[Equest-users] Baseline Fan power calculation for Ventilation units

Sharad Kumar sharadcapricious at gmail.com
Tue Nov 3 03:47:17 PST 2015


Dear Vishal,

The Baseline case fan power has to be calculated as per the system type
considered in the Baseline Case.
The Baseline Case System type has to be considered from the table G3.1.1A.
The system type consideration in the Baseline Case is as per the number of
floors, building type, conditioned area and type of heating system in the
building.
Now when the Baseline Case system is achieved the Baseline case fan power
is considered from the table G3.1.2.9. For system type 1 and 2 the baseline
case fan power is taken from the section G3.1.2.9 (0.0003 kW/cfm).

The fan power for ventilation and exhaust fans is considered under
miscellaneous load. The savings under this category is achieved by having
some exceptional calculations.
If the proposed case ventilation or exhaust fan is having two speed to
variable flow motors then we can adjust the schedules to have energy
savings in the proposed case.
The schedules for ventilation and exhaust fans can be altered depending
upon the number of occupied hours and the need of building or space type to
have the fans to be operating at lower speeds.
The Baseline case fan is being to have the  constant flow based schedules.
This has been accepted by USGBC in  past for parking fan loads.Hope this
might be helpful.To not to have a heck you can use same fan power and
schedules in both the cases.

Thanks,
Sharad.Kumar
Green Horizon Consulting LLP



On Tue, Nov 3, 2015 at 2:31 AM, <equest-users-request at lists.onebuilding.org>
wrote:

> Send Equest-users mailing list submissions to
>         equest-users at lists.onebuilding.org
>
> To subscribe or unsubscribe via the World Wide Web, visit
>
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
>
> or, via email, send a message with subject or body 'help' to
>         equest-users-request at lists.onebuilding.org
>
> You can reach the person managing the list at
>         equest-users-owner at lists.onebuilding.org
>
> When replying, please edit your Subject line so it is more specific
> than "Re: Contents of Equest-users digest..."
>
> Today's Topics:
>
>    1. Baseline Fan power calculation for Ventilation units
>       (Vishal Jagdale)
>
>
> ---------- Forwarded message ----------
> From: Vishal Jagdale <jagdalevishal07 at gmail.com>
> To: equest-users at lists.onebuilding.org
> Cc:
> Date: Mon, 2 Nov 2015 19:56:25 +0530
> Subject: [Equest-users] Baseline Fan power calculation for Ventilation
> units
> Hi,
>
> As we are working on a factory Building,manufacturing building part is an
> Air-conditioned .The Warehouse area has an individual Supply ventilation &
> individual exhaust units.
> While working for baseline fan power calculation for manufacturing Ahu's,
> i will be following section G.3.1.2.9.
> *Please confirm* weather the same fan power calculation formulas based on
> G.3.1.2.9 is to be used for ventilation & exhaust units *or* the fan
> power values to be considered identical as that of proposed case.
>
>
> Regards,
> Vishal
>
> _______________________________________________
> Equest-users mailing list
> Equest-users at lists.onebuilding.org
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20151103/2183a984/attachment-0005.htm>


More information about the Equest-users mailing list