[Equest-users] Issue with SS-K Report
    Jones, Christopher 
    Christopher.r.Jones at wspgroup.com
       
    Thu Nov 19 10:41:15 PST 2015
    
    
  
When I run the file, the only months I see 0 for the difference between temperature of OA & room air is when the fan run hours are also 0 for those months.
You have -999 for all hours of the fan schedule.
From the manual:
A value of -999 defines an optimum start period of up to six hours. During this period the fan start
time is delayed until the fan run time matches that needed to meet the desired zone temperatures.
Notice that this decision is made on an hourly basis, whereas in the real world it is made on much
smaller increments (ten minutes or less). For the hourly calculation, the number of hours needed to
bring each zone on the system up or down to its set point is estimated. If the number of such hours
for the majority of the zones is equal to or greater than the number of hours remaining in the start
period, the fans are turned on. The target zone temperatures used in the calculation are the heating and
cooling set point temperatures given in HEAT-TEMP-SCH and COOL-TEMP-SCH that correspond
to the first hour following the scheduled optimum start period.
[cid:image003.png at 01D09C46.E75BA0D0]
Christopher Jones, P.Eng.
Senior Engineer
WSP Canada Inc.
2300 Yonge Street, Suite 2300
Toronto, ON M4P 1E4
T +1 416-644-4226
F +1 416-487-9766
C +1 416-697-0056
www.wspgroup.com<http://www.wspgroup.com/>
From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Morteza Kasmai
Sent: Thursday, November 19, 2015 12:22 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Issue with SS-K Report
Hello all,
I have created identical
"Minimum OA Schedule" for the baseline case and the proposed
design.  The schedule type is
"Frac/Design" and have values of "0" when the outside air
damper closed, and "-999" for other time of the day. After simulation
runs, SS-K report of the baseline case model shows the difference between temperature
of OA & room air “fan on hours” but this value in the SS-K report of the
proposed design is “0”. Please find the attached pd2 and inp files of the model.
I was wondering if anyone could have look at the model and let me know if I
missed something.
Thank you for your time,
Morteza
[Image removed by sender.]
________________________________
You are receiving this communication because you are listed as a current WSP contact. Should you have any questions regarding WSP’s electronic communications policy, please consult our Anti-Spam Commitment www.wspgroup.com/casl. For any concern or if you believe you should not be receiving this message, please forward this message to us at caslcompliance at wspgroup.com<mailto:caslcompliance at wspgroup.com> so that we can promptly address your request. This message is intended only for the use of the individual or entity to which it is addressed, and may contain information which is privileged, confidential, proprietary or exempt from disclosure under applicable law. If you are not the intended recipient or the person responsible for delivering the message to the intended recipient, you are strictly prohibited from disclosing, distributing, copying or in any way using this message. If you have received this communication in error, please notify the sender, and destroy and delete any copies you may have received.
WSP provides professional land surveying services through the following entities: WSP Surveys (AB) Limited Partnership and WSP Surveys (BC) Limited Partnership
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20151119/04fcd639/attachment-0005.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: ~WRD000.jpg
Type: image/jpeg
Size: 823 bytes
Desc: ~WRD000.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20151119/04fcd639/attachment-0005.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 6574 bytes
Desc: image001.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20151119/04fcd639/attachment-0005.png>
    
    
More information about the Equest-users
mailing list