[Equest-users] How to model infrared gas heater
Nicholas Caton
ncaton at catonenergy.com
Wed Oct 7 14:31:01 PDT 2015
Another fast approximation might involve:
- Unit heaters on a per zone basis
- Zeroed out fan energy
- Drop zonal heating setpoint by ~10 degrees from comfort
(reference specified manufacturer recommendations and general guidelines
regarding occupant comfort for the associated controls)
- Assign a unitary efficiency for the “furnace” of the unit
heaters in consideration of what radiant fraction is expected to be
delivered to the space vs. exhausted (for powered IR units only)
- Noting IR heating is commonly leveraged in exterior and
semi-exterior environments where heating the conditioned volume of air
doesn’t make sense due to fast turnover / wind effects: Invest some of the
time you’ve saved so far to give some serious consideration to the
associated infiltration inputs, to accurately capture outside air change
rates
There’s
~Nick
*NICK CATON, P.E.*
*Owner*
*Caton Energy Consulting*
306 N Ferrel
Olathe, KS 66061
office: 785.410.3317
www.catonenergy.com
*From:* Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] *On
Behalf Of *Bishop, Bill
*Sent:* Wednesday, October 07, 2015 3:13 PM
*To:* Humphreys, Matthew; equest-users at lists.onebuilding.org
*Subject:* Re: [Equest-users] How to model infrared gas heater
You can approximate a gas infrared heater by adding baseboard heating to
your system and selecting BASEBOARD-SOURCE = FURNACE.
Regards,
~Bill
*William Bishop, PE, BEMP, BEAP, CEM, LEED AP **|** Pathfinder Engineers &
Architects LLP*
*Senior Energy Engineer*
134 South Fitzhugh Street Rochester, NY 14608
*T: (585) 698-1956 * F: (585) 325-6005
bbishop at pathfinder-ea.com <wbishop at pathfinder-ea.com>
www.pathfinder-ea.com
[image: http://png-5.findicons.com/files/icons/977/rrze/720/globe.png]Carbon
Fee and Dividend - simple, effective, and market-based.
*From:* Equest-users [mailto:equest-users-bounces at lists.onebuilding.org
<equest-users-bounces at lists.onebuilding.org>] *On Behalf Of *Humphreys,
Matthew
*Sent:* Wednesday, October 07, 2015 4:06 PM
*To:* equest-users at lists.onebuilding.org
*Subject:* [Equest-users] How to model infrared gas heater
Does anyone have an idea how to model a gas infrared heater in eQUEST?
*Matthew Humphreys, PE *Mechanical Engineer
Associate
. . . . . . . . . . . . . . . . . . . . . . . . . . . . .
*SSOE Group*
256.585.6269* direct*
256.534.2353 x8676269
*mhumphreys at ssoe.com*
<MHumphreys at ssoe.com>
*We're exploring how advances in cloud technology, design software, and
clash detection are improving collaboration, maximizing efficiency, and
smoothing the road from design to construction: *http://www.ssoe.com/scenes
<http://www.ssoe.com/spring2015>
*Confidentiality Notice:* This e-mail message, including attachments, is
for the sole use of the intended recipient(s) and may contain confidential
and privileged information. It is intended for use by the person(s) to whom
it is addressed. Any unauthorized use, review, dissemination, forwarding,
copying or printing is strictly prohibited. If you received this e-mail in
error, please contact the sender immediately.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20151007/830bd8d6/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 1517 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20151007/830bd8d6/attachment-0004.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.jpg
Type: image/jpeg
Size: 1647 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20151007/830bd8d6/attachment-0005.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.png
Type: image/png
Size: 3856 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20151007/830bd8d6/attachment-0002.png>
More information about the Equest-users
mailing list