[Equest-users] % LOAD ATTRIBUTED TO OA DELIVERY
Keith Swartz
KSwartz at seventhwave.org
Tue Oct 13 09:02:31 PDT 2015
Good point, David. The system report adds more than just ventilation load to the space load.
Keith Swartz, PE | Senior Energy Engineer
Seventhwave | Madison.Chicago.Minneapolis
608.210.7123 seventhwave.org
From: David Eldridge [mailto:DEldridge at grummanbutkus.com]
Sent: Tuesday, October 13, 2015 10:47 AM
To: Keith Swartz <KSwartz at seventhwave.org>; Mark.Hallman at rwdi.com
Subject: RE: [Equest-users] % LOAD ATTRIBUTED TO OA DELIVERY
I'm not sure if that will exactly give the ventilation loads - the "L" reports are the building space loads, but the "S" reports will include other system effects such as fan heat, reheat, heat gain to the return air, so that the difference might not exactly be a ventilation load, and might be pretty far from an OA-only load.
If there is a preheat coil, you can set up a report to trend that coil's load if you are after the heating loads. You could trend the cooling coil load as well, but this is a function of economizer operation and outside air temperature as well.
David
David S. Eldridge, Jr., P.E., LEED AP BD+C, BEMP, BEAP, HBDP
Grumman/Butkus Associates
From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Keith Swartz
Sent: Monday, October 12, 2015 8:55 AM
To: equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: Re: [Equest-users] % LOAD ATTRIBUTED TO OA DELIVERY
Mark,
Look at the differences between values in reports LS-D and SS-D. SS-D includes ventilation. LS-D does not. (The first letter "S" stands for "system." "L" is for "load," the load in the space.)
Keith Swartz, PE | Senior Energy Engineer
Seventhwave | Madison.Chicago.Minneapolis
608.210.7123 seventhwave.org
From: Shaun Martin [mailto:smartin at shaunmartinconsulting.com]
Sent: Friday, October 09, 2015 12:13 PM
To: 'Mark Hallman' <Mark.Hallman at rwdi.com<mailto:Mark.Hallman at rwdi.com>>; 'Bishop, Bill' <bbishop at pathfinder-ea.com<mailto:bbishop at pathfinder-ea.com>>; equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: Re: [Equest-users] % LOAD ATTRIBUTED TO OA DELIVERY
Hi Mark,
You can use hourly reports to pull out the outside air volume (variable PO) plus the supply and return volumes and temperatures. Then off to a spreadsheet.
Or, if you're feeling ambitious, you could write an input function (see Topics).
Shaun
Shaun Martin LEED-AP, BEMP
Principal
Shaun Martin Consulting
#90 - 425 Carrall Street
Vancouver, BC V6B 6E3
p. 604-789-1095
From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Mark Hallman
Sent: Wednesday, October 7, 2015 7:59 PM
To: 'Bishop, Bill' <bbishop at pathfinder-ea.com<mailto:bbishop at pathfinder-ea.com>>; 'equest-users at lists.onebuilding.org' <equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>>
Subject: Re: [Equest-users] % LOAD ATTRIBUTED TO OA DELIVERY
Thanks Bill, nice tip. Any way of parsing it out without running two simulations?
Tx!
Mark.
mark hallman
p.eng. leed ap bd&c
project engineer
mdh at rwdi.com<mailto:mdh at rwdi.com>
519 823 1311 x2494
RWDI: the science of buildings, structures & the environment. See what we do HERE<http://www.rwdi.com/#!services3/c1h0m>.
From: Bishop, Bill [mailto:bbishop at pathfinder-ea.com]
Sent: Wednesday, October 07, 2015 11:12
To: Mark Hallman; 'equest-users at lists.onebuilding.org'
Subject: RE: % LOAD ATTRIBUTED TO OA DELIVERY
One way would be to create a MIN-AIR-SCH with all hourly values set to 0 (or 0.001 to activate economizer), apply it to all SYSTEMs and use the difference in the outputs.
Regards,
~Bill
William Bishop, PE, BEMP, BEAP, CEM, LEED AP | Pathfinder Engineers & Architects LLP
Senior Energy Engineer
[cid:image001.jpg at 01D104F5.971C54D0] [cid:image002.jpg at 01D104F5.971C54D0]
134 South Fitzhugh Street Rochester, NY 14608
T: (585) 698-1956 F: (585) 325-6005
bbishop at pathfinder-ea.com<mailto:wbishop at pathfinder-ea.com> www.pathfinder-ea.com<http://www.pathfinder-ea.com/>
[http://png-5.findicons.com/files/icons/977/rrze/720/globe.png]Carbon Fee and Dividend - simple, effective, and market-based.
From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Mark Hallman
Sent: Wednesday, October 07, 2015 10:59 AM
To: 'equest-users at lists.onebuilding.org' <equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>>
Subject: [Equest-users] % LOAD ATTRIBUTED TO OA DELIVERY
Hi there,
Is there a way to accurately parse out from the eQUEST output file the percentage of the cooling and heating load that is attributed to OA delivery? Any advice would be appreciated.
Thanks in advance!
Mark Hallman.
mark hallman
p.eng. leed ap bd&c
project engineer
mdh at rwdi.com<mailto:mdh at rwdi.com>
519 823 1311 x2494
RWDI: the science of buildings, structures & the environment. See what we do HERE<http://www.rwdi.com/#!services3/c1h0m>.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20151013/fa41afb3/attachment-0005.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 1517 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20151013/fa41afb3/attachment-0010.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.jpg
Type: image/jpeg
Size: 1647 bytes
Desc: image002.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20151013/fa41afb3/attachment-0011.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.png
Type: image/png
Size: 3856 bytes
Desc: image003.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20151013/fa41afb3/attachment-0005.png>
More information about the Equest-users
mailing list