer*
>
>
>
>
>
> 134 South Fitzhugh Street Rochester, NY 14608
>
> *T: (585) 698-1956 <%28585%29%20698-1956>* F: (585)
> 325-6005
>
> bbishop at pathfinder-ea.com <wbishop at pathfinder-ea.com>
> www.pathfinder-ea.com
>
> [image: http://png-5.findicons.com/files/icons/977/rrze/720/globe.png]Carbon
> Fee and Dividend - simple, effective, and market-based.
>
>
>
> *From:* Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] *On
> Behalf Of *Michael Campbell via Equest-users
> *Sent:* Monday, April 25, 2016 9:17 AM
> *To:* equest-users at lists.onebuilding.org
> *Subject:* [Equest-users] PSZ Dehumidification reheat?
>
>
>
> Hello,
>
> Hoping someone can help me out here. I am modeling a PSZ heat pump with
> ERV as a DOAS. It is supposed to dehumidify to keep RH below 60%. It
> appears to be doing this currently based on the hourly reports. However, I
> need to also model an electric resistance coil that will reheat the
> dehumidified air back up to 73F. Does anyone know how I can accomplish
> this with PSZ? I've tried making "ZONE-HEAT-SOURCE" electric resistance,
> but this does not seem to have any effect at all. I also thought about
> applying preheat to the zones served by the DOAS but it states in the item
> description that preheat is appled to the mixed air flow, not just outside
> air so that won't work for me. Any recommendations?
>
> Thank you,
>
> Mike C
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20160426/2be8b2e0/attachment-0002.htm>
More information about the Equest-users
mailing list