[Equest-users] Unmet hours in residential building
Joe Huang
yjhuang at whiteboxtechnologies.com
Wed Oct 28 18:14:28 PDT 2015
Mike,
Allow me to jump in here a bit. Have you looked at the SV-A report to see what DOE-2.2
has sized for the HVAC system, particularly the supply-cfm and heating/cooling capacities
for the bathroom ?
Joe
Joe Huang
White Box Technologies, Inc.
346 Rheem Blvd., Suite 205A
Moraga CA 94556
yjhuang at whiteboxtechnologies.com
http://weather.whiteboxtechnologies.com for simulation-ready weather data
(o) (925)388-0265
(c) (510)928-2683
"building energy simulations at your fingertips"
On 10/28/2015 1:17 PM, Michael Campbell wrote:
> I've tried different values for the degree day multipliers, into the hundreds. I'm
> trying out different scenarios now to see what works, but I'm still getting unmet
> heating hours in the bathroom.
>
> On Wed, Oct 28, 2015 at 3:57 PM, Julien Marrec <julien.marrec at gmail.com
> <mailto:julien.marrec at gmail.com>> wrote:
>
> Mike,
>
> You have set a zonal exhaust with make up air defined as infiltration? And your
> space linked to the thermal zone has an infiltration defined as ACH with a higher
> value for design days? How much higher?
> Your HVAC is autosized for the zone?
> Do you still have unmet hours for the bathroom?
>
> If this is not doing anything, your HVAC system might be already autosized to a
> greater value due to another parameter such as sizing factor so that the added
> infiltration does nothing.
> Or maybe your zonal fan doesn't actually run? Try and request some hourly variables
> to understand what is going on.
>
> Julien
> Envoyé de mon iPhone
>
> Le 28 oct. 2015 à 20:27, Michael Campbell <mcamp1206 at gmail.com
> <mailto:mcamp1206 at gmail.com>> a écrit :
>
>> Julien,
>>
>> Regarding the infiltration method... I am currently trying to do this with a small
>> bathroom with 50cfm exhaust. This is a core zone. Adjusting the design day values
>> as described in the write-up does not appear to be doing anything. Any thoughts?
>>
>> Thanks,
>> Mike
>>
>> On Thu, Oct 15, 2015 at 11:45 AM, Julien Marrec <julien.marrec at gmail.com
>> <mailto:julien.marrec at gmail.com>> wrote:
>>
>> Michael,
>>
>> First, you're under 300 hours so indeed it's a minor problem.
>>
>> I've only looked at your model very briefly but:
>>
>> * HW loop operation is set to "SNAP" at OA of 60°F. This is causing some
>> minor underheating in shoulder season.
>>
>> * You have local exhaust fan with makeup = infiltration. Basically equest
>> ignores this added infiltration during the sizing, so you have to trick it
>> to take it into account by having a different schedule for sizing (heating
>> AND cooling design days). I've put together my findings on the subject on
>> Unmet Hours here
>> <https://unmethours.com/question/3102/how-do-you-model-exhaust-fans-in-equest/>
>> in some kind of tutorial that I hope is helpful.
>>
>>
>> Do the above and your unmet hours disappear.
>>
>>
>> Additionally:
>>
>> * Throttle range of 0.3°R seems pretty aggressive to me.
>> * when you use baseboards and want to oversize, use the system's sizing ratio
>>
>>
>> Hope this helps,
>> Julien
>>
>>
>> --
>> Julien Marrec, EBCP, BPI MFBA
>> Energy&Sustainability Engineer
>> T: +33 6 95 14 42 13 <tel:%2B33%206%2095%2014%2042%2013>
>>
>> LinkedIn (en) : www.linkedin.com/in/julienmarrec
>> <http://www.linkedin.com/in/julienmarrec>
>> LinkedIn (fr) : www.linkedin.com/in/julienmarrec/fr
>> <http://www.linkedin.com/in/julienmarrec/fr>
>>
>> 2015-10-15 16:30 GMT+02:00 Michael Campbell <mcamp1206 at gmail.com
>> <mailto:mcamp1206 at gmail.com>>:
>>
>> I mistakenly attached the PRD file instead of PD2. Correct files are attached.
>>
>> On Thu, Oct 15, 2015 at 10:16 AM, Michael Campbell <mcamp1206 at gmail.com
>> <mailto:mcamp1206 at gmail.com>> wrote:
>>
>> Hello,
>>
>> I'm having what appears to be a minor issue with unmet hours in a model
>> that I've inherited. My INP and PD2 files are attached. I've tried
>> adjusting the cool sizing ratio and and adjusted infiltration rates and
>> equipment loads with no real effects. Anybody have any ideas?
>>
>> Thanks,
>> Mike Campbell
>>
>>
>>
>> _______________________________________________
>> Equest-users mailing list
>> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
>> To unsubscribe from this mailing list send a blank message to
>> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>> <mailto:EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG>
>>
>>
>>
>
>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20151028/1a6b0d63/attachment-0002.htm>
More information about the Equest-users
mailing list