[Equest-users] PTAC vs WLHP Annual Energy Consumption
David Reddy
david at 360-analytics.com
Mon May 4 09:39:44 PDT 2015
Hi Morteza,
I have not reviewed the results or detailed inputs of your model, but
one thing to be aware is that depending on the rating conditions of your
efficiency data, you may have to adjust the EIRs to be consistent with
DOE-2 performance curves. The default DOE-2 curves are normalized to
the GSHP rating condition, so if using these and if your efficiency data
is @ the WSHP rating condition, you will need to apply these adjustments.
Here is the table from the DOE-2 help provided with eQUEST. There is a
library of DOE-2 WSHP curves available from ClimateMaster that do not
need these adjustments.
- David
On 5/4/2015 9:04 AM, Morteza Kasmai wrote:
>
> Dear all,
>
>
> This is a multifamily mid-rise building, 9 floors above grade. Per
> ASHRAE Table G3.1.1A the Baseline HVAC system is system 1 (PTAC with
> hot-water fossil fuel boiler) 9.3 to 11 EER.
> Selected HVAC system for the proposed design is WLHP (3 Ton High
> efficiency HP by Daikin, 15.9 EER and 4.83 COP) with 2 cell cooling
> tower, DOAS unit (9.8 EER) and 2 Boilers (0.92 Eff.).
>
> Although the efficiency of the selected HVAC systems is much higher
> than the efficiency of the baseline model, the simulation results
> indicate annual energy consumption of the proposed design is much
> higher than the baseline!
>
> Am I missing something or did something wrong in the models? Please
> see the attached files of the both models
>
> .
>
> I would greatly appreciate it if anyone kindly gives some feedback on
> this,
>
> Morteza
>
>
>
>
>
>
>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20150504/471f2033/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 8552 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20150504/471f2033/attachment-0002.png>
More information about the Equest-users
mailing list