[Equest-users] Equipment control
Nicholas Caton
ncaton at catonenergy.com
Wed Oct 7 08:06:27 PDT 2015
Hi Sambhav,
If your EQUIP-CTRL is for chiller sequencing, assign it to the CHW loop to
which the chillers are attached.
If your EQUIP-CTRL is for tower sequencing, assign it to the CW to which
the heat rejection equipment is attached.
~Nick
* NICK CATON, P.E.*
*Owner*
*Caton Energy Consulting*
306 N Ferrel
Olathe, KS 66061
office: 785.410.3317
www.catonenergy.com
*From:* Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] *On
Behalf Of *Sambhav Tiwari
*Sent:* Wednesday, October 07, 2015 12:36 AM
*To:* equest-users
*Subject:* [Equest-users] Equipment control
Hi Friends,
If we give sequencing to chillers by equipment control in the case shall we
assign equipment control only to CHW loop under control tab or to both
loops CHW as well as CW loop under control tab.
Regards
Sambhav