[Equest-users] Correct Baseline System for Addition
Cam Fitzgerald
cam at energyopportunities.com
Thu Oct 8 04:44:58 PDT 2015
Good morning, Steve,
It doesn't look like anyone took the time to answer your question. It isn't
as grey as you might think. Table G3.1#2 addresses the conditions that must
be met to allow the addition to be modeled without the remainder of the
building. If all these conditions are met, it is reasonable to use only the
addition area to determine the Baseline system type. If the addition systems
are not distinctly separated from the existing building systems, it is
likely that the entire building would need to be modeled (all the listed
conditions would not be met), in which case the total building area
including the existing must be used to determine the Baseline system type.
Hope this helps. Have a great day!
Cam Fitzgerald
Energy Opportunities/a 7group company
From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On
Behalf Of Steve Jacobs
Sent: Wednesday, October 07, 2015 2:36 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Correct Baseline System for Addition
Hi guys,
This might have come up in the past but I could find the conversation.
If I am only certifying/modeling a new addition, is the baseline system type
based on the area of the whole building or only the new addition? Is there
black and white guidelines on this or is it a bit of grey area depending on
how integrated the HVAC in the addition is with the whole building?
Thanks,
Steve