[Equest-users] % LOAD ATTRIBUTED TO OA DELIVERY

Mark Hallman Mark.Hallman at rwdi.com
Fri Oct 16 22:59:52 PDT 2015


Thanks for the feedback, folks!  I agree  --- the best way is as Bill describes.  I’ll take this all under advisement.
Mark.

mark hallman
p.eng. leed ap bd&c
project engineer

mdh at rwdi.com<mailto:mdh at rwdi.com>
519 823 1311 x2494
RWDI:  the science of buildings, structures & the environment.  See what we do HERE<http://www.rwdi.com/#!services3/c1h0m>.

From: Jones, Christopher [mailto:Christopher.r.Jones at wspgroup.com]
Sent: Friday, October 16, 2015 12:12
To: Mark Hallman; equest-users at lists.onebuilding.org
Subject: RE: [Equest-users] % LOAD ATTRIBUTED TO OA DELIVERY

Mark,
Are you in one of RWDI’s Canadian offices? If so, are you reviewing an EE4 model that has heat recovery on a make-up air system serving fan coils or heat pumps?  EE4 uses a work around to approximate heat recovery for make-up air systems serving fan coils and heat pumps.  EE4 defines a “dummy” zone served by the make-up air system then uses the OA-FROM-SYSTEM keywork in each fan coil/heat pump zonal system.  To approximate the effectiveness of the heat recovery, EE4 reduces the specified outdoor air by (1-HReef).  For example, if the make-up air system is design to provide 10,000 cfm of outdoor and the specified heat recovery effectiveness is 70%, then the modeled outdoor air will be 10,000 * (1-0.7) = 3,000 cfm.  This, in addition to the other issues raised by the egroup make it difficult to review the .sim file to determine the accuracy of the model.



[cid:image003.png at 01D09C46.E75BA0D0]
Christopher Jones, P.Eng.
Senior Engineer

WSP Canada Inc.
2300 Yonge Street, Suite 2300
Toronto, ON M4P 1E4
T +1 416-644-4226
F +1 416-487-9766
C +1 416-697-0056

www.wspgroup.com<http://www.wspgroup.com/>

From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Mark Hallman
Sent: Friday, October 16, 2015 11:27 AM
To: 'Shaun Martin'; 'Keith Swartz'; 'Porter, Frederick NOR'; 'Nathan Miller'; 'Daniel Knapp'; equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] % LOAD ATTRIBUTED TO OA DELIVERY

Thanks for all the helpful comments, folks.

Is there anyway of parsing this out without having the model available, just the SIM files?  I’m reviewing results as a 3rd party but don’t have access to the model nor the hourly results.   What I’ve been doing so far is:

Cooling Load without OA = LS-C cooling load
Cooling Load with OA = Plant Cooling Load (SS-D report) + System Cooling Load (Max Cooling elec load from SS-H report)

Tx!
Mark.

mark hallman
p.eng. leed ap bd&c
project engineer

mdh at rwdi.com<mailto:mdh at rwdi.com>
519 823 1311 x2494
RWDI:  the science of buildings, structures & the environment.  See what we do HERE<http://www.rwdi.com/#!services3/c1h0m>.

From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Shaun Martin
Sent: Thursday, October 15, 2015 13:11
To: 'Keith Swartz'; 'Porter, Frederick NOR'; 'Nathan Miller'; 'Daniel Knapp'; equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: Re: [Equest-users] % LOAD ATTRIBUTED TO OA DELIVERY

With MIN-AIR-SCH,  you have to zero out all zone exhausts, because exhaust overrides the schedule.  And, almost every building I work on has ventilation heat recovery, which affects the mixed air temp.  I’m not quite sure what will happen at MIN-AIR-SCH =.001.  Be careful with the control strategy.

Shaun Martin LEED-AP, BEMP
Principal
Shaun Martin Consulting
#90 – 425 Carrall Street
Vancouver, BC  V6B 6E3
p. 604-789-1095


From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Keith Swartz
Sent: Thursday, October 15, 2015 6:51 AM
To: Porter, Frederick NOR <fporter at noresco.com<mailto:fporter at noresco.com>>; Nathan Miller <nathanm at rushingco.com<mailto:nathanm at rushingco.com>>; Daniel Knapp <danielk at arborus.ca<mailto:danielk at arborus.ca>>
Cc: equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: Re: [Equest-users] % LOAD ATTRIBUTED TO OA DELIVERY


Here are details from the help screen:





[cid:image001.png at 01D10805.42E90080]



Keith Swartz, PE | Senior Energy Engineer

Seventhwave | Madison.Chicago.Minneapolis

608.210.7123 seventhwave.org



-----Original Message-----
From: Porter, Frederick NOR [mailto:fporter at noresco.com]
Sent: Wednesday, October 14, 2015 11:46 AM
To: Nathan Miller <nathanm at rushingco.com<mailto:nathanm at rushingco.com>>; Daniel Knapp <danielk at arborus.ca<mailto:danielk at arborus.ca>>
Cc: equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: Re: [Equest-users] % LOAD ATTRIBUTED TO OA DELIVERY



All,

Bill describes  how to do this easily in his initial reply. The MIN-AIR-SCH at the system level over-rides the zone OA inputs (Actually, I'm not positive what happens if there are zone exhaust fans in the model! I avoid these like the plague.) MOST AHU models should have a SYSTEM MIN-AIR-SCH which is either -999  (default, model uses sum of zone OA  flows, or system MIN-OA if there are no zone OA flows) during occupied periods or 0.0 (no econ, no damper leakage) or 0.01-0.03 or so (leakage, economizer allowed)  for hours when the system can cycle on during unoccupied periods. Changing this one system schedule to one with zero or 0.01 at all hours is absolutely the easiest way to do a run with "no" OA.  It is very easy to do as a "parametric."



Fred



-----Original Message-----

From: Nathan Miller [mailto:nathanm at rushingco.com]

Sent: Wednesday, October 14, 2015 7:35 AM

To: Daniel Knapp; Porter, Frederick NOR

Cc: equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>

Subject: [External] RE: [Equest-users] % LOAD ATTRIBUTED TO OA DELIVERY



Depending on your system, you can allow economizer by assigning an arbirtrary, tiny OA CFM (like 0.01 CFM) to the zone. Then there is essentially no OA being delivered in normal operation, but economizer can be engaged.





Nathan Miller, PE, LEED AP BD+C - Mechanical Engineer/Senior Energy Analyst RUSHING | D 206-788-4577 | O 206-285-7100 www.rushingco.com<http://www.rushingco.com>



-----Original Message-----

From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Daniel Knapp

Sent: Wednesday, October 14, 2015 9:32 AM

To: Porter, Frederick NOR <fporter at noresco.com<mailto:fporter at noresco.com>>

Cc: equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>

Subject: Re: [Equest-users] % LOAD ATTRIBUTED TO OA DELIVERY



There should be a way to run without outdoor air while still allowing economizer operation. If you set the outdoor air to zero at the zone level, and allow for an economizer at the system level, I imagine that eQUEST would do this. It would be worth looking at the hourly reports for the OA fraction at the system level to confirm that the outdoor air flow rate is behaving as expected.



All the best,



Dan





-

Daniel Knapp, PhD, PPhys, LEED(r) AP O+M danielk at arborus.ca<mailto:danielk at arborus.ca>



Arborus Consulting

Energy Strategies for the Built Environment www.arborus.ca<http://www.arborus.ca>

76 Chamberlain Avenue

Ottawa, ON, K1S 1V9

Phone: (613) 234-7178 ext. 113

Fax: (613) 234-0740









> On Oct 13, 2015, at 7:37 PM, Porter, Frederick NOR <fporter at noresco.com<mailto:fporter at noresco.com>> wrote:

>

> Mark,

> I'd stick with Bill's original suggestion. Run the model with "zero" OA and compare to the "proposed" case. Seem's close enough to me... As Joe notes, in the end there can be some ambiguity about exactly how the total hourly coil  load should be apportioned. If you are curious about how the model works on an hourly basis, generate some hourly AHU reports (coil loads, MA and SA conditions), from the two runs. Do not just compare L- and S- loads reports. L- reports are at a constant temp, and in addition to OA, do not include any "false" loads from overcool/reheat, fan heat... I'm sure there are more.

>

> One thing to check first; make sure your coil capacity with the OA is large enough to fully condition the air at each timestep. Also, for models that use it, set the "cooling coil/cool control range" to 0.1F or so to avoid possible small changes in the coil leaving air temps between runs.

>

> I think Trace and HAP provide a "ventilation load" in reports they probably do some intermediate calculation each hour for the AHU w/ and w/o OA. They may even allocate it per zone.

>

> Food for thought: In buildings without high exhaust flows, some of the "OA ventilation load," imposed by OA at the AHU, actually offsets some infiltration load that would occur throughout the building if that OA was not brought in, or ended up in an ERV somehow. "Simple" simulation programs attempt to account for this with schedules that are applied to infiltration based on initial AHU operating schedules, however those infiltration schedules are not directly linked to OA schedules. I've seen "efficient" buildings that were not adequately pressurized because the nifty heat recovery ventilator exhaust fan used up all the air that would otherwise kept the building pressurized.

>

> Fred

> Fred Porter, BEMP, LEED(c) AP

> Principal Engineer

> Sustainability Services

> NORESCO

> 2540 Frontier Ave, Suite 100, Boulder, CO  80301 Phone 303.459.7425 |

> Cell 303.748.4536  |  fporter at noresco.com<mailto:fporter at noresco.com> www.noresco.com<http://www.noresco.com>

>

> Confidentiality Note:

> Dissemination, distribution or copying of this e-mail or the information herein by anyone other than the intended recipient, or an employee or agent of a system responsible for delivering the message to the intended recipient, is prohibited. If you are not the intended recipient, please inform the sender and delete all copies.

>

>

>

>

> From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org]

> On Behalf Of Joe Huang

> Sent: Tuesday, October 13, 2015 1:58 PM

> To: equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>

> Subject: [External] Re: [Equest-users] % LOAD ATTRIBUTED TO OA

> DELIVERY

>

> There are so many differences between what's reported in the LS-D and SS-D that I would not use this method for anything more than an extremely crude look at the load attributable to OA.  In Loads,  all the heat flows are calculated at the reference temperature (TLOADS) and counted as Cooling if the net space load that hour is positive or Heating if it's negative.  In Systems, these loads are corrected to the actual zone temperature and the load from OA and interzone heat transfer added, while solving for the zone temperature. If the zone temperature is outside the thermostat deadband, a deficit would be considered a heating load and an excess as a cooling  load on the HVAC system.

>

> There's a much better way to get the OA load, but it would take some work, either with a User-Function, which unfortunately is not available in DOE-2.2 (although I've heard that Expressions could do much the same thing...), or by post-processing hourly outputs.  Print out an Hourly Report with the following parameters: Outdoor Air Temp (To), Room Air Temperature (Trm), Outside Air CFM, and the Zone Load.  Then, use Excel or awk ( my favorite :-) :-) ) to calculate the load due to the OA as (Trm-To)*CFM*Cp of air .  This can then be compared to the Zone Load, but you'll notice some anomalies  such as during the swing season when the OA Load is actually "free cooling".   You'll then have to decide how to attribute the OA heat flows to the HVAC loads, which can be tricky.

>

> Various people, including me, Dan Fisher, Jason Glazer, etc., have

> wandered into this area of deriving component loads, and have found

> that it ultimately raises philosophical questions.  :-) :-)

>

> Joe

> Joe Huang

> White Box Technologies, Inc.

> 346 Rheem Blvd., Suite 205A

> Moraga CA 94556

> yjhuang at whiteboxtechnologies.com<mailto:yjhuang at whiteboxtechnologies.com>

> http://weather.whiteboxtechnologies.com for simulation-ready weather

> data

> (o) (925)388-0265

> (c) (510)928-2683

> "building energy simulations at your fingertips"

> On 10/13/2015 9:02 AM, Keith Swartz wrote:

> Good point, David. The system report adds more than just ventilation load to the space load.

>

> Keith Swartz, PE | Senior Energy Engineer Seventhwave |

> Madison.Chicago.Minneapolis

> 608.210.7123 seventhwave.org

>

> From: David Eldridge [mailto:DEldridge at grummanbutkus.com]

> Sent: Tuesday, October 13, 2015 10:47 AM

> To: Keith Swartz <KSwartz at seventhwave.org<mailto:KSwartz at seventhwave.org>>; Mark.Hallman at rwdi.com<mailto:Mark.Hallman at rwdi.com>

> Subject: RE: [Equest-users] % LOAD ATTRIBUTED TO OA DELIVERY

>

> I'm not sure if that will exactly give the ventilation loads - the "L" reports are the building space loads, but the "S" reports will include other system effects such as fan heat, reheat, heat gain to the return air, so that the difference might not exactly be a ventilation load, and might be pretty far from an OA-only load.

>

> If there is a preheat coil, you can set up a report to trend that coil's load if you are after the heating loads. You could trend the cooling coil load as well, but this is a function of economizer operation and outside air temperature as well.

>

> David

>

>

>

>

> David S. Eldridge, Jr., P.E., LEED AP BD+C, BEMP, BEAP, HBDP

> Grumman/Butkus Associates

>

>

>

> From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org]

> On Behalf Of Keith Swartz

> Sent: Monday, October 12, 2015 8:55 AM

> To: equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>

> Subject: Re: [Equest-users] % LOAD ATTRIBUTED TO OA DELIVERY

>

> Mark,

>

> Look at the differences between values in reports LS-D and SS-D. SS-D

> includes ventilation. LS-D does not. (The first letter "S" stands for

> "system." "L" is for "load," the load in the space.)

>

> Keith Swartz, PE | Senior Energy Engineer Seventhwave |

> Madison.Chicago.Minneapolis

> 608.210.7123 seventhwave.org

>

> From: Shaun Martin [mailto:smartin at shaunmartinconsulting.com]

> Sent: Friday, October 09, 2015 12:13 PM

> To: 'Mark Hallman' <Mark.Hallman at rwdi.com<mailto:Mark.Hallman at rwdi.com>>; 'Bishop, Bill'

> <bbishop at pathfinder-ea.com<mailto:bbishop at pathfinder-ea.com>>; equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>

> Subject: Re: [Equest-users] % LOAD ATTRIBUTED TO OA DELIVERY

>

> Hi Mark,

>

> You can use hourly reports to pull out the outside air volume (variable PO) plus the supply and return volumes and temperatures. Then off to a spreadsheet.

>

> Or, if you're feeling ambitious, you could write an input function (see Topics).

>

> Shaun

>

> Shaun Martin LEED-AP, BEMP

> Principal

> Shaun Martin Consulting

> #90 - 425 Carrall Street

> Vancouver, BC  V6B 6E3

> p. 604-789-1095

>

>

>

>

> From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org]

> On Behalf Of Mark Hallman

> Sent: Wednesday, October 7, 2015 7:59 PM

> To: 'Bishop, Bill' <bbishop at pathfinder-ea.com<mailto:bbishop at pathfinder-ea.com>>;

> 'equest-users at lists.onebuilding.org'

> <equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>>

> Subject: Re: [Equest-users] % LOAD ATTRIBUTED TO OA DELIVERY

>

> Thanks Bill, nice tip.  Any way of parsing it out without running two simulations?

>

> Tx!

> Mark.

>

> mark hallman

> p.eng. leed ap bd&c

> project engineer

>

> mdh at rwdi.com<mailto:mdh at rwdi.com>

> 519 823 1311 x2494

> RWDI:  the science of buildings, structures & the environment.  See what we do HERE.

>

> From: Bishop, Bill [mailto:bbishop at pathfinder-ea.com]

> Sent: Wednesday, October 07, 2015 11:12

> To: Mark Hallman; 'equest-users at lists.onebuilding.org'

> Subject: RE: % LOAD ATTRIBUTED TO OA DELIVERY

>

> One way would be to create a MIN-AIR-SCH with all hourly values set to 0 (or 0.001 to activate economizer), apply it to all SYSTEMs and use the difference in the outputs.

>

> Regards,

> ~Bill

>

> William Bishop, PE, BEMP, BEAP, CEM, LEED AP | Pathfinder Engineers &

> Architects LLP Senior Energy Engineer <image001.jpg>  <image002.jpg>

>

> 134 South Fitzhugh Street                 Rochester, NY 14608

> T: (585) 698-1956                        F: (585) 325-6005

> bbishop at pathfinder-ea.com<mailto:bbishop at pathfinder-ea.com>             www.pathfinder-ea.com<http://www.pathfinder-ea.com>

> <image003.png>Carbon Fee and Dividend - simple, effective, and market-based.

>

>

> From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org]

> On Behalf Of Mark Hallman

> Sent: Wednesday, October 07, 2015 10:59 AM

> To: 'equest-users at lists.onebuilding.org'

> <equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>>

> Subject: [Equest-users] % LOAD ATTRIBUTED TO OA DELIVERY

>

> Hi there,

>

> Is there a way to accurately parse out from the eQUEST output file the percentage of the cooling and heating load that is attributed to OA delivery?   Any advice would be appreciated.

>

> Thanks in advance!

> Mark Hallman.

>

>

>

>

> mark hallman

> p.eng. leed ap bd&c

> project engineer

>

> mdh at rwdi.com<mailto:mdh at rwdi.com>

> 519 823 1311 x2494

> RWDI:  the science of buildings, structures & the environment.  See what we do HERE.

>

>

>

>

> _______________________________________________

> Equest-users mailing list

> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org

> To unsubscribe from this mailing list send  a blank message to

> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG<mailto:EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG>

>

> _______________________________________________

> Equest-users mailing list

> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org

> To unsubscribe from this mailing list send  a blank message to

> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG<mailto:EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG>



_______________________________________________

Equest-users mailing list

http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org

To unsubscribe from this mailing list send  a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG<mailto:EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG>



________________________________

You are receiving this communication because you are listed as a current WSP contact. Should you have any questions regarding WSP’s electronic communications policy, please consult our Anti-Spam Commitment www.wspgroup.com/casl. For any concern or if you believe you should not be receiving this message, please forward this message to us at caslcompliance at wspgroup.com<mailto:caslcompliance at wspgroup.com> so that we can promptly address your request. This message is intended only for the use of the individual or entity to which it is addressed, and may contain information which is privileged, confidential, proprietary or exempt from disclosure under applicable law. If you are not the intended recipient or the person responsible for delivering the message to the intended recipient, you are strictly prohibited from disclosing, distributing, copying or in any way using this message. If you have received this communication in error, please notify the sender, and destroy and delete any copies you may have received.

WSP provides professional land surveying services through the following entities: WSP Surveys (AB) Limited Partnership and WSP Surveys (BC) Limited Partnership
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20151017/7e1d090f/attachment-0005.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 6574 bytes
Desc: image001.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20151017/7e1d090f/attachment-0010.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.png
Type: image/png
Size: 168088 bytes
Desc: image002.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20151017/7e1d090f/attachment-0011.png>


More information about the Equest-users mailing list