[Equest-users] Water side economizer

John Aulbach jra_sac at yahoo.com
Thu Nov 5 09:21:17 PST 2015


Gentlemen:
Here is the model. Pick away. I just don't think it makes sense in SoCal vs an air side.
Please keep the client close to your vest. This building is on the site of the old Gene Autry studios. 


     On Thursday, November 5, 2015 8:39 AM, "Bishop, Bill" <bbishop at pathfinder-ea.com> wrote:
   

 #yiv5881716729 #yiv5881716729 -- _filtered #yiv5881716729 {panose-1:2 4 5 3 5 4 6 3 2 4;} _filtered #yiv5881716729 {font-family:Calibri;panose-1:2 15 5 2 2 2 4 3 2 4;} _filtered #yiv5881716729 {font-family:Verdana;panose-1:2 11 6 4 3 5 4 4 2 4;} _filtered #yiv5881716729 {panose-1:2 11 6 3 2 1 2 2 2 4;}#yiv5881716729 #yiv5881716729 p.yiv5881716729MsoNormal, #yiv5881716729 li.yiv5881716729MsoNormal, #yiv5881716729 div.yiv5881716729MsoNormal {margin:0in;margin-bottom:.0001pt;font-size:12.0pt;}#yiv5881716729 p.yiv5881716729MsoBodyText, #yiv5881716729 li.yiv5881716729MsoBodyText, #yiv5881716729 div.yiv5881716729MsoBodyText {margin-right:0in;margin-left:0in;font-size:12.0pt;}#yiv5881716729 a:link, #yiv5881716729 span.yiv5881716729MsoHyperlink {color:blue;text-decoration:underline;}#yiv5881716729 a:visited, #yiv5881716729 span.yiv5881716729MsoHyperlinkFollowed {color:purple;text-decoration:underline;}#yiv5881716729 span.yiv5881716729EmailStyle17 {color:#1F497D;}#yiv5881716729 span.yiv5881716729EmailStyle18 {color:windowtext;}#yiv5881716729 span.yiv5881716729d2hbreadcrumbslinkseparator {}#yiv5881716729 span.yiv5881716729BodyTextChar {}#yiv5881716729 .yiv5881716729MsoChpDefault {} _filtered #yiv5881716729 {margin:1.0in 1.0in 1.0in 1.0in;}#yiv5881716729 div.yiv5881716729WordSection1 {}#yiv5881716729 John, The energy savings for air handler water-side economizers (WSE) will largely depend on the pumping energy, as you note. These are different than the water-side economizers that are cooling towers for serving chilled water systems, allowing chiller(s) to turn off. The default coil head is pretty high (20’) so override the default if appropriate to your design.        The DOE2.2 help menu description for WSE is in this section:Volume 2: Dictionary >HVAC Components >SYSTEM >Cooling Equipment Part of the description mentions operation to supplement (not entirely replace) the cooling coil and/or air-side economizer: The water-side economizer coil is assumed to be downstream of the mixed air plenum, and upstream of the cooling coil. As such, the cooling coil may supplement the operation of the water-side economizer. The air handler may also have a conventional outdoor-air economizer, in which case the outdoor-air economizer will operate first to meet the supply-air setpoint, then the water-side economizer will supplement the outdoor-air economizer, and the cooling coil will pick up the remaining load, if any.  Regards, Bill    William Bishop, PE, BEMP, BEAP, CEM, LEED AP| Pathfinder Engineers & Architects LLP 
| Senior Energy Engineer  |    |
|     |
| 134 South Fitzhugh Street                Rochester, NY 14608  |
| T: (585) 698-1956                       F: (585) 325-6005  |
| bbishop at pathfinder-ea.com            www.pathfinder-ea.com  |
| Carbon Fee and Dividend - simple, effective, and market-based.  |

   From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org]On Behalf Of Julien Marrec
Sent: Thursday, November 05, 2015 11:17 AM
To: John Aulbach <jra_sac at yahoo.com>
Cc: Equest-users <equest-users at lists.onebuilding.org>
Subject: Re: [Equest-users] Water side economizer    John, Never did a waterside economizer for RTUs, but a couple of points I think I remember: The waterside economizer in eQuest is all or nothing: if it can satisfy the entire load, then it's on, otherwise it's off. Are you autosizing or hardsizing it? It also poses the questions of how you reset the condenser water loop temperature, and how you reset the rooftop supply air temperature during low load condition. What are your current settings? Julien    
 --
Julien Marrec, EBCP, BPI MFBA
Energy&Sustainability Engineer
T: +33 6 95 14 42 13

LinkedIn (en) : www.linkedin.com/in/julienmarrec
LinkedIn (fr) : www.linkedin.com/in/julienmarrec/fr    2015-11-05 15:11 GMT+01:00 John Aulbach <jra_sac at yahoo.com>: 
Hello all and HALP !!    I have an office building in Los Angeles that is looking to go LEED Core and Shell. It has some exterior and back of the house lighting, so the savings there make sense. But the building has 6 DX 30-50 ton Trane rooftop package units, two on the 1st floor and one for each of the other 4 floors. These are WATER COOLED units.    These units have a central outside air stream, and have WATER SIDE ECONOMIZERS.    My Base model has an air side economizer (still water cooled condensers). The proposed model removes the air side and replaces it with the water side.    The units themselves are EER 14+, whereas the Base units are 10.8 EER.    Results show a SLIGHT savings in Space Cooling, which I attribute to the EER improvement MINUS the air side economizer removal (Jan and Dec space cooling load INCREASES in the Proposed Case).    But the pumping energy skyrockets about 50% (remember, no chilled water).    I am unsure if I am running the water side correctly. There is only the one line of data at ever SYSTEM level.    Help??    John R. Aulbach Aging engineer (by the minute) 
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send  a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG 
   

  
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20151105/23e5c7a2/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image008.png
Type: image/png
Size: 81500 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20151105/23e5c7a2/attachment-0004.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image009.jpg
Type: image/jpeg
Size: 1517 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20151105/23e5c7a2/attachment-0004.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image010.jpg
Type: image/jpeg
Size: 1647 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20151105/23e5c7a2/attachment-0005.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image011.png
Type: image/png
Size: 3861 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20151105/23e5c7a2/attachment-0005.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: Bronson Studios Office Add-PROPOSED DETAIL.pd2
Type: application/octet-stream
Size: 69604 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20151105/23e5c7a2/attachment-0004.obj>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: Bronson Studios Office Add-PROPOSED DETAIL.inp
Type: application/octet-stream
Size: 223011 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20151105/23e5c7a2/attachment-0005.obj>


More information about the Equest-users mailing list