[Equest-users] The problem of minimum equipment efficiency requirement of Ashrae 90.1-2007
Julien Marrec
julien.marrec at gmail.com
Sun May 24 05:19:45 PDT 2015
Hey,
He's saying that you need to make sure that the curve boiler-fPLR gives you a constant efficiency. As far as I remember, the default atmospheric curve from equest is like this.
Don't be confused by "flat". A flat efficiency curve is when you plot efficiency=f(PLR). In equest, it should be a curve that is y=x
Look at the curve you used.
Best,
Julien
Envoyé de mon iPhone
> Le 24 mai 2015 à 11:27, "赵永青" <503271081 at qq.com> a écrit :
>
> I get the energy model comments from LEED reviewer as following:
>
> The narrative response indicates that the Baseline boiler has been modeled utilizing operating performance curves and a boiler HIR of 1.25. However, since the boiler operation HIR is based on the performance curves, the HIR is less than 1.25 in the part-load condition, which is inappropriate. Revise the Baseline boilers to include a flat efficiency of 80% for all part-loads. Provide eQuest input files or screen shots verifying the boiler efficiency has been modeled as required.
> <545E22AD at FA528147.9F996155>
> However, I can not understand it very much. The minimum equipment efficiency requirement(80 % Et) of Ashrae 90.1-2007 should be base on full load condition.Why the LEED reviewer raise such a question?Any insight is appreciate!!
>
> Thanks
> ------------------
> Yongqing Zhao
> Changsha Green Building & Energy Saving Technology CO.,LTD
> NO.438,Shaoshan Road,Changsha,Hunan,China
> Telephone:13574805636
> Email:zhaoyongqing1987 at 126.com
> 503271081 at qq.com
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20150524/d1c76cb4/attachment-0005.htm>
More information about the Equest-users
mailing list