[Equest-users] eQuest heat pump performance curves
Fernando Varela
fvarela at ind.uned.es
Wed Nov 18 08:49:07 PST 2015
Dear Bill and Jeff:
The problem arises when you plot for a fix hot water outlet (let's say
113ºF) the whole curve for exterior temperatures (from 9 to 59ºF), using
the expression of 39- curve for values till 39ºF and 39+ for the rest of
them.
It shows like this:
[image: Imágenes integradas 1]
Shouldn't COP increase with higher exterior temperatures for a fixed hot
water outlet temperature? It seems even to decay after 54ºF...
With capacity curves is the same, but in that case it makes more sense.
Thanks.
*Fernando Varela Díez*
Dpto. Ingeniería Energética - ETSI Industriales
Email: fvarela at ind.uned.es
Tlf: 91 398 6468
Universidad Nacional de Educación a Distancia (UNED)
C/ Juan del Rosal, 12. Despacho 2.20
Ciudad Universitaria, 28040, Madrid
2015-11-17 16:03 GMT+01:00 Bishop, Bill <bbishop at pathfinder-ea.com>:
> Fernando,
>
> The curves look okay to me. I plotted them out for a range of hot water
> temperatures from 90F to 130F.
>
> - I plotted the “…39+” curve for the range of entering dry bulb
> from 40F to 60F.
>
> - I plotted the ”…39-“ curve for the range of Edb from 20F to 38F.
>
> - Both curves show decreasing capacity as the heat pump chiller
> makes hotter water, which makes sense.
>
> - Both curves show decreasing capacity with lower outside air
> condenser temperatures, which makes sense.
>
> - The “…39-“ curve shows rapidly decreasing capacity with
> decreasing condenser temperature below 39F, which makes sense since larger
> portions of the chiller heat pump heat is needed to defrost the condenser
> coils.
>
> - I’m guessing that the curves are normalized to 110F HWT and 44F
> Edb.
>
> I can share an Excel file I used to generate the curves and chart if
> anybody wants it.
>
> ~Bill
>
>
>
>
>
>
>
> *William Bishop, PE, BEMP, BEAP, CEM, LEED AP **|** Pathfinder Engineers
> & Architects LLP*
>
> *Senior Energy Engineer*
>
>
>
>
>
> 134 South Fitzhugh Street Rochester, NY 14608
>
> *T: (585) 698-1956 <%28585%29%20698-1956>* F: (585)
> 325-6005
>
> bbishop at pathfinder-ea.com <wbishop at pathfinder-ea.com>
> www.pathfinder-ea.com
>
> [image: http://png-5.findicons.com/files/icons/977/rrze/720/globe.png]Carbon
> Fee and Dividend - simple, effective, and market-based.
>
>
>
>
>
> *From:* Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] *On
> Behalf Of *Fernando Varela
> *Sent:* Tuesday, November 17, 2015 5:04 AM
> *To:* equest-users at lists.onebuilding.org
> *Subject:* [Equest-users] eQuest heat pump performance curves
>
>
>
> Dear users:
>
>
>
> I've noticed that eQuest heat pump performance curves:
>
>
>
> ChlrHPAirHeatCap-fHW&39+
>
> ChlrHPAirHeatCap-fHW&39-
>
>
>
> which refer, respectively, to the temperature capacity factor of the heat
> pump in normal and defrost mode, seem to be exchanged. This is,
> ChlrHPAirHeatCap-fHW&39+ curve seems to be the defrost mode curve, and
> ChlrHPAirHeatCap-fHW&39- the curve regarding to normal mode.
>
>
>
> I've plotted (with fixed condensing temperature) both capacities varying
> exterior temperature, and observing the results taking the curves in the
> opposite way as it shoud be (below 39ºF,ChlrHPAirHeatCap-fHW&39+, and
> ChlrHPAirHeatCap-fHW&39- above 39ºF ), the resulting HP capacity curve
> seems more like it should be.
>
>
>
> Am I doing something wrong?
>
>
>
> Thank you in advance.
>
> [image: Image removed by sender.]
>
> *Fernando Varela Díez*
> Dpto. Ingeniería Energética - ETSI Industriales
> Email: fvarela at ind.uned.es
> Tlf: 91 398 6468
>
> Universidad Nacional de Educación a Distancia (UNED)
> C/ Juan del Rosal, 12. Despacho 2.20
> Ciudad Universitaria, 28040, Madrid
>
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20151118/fd61ff69/attachment-0005.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image012.png
Type: image/png
Size: 3859 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20151118/fd61ff69/attachment-0015.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image011.jpg
Type: image/jpeg
Size: 1647 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20151118/fd61ff69/attachment-0015.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image013.jpg
Type: image/jpeg
Size: 500 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20151118/fd61ff69/attachment-0016.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image010.jpg
Type: image/jpeg
Size: 1517 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20151118/fd61ff69/attachment-0017.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 68290 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20151118/fd61ff69/attachment-0016.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image.png
Type: image/png
Size: 12658 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20151118/fd61ff69/attachment-0017.png>
More information about the Equest-users
mailing list