Julien,
Regarding the infiltration method... I am currently trying to do this with
a small bathroom with 50cfm exhaust. This is a core zone. Adjusting the
design day values as described in the write-up does not appear to be doing
anything. Any thoughts?
Thanks,
Mike
On Thu, Oct 15, 2015 at 11:45 AM, Julien Marrec <julien.marrec at gmail.com>
wrote:
> Michael,
>
> First, you're under 300 hours so indeed it's a minor problem.
>
> I've only looked at your model very briefly but:
>
> - HW loop operation is set to "SNAP" at OA of 60°F. This is causing
> some minor underheating in shoulder season.
>
>
> - You have local exhaust fan with makeup = infiltration. Basically
> equest ignores this added infiltration during the sizing, so you have to
> trick it to take it into account by having a different schedule for sizing
> (heating AND cooling design days). I've put together my findings on the
> subject on Unmet Hours here
> <https://unmethours.com/question/3102/how-do-you-model-exhaust-fans-in-equest/>
> in some kind of tutorial that I hope is helpful.
>
>
> Do the above and your unmet hours disappear.
>
>
> Additionally:
>
> - Throttle range of 0.3°R seems pretty aggressive to me.
> - when you use baseboards and want to oversize, use the system's
> sizing ratio
>
>
> Hope this helps,
> Julien
>
>
> --
> Julien Marrec, EBCP, BPI MFBA
> Energy&Sustainability Engineer
> T: +33 6 95 14 42 13
>
> LinkedIn (en) : www.linkedin.com/in/julienmarrec
> LinkedIn (fr) : www.linkedin.com/in/julienmarrec/fr
> <http://www.linkedin.com/in/julienmarrec>
>
> 2015-10-15 16:30 GMT+02:00 Michael Campbell <mcamp1206 at gmail.com>:
>
>> I mistakenly attached the PRD file instead of PD2. Correct files are
>> attached.
>>
>> On Thu, Oct 15, 2015 at 10:16 AM, Michael Campbell <mcamp1206 at gmail.com>
>> wrote:
>>
>>> Hello,
>>>
>>> I'm having what appears to be a minor issue with unmet hours in a model
>>> that I've inherited. My INP and PD2 files are attached. I've tried
>>> adjusting the cool sizing ratio and and adjusted infiltration rates and
>>> equipment loads with no real effects. Anybody have any ideas?
>>>
>>> Thanks,
>>> Mike Campbell
>>>
>>
>>
>> _______________________________________________
>> Equest-users mailing list
>> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
>> To unsubscribe from this mailing list send a blank message to
>> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>>
>>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20151028/235463e5/attachment-0005.htm>
More information about the Equest-users
mailing list