[Equest-users] Using PSZ as DOAS?
Nathan Miller via Equest-users
equest-users at lists.onebuilding.org
Thu Apr 21 07:04:53 PDT 2016
I’m just getting back from a vacation, so sorry for the delayed response on this, but there is a way to force a PSZ system to have discharge air temp control. I’m ignoring the ERV portion of your system right now because that complicates matters.
We use this methodology frequently to model corridor/DOAS systems for multifamily projects. Note that this is only accounting for the energy use of the ventilation air. I’m assuming you will model separate systems for the dwelling units to meet the space conditioning demands (basically it looks like you are supplying neutral vent air, which won’t have much impact on how much load shows up on the in-unit VRF).
1) Create a new space (call it “DOAS Dummy space” or something). Make the size minimal- 1’x1’x1’ works well. Make sure there are no internal loads or walls/roofs/floors assigned to it.
2) Create a new zone (call it “DOAS Dummy zone” or something). Assign the dummy space to the zone. Give the zone Heating/Cooling t-stat schedules that are equivalent to the discharge air temp range you want to control to. In your example you’d have a 24/7 heating schedule at 73 deg F and 24/7 cooling schedule at 75 deg.
3) Give this dummy zone control of your PSZ unit. Because there are no loads in the space, the PSZ unit should discharge air between 73-75 Deg to keep that 1 cubic foot space at the desired temp range. You can confirm this by looking at hourly reports.
4) If you have multiple conditioned zones assigned to the unit, they will “come along for the ride” meaning they will get the same supply air temp, with no consideration for their space temps. You may have to assign a realistic “relaxed” t-stat schedule to those space to avoid lots of unmet load hours.
5) Depending on how the vent air is being distributed in the dwelling units, you might have to play around with how the fan power is assigned. For example- do the in unit fans have to run 24/7 to distribute the vent air, or do they only cycle to meet the loads in the space?
Having an ERV can significantly complicate this modeling method depending on where the return air is coming from (and the expected temperature of that return air) for the heat-recovery.
Nathan Miller, PE, LEED AP BD+C – Mechanical Engineer/Senior Energy Analyst
RUSHING | D 206-788-4577 | O 206-285-7100
www.rushingco.com<http://www.rushingco.com/>
From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Michael Campbell via Equest-users
Sent: Monday, April 18, 2016 4:07 PM
To: Elizabeth Gillmor <elizabeth at energetics-eng.com>
Cc: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Using PSZ as DOAS?
Thank you Elizabeth!
On Mon, Apr 18, 2016 at 3:30 PM, Elizabeth Gillmor <elizabeth at energetics-eng.com<mailto:elizabeth at energetics-eng.com>> wrote:
Hi Michael,
I have always used a Powered Induction Unit system type for DOAS systems. (Or standard Induction Unit system if CHW instead of DX.) This should give you the control and heat source capability that you need.
Good luck!
Elizabeth
Elizabeth Gillmor PE, BEMP, LC, LEED AP
e n e r g e t i c s consulting engineers, llc
energetics-eng.com<http://energetics-eng.com> | 303.619.0091<tel:303.619.0091>
On Mon, Apr 18, 2016 at 12:52 PM, Michael Campbell via Equest-users <equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>> wrote:
I also have a follow up question. Is there any system type that I can use which will allow me to select heat pump as the heating source and also be controlled by the supply air temperature? It appears that constant temp control would be available for PMZS but I cannot use heat pump heat with this type of system.
On Mon, Apr 18, 2016 at 9:37 AM, Michael Campbell <mcamp1206 at gmail.com<mailto:mcamp1206 at gmail.com>> wrote:
Hello,
I'm trying to use a PSZ system as a DOAS. The system I'm trying to model uses and ERV tied to a heat pump to supply fresh air to common areas and dwelling units. There are then separate VRF systems for space conditioning. The DOAS is designed to supply a constant temperature outside air (73F when heating, 75F when cooling). How can I make the PSZ system in equest supply a constant temperature supply air?
Thank you
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG<mailto:EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20160421/e3d93b25/attachment-0002.htm>
More information about the Equest-users
mailing list