I'm assuming that you're asking if it's possible to use multiple utility rates for the same fuel type within a model.  If so, the answer is yes.
In order to do so you'll have to follow a few steps.  For all of these steps I'm going to assume that you're creating a separate electric meter although the steps would be the same for any other fuel meter.
1.       Create a second electric meter (Utility & Economics > Electric Meters > Create Electric Meter...).
2.       Assign the meter to the appropriate end-uses in all zones which will be using the secondary utility rate (Air-Side HVAC > Thermal Zone > Meters).
3.       Create two utility rates (Utility & Economics > Utility Rates > Create Utility Rate...) and assign the each meter to the appropriate utility rate.
Hopefully that helps.
Cheers,
Luke McGuire, PE, BEMP, LEED BD+C
Senior Building Energy Analyst
www.ecoworks-studio.com
Ecoworks Studio  I  LEED Proven Provider
619 Edgewood Ave SE, Suite 200, Atlanta, GA 30312
p: 404.793.2003
e: luke at ecoworks-studio.com<mailto:luke at ecoworks-studio.com>
From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Juan Carlos Sanabria F.
Sent: Monday, April 4, 2016 17:03
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] 2 Different Rates
Hi all, I need to know if you can model on eQuest with two different rates? If it's possible please explain how to do it thanks.
Kind regards,
  Ing. Juan Carlos Sanabria F.
   Tel.: (506) 2256-7020
  Fax: (506) 2256-5608
  From USA: 1-305-433-3668
  Calle 30, Avenida 0 y 2. San José, Costa Rica
[Logo CTS firma]
Este correo puede contener información protegida por el secreto profesional. Si usted no es la persona a quien va dirigido, por favor tome en cuenta que su divulgación, distribución o reproducción es estrictamente prohibida. Cualquier persona que reciba este mensaje por error debe notificarlo inmediatamente al remitente vía telefónica o correo electrónico y borrarlo permanentemente de su computador. Los comentarios plasmados en este correo son del remitente solamente y no reflejan necesariamente la posición de CTS S.A.
Por favor considere su responsabilidad con el medio ambiente antes de imprimir este correo electrónico
----------------------------------------------------------------------------------------------------------------
This mail may contain information that is legally privileged, confidential or exempt from disclosure.  If you are not the intended recipient, please note that any dissemination, distribution or copying of this message is strictly prohibited.  Anyone who receives this message in error should notify the sender immediately by telephone or by e-mail and delete it permanently from their computer.  The opinions above are those of the author and do not necessarily reflect the position of CTS S.A.
Please consider your environmental responsibility before printing this e-mail
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20160404/cc48fcb9/attachment-0005.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 5449 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20160404/cc48fcb9/attachment-0005.jpg>
    
    
More information about the Equest-users
mailing list