[Equest-users] eQuest & NoteTab Question
Julien Marrec
julien.marrec at gmail.com
Thu Sep 10 00:26:52 PDT 2015
Jesse,
I've created an example here : https://regex101.com/r/iZ5jO8/1. This should
really help understanding how I'm getting the result, by decomposing each
step of the regex.
Note that I added names to capturing groups, you don't have to do that, you
could use just positional:
Look for: (SYSTEM *\n *?TYPE *= )HP(.*?FURNACE-HIR +?=
[.0-9]+)\n(.*?\.\.\n)(\".*?\")
Replace with: \1PSZ\2\n CONTROL-ZONE = \4\n\3\4
A few things: dot (.) has to match newline characters for it to work.
Also, in notepad++ to replace with named capturing groups, you use $+{Name}
You have to replace \n (unix convention) by \r\n.
Anyways, for notepad++ try:
Search:
(?<System1>SYSTEM *\r\n *?TYPE *= )HP(?<System2>.*?FURNACE-HIR +?=
[.0-9]+)\r\n(?<System3>.*?\.\.\r
\n)(?<ZoneName>\".*?\")
Replace with:
$+{System1}PSZ$+{System2}\n CONTROL-ZONE =
$+{ZoneName}\n$+{System3}$+{ZoneName}
I've loaded it up in eQuest, seems to do the job just fine. Let me know if
you are trouble implementing. I've also attached the file back, but I'd be
a shame to not take this as an opportunity to learn regex
PS: By the way, you should really use floor multipliers.
Best,
Julien
--
Julien Marrec, EBCP, BPI MFBA
Energy&Sustainability Engineer
T: +33 6 95 14 42 13
LinkedIn (en) : www.linkedin.com/in/julienmarrec
LinkedIn (fr) : www.linkedin.com/in/julienmarrec/fr
<http://www.linkedin.com/in/julienmarrec>
2015-09-09 22:32 GMT+02:00 Phillips, Jesse <jphillips at rdkengineers.com>:
> Thanks Julien.
>
>
>
> I’ve attached the inp file. I am not familiar with Regex at all but I’ll
> check out that website. If you could send me some examples tomorrow
> though, that would be great!
>
>
>
> thanks,
>
>
>
> Jesse
>
>
>
> *From:* Julien Marrec [mailto:julien.marrec at gmail.com]
> *Sent:* Wednesday, September 09, 2015 4:27 PM
> *To:* Phillips, Jesse <jphillips at RDKEngineers.com>
> *Cc:* Nathan Miller <nathanm at rushingco.com>;
> equest-users at lists.onebuilding.org
> *Subject:* Re: [Equest-users] eQuest & NoteTab Question
>
>
>
> Hi,
>
> I don't know Notetab, but as long as you have one system for each zone,
> this is pretty easy if your editor supports Regular Expressions (Regex).
>
> As you might know, inp files has what I call a positional input for a few
> things (space > surface > window/door, same for system > zone). Meaning if
> you find something that is a system, everything that's right after (which
> are zones) below to this system until you find another system. As opposed
> to having a keyword linking those two objects.
>
> So you could use a regex for this job. Especially using positive
> lookaheads to delimit a single system and its zone (singular here, could be
> plural).
>
> If you do have only a single zone per system, it's even easier.
>
> Just look for a system and it's zone below it.
>
> If you are not familiar with regex and can't manage to build it, let me
> know, I'll try to find a few tomorrow to help you out (send me your file or
> an extract or it so I don't have to create a dummy one to play with it).
>
> By the way, here's a website I wish existed when I first started playing
> with regex: https://regex101.com/. Fyi, Notepad++ uses the prce engine.
>
> Cheers,
>
> Julien
>
>
>
>
> --
> Julien Marrec, EBCP, BPI MFBA
> Energy&Sustainability Engineer
> T: +33 6 95 14 42 13
>
> LinkedIn (en) : www.linkedin.com/in/julienmarrec
> LinkedIn (fr) : www.linkedin.com/in/julienmarrec/fr
>
>
>
> 2015-09-09 22:04 GMT+02:00 Phillips, Jesse <jphillips at rdkengineers.com>:
>
> I don’t think you can create macros in NoteTab. What would that macro
> look like in boxer?
>
>
>
> Jesse Phillips
>
> Energy Engineer
>
> RDK Engineers
>
> P: 857-221-5957
>
>
>
> *From:* Nathan Miller [mailto:nathanm at rushingco.com]
> *Sent:* Wednesday, September 09, 2015 3:38 PM
> *To:* Phillips, Jesse <jphillips at RDKEngineers.com>;
> equest-users at lists.onebuilding.org
> *Subject:* RE: eQuest & NoteTab Question
>
>
>
> Can you create a macro that searches for each instance of “=ZONE”, copies
> the text before the “=” to get the zone name, and the pastes in the lines
> necessary to create a new single zone system, using the zone name now
> stored in the clip-board to paste in the control zone?
>
>
>
> I’m not familiar with NoteTab, but you can do that in boxer.
>
>
>
>
>
> *Nathan Miller, PE, LEED AP BD+C** – **Mechanical Engineer/Senior Energy
> Analyst*
>
> *RUSHING* | *D* 206-788-4577 | *O* 206-285-7100
>
> *www.rushingco.com <http://www.rushingco.com/>*
>
>
>
> *From:* Equest-users [mailto:equest-users-bounces at lists.onebuilding.org
> <equest-users-bounces at lists.onebuilding.org>] *On Behalf Of *Phillips,
> Jesse
> *Sent:* Wednesday, September 09, 2015 3:23 PM
> *To:* equest-users at lists.onebuilding.org
> *Subject:* [Equest-users] eQuest & NoteTab Question
>
>
>
> Hi,
>
>
>
> I have a model with 233 zones. Right now, every zone has a water loop
> heat pump. I want to convert these all to packaged single zone systems.
> To do this, I am working in the .inp file and doing a “find and replace” in
> NoteTab. The replacing of the system type is easy. I simply search for
> the “type = HP” line and replace with “type = PSZ”. However, the
> PSZ system requires a control zone. I would like each control zone to be
> the zone in which that particular system resides. Which means, for each of
> my 233 zones, I will have a different control zone (i.e. no longer a simple
> find and replace search).
>
>
>
> Does anyone know of a way to use “find and replace” (or another method) to
> set each control zone with the zone name which the system resides?
>
>
>
> This is what the .inp file should look like for a packaged single zone
> system:
>
>
>
> "EL1 Sys1 (PTAC) (G.SSW1)" = SYSTEM
>
> TYPE = PSZ
>
> HEAT-SOURCE = HEAT-PUMP
>
> ZONE-HEAT-SOURCE = NONE
>
> SIZING-RATIO = 1
>
> COOL-SIZING-RATI = 1
>
> MIN-SUPPLY-T = 58
>
> FAN-SCHEDULE = "S1 Sys1 (PTAC) Fan Sch"
>
> CW-LOOP = "DEFAULT-CW"
>
> COOLING-CAPACITY = 15752
>
> COOL-SH-CAP = 11839
>
> HP-SUPP-SOURCE = NONE
>
> FURNACE-HIR = 1.24067
>
> CONTROL-ZONE = "EL1 SSW Perim Zn (G.SSW1)"
>
> C-EER95 = 8.24
>
> C-COP47 = 0.78
>
> C-AFUE = 0.78
>
> C-SF-MTR-TYPE = 1
>
> C-RF-MTR-TYPE = 1
>
> C-OSA-DMPR-CTRL = 1
>
> C-HTG-DUCT-LOCN = *Ceiling Plenum*
>
> C-HTG-DUCT-RVAL = 7
>
> C-CLG-DUCT-LOCN = *Ceiling Plenum*
>
> C-CLG-DUCT-RVAL = 7
>
> C-CLG-CAP-CATEG = 14
>
>
>
> For my next system, everything would be exactly the same except the
> highlighted lines (and so on for all 233 systems):
>
>
>
> "EL1 Sys1 (PTAC) (G.W2)" = SYSTEM
>
> TYPE = PSZ
>
> HEAT-SOURCE = HEAT-PUMP
>
> ZONE-HEAT-SOURCE = NONE
>
> SIZING-RATIO = 1
>
> COOL-SIZING-RATI = 1
>
> MIN-SUPPLY-T = 58
>
> FAN-SCHEDULE = "S1 Sys1 (PTAC) Fan Sch"
>
> CW-LOOP = "DEFAULT-CW"
>
> COOLING-CAPACITY = 15752
>
> COOL-SH-CAP = 11839
>
> HP-SUPP-SOURCE = NONE
>
> FURNACE-HIR = 1.24067
>
> CONTROL-ZONE = "EL1 Sys1 (PTAC) (G.W2)"
>
> C-EER95 = 8.24
>
> C-COP47 = 0.78
>
> C-AFUE = 0.78
>
> C-SF-MTR-TYPE = 1
>
> C-RF-MTR-TYPE = 1
>
> C-OSA-DMPR-CTRL = 1
>
> C-HTG-DUCT-LOCN = *Ceiling Plenum*
>
> C-HTG-DUCT-RVAL = 7
>
> C-CLG-DUCT-LOCN = *Ceiling Plenum*
>
> C-CLG-DUCT-RVAL = 7
>
> C-CLG-CAP-CATEG = 14
>
>
>
>
>
> thank you,
>
>
>
> Jesse Phillips | Energy Engineer
>
>
>
>
>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
>
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20150910/5346f3c1/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: VRF Cool & Heat - 9_9_15.inp
Type: application/octet-stream
Size: 1256950 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20150910/5346f3c1/attachment-0002.obj>
More information about the Equest-users
mailing list