Hi Vikram,
Additionally, kindly have a go through the weather file.
The result can also depend on the location whether it is cool or hot.
If it is cold then the result is all right.
Thanks,
Sharad.Kumar
Green Horizon Consulting LLP.
Gurgaon
India.
On Wed, May 20, 2015 at 1:33 AM, <equest-users-request at lists.onebuilding.org
> wrote:
> Send Equest-users mailing list submissions to
> equest-users at lists.onebuilding.org
>
> To subscribe or unsubscribe via the World Wide Web, visit
>
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
>
> or, via email, send a message with subject or body 'help' to
> equest-users-request at lists.onebuilding.org
>
> You can reach the person managing the list at
> equest-users-owner at lists.onebuilding.org
>
> When replying, please edit your Subject line so it is more specific
> than "Re: Contents of Equest-users digest..."
>
> Today's Topics:
>
> 1. Thermostat setpoint quandry (Sami, Vikram)
> 2. Re: Thermostat setpoint quandry (Erik Kolderup)
>
>
> ---------- Forwarded message ----------
> From: "Sami, Vikram" <vikram.sami at zgf.com>
> To: "equest-users at lists.onebuilding.org" <
> equest-users at lists.onebuilding.org>
> Cc:
> Date: Mon, 18 May 2015 22:51:55 +0000
> Subject: [Equest-users] Thermostat setpoint quandry
>
> I’m a little stumped here.
>
>
>
> I’m running a simple single zone VAV simulation that has a setback
> temperature schedule for heating and cooling seasons. For some reason, if
> you examine the hourly report, it seems to use the heating schedule for the
> entire year (inp file attached).What am I missing?
>
>
>
> Any insight would be much appreciated.
>
>
>
>
>
> *Vikram Sami*
> AIA, BEMP, LEED BD+C
> Associate Partner
>
>
>
> ZGF ARCHITECTS LLP
> *T *206.521.3509 *E *vikram.sami at zgf.com
> 925 Fourth Avenue, Suite 2400
> Seattle, WA 98104
>
>
> ZGF Email Disclaimer <https://www.zgf.com/ZGF_Email_Disclaimer.html>
>
>
> ---------- Forwarded message ----------
> From: Erik Kolderup <erik at kolderupconsulting.com>
> To: "Sami, Vikram" <vikram.sami at zgf.com>
> Cc: "equest-users at lists.onebuilding.org" <
> equest-users at lists.onebuilding.org>
> Date: Mon, 18 May 2015 17:05:59 -0700
> Subject: Re: [Equest-users] Thermostat setpoint quandry
> Vikram,
>
> I suggest checking your minimum airflow schedule ("Annual Schedule
> Airflow"). Looks like the values are greater than one, resulting in a
> constant volume system that gets driven to the heating setpoint. If the
> airflow were allowed to drop then there would probably be hours at the
> cooling setpoint.
>
> Regards,
> Erik
>
> *Erik Kolderup, PE, LEED AP*
> erik at kolderupconsulting.com | 415.531.5198 | www.kolderupconsulting.com
>
> On Mon, May 18, 2015 at 3:51 PM, Sami, Vikram <vikram.sami at zgf.com> wrote:
>
>> I’m a little stumped here.
>>
>>
>>
>> I’m running a simple single zone VAV simulation that has a setback
>> temperature schedule for heating and cooling seasons. For some reason, if
>> you examine the hourly report, it seems to use the heating schedule for the
>> entire year (inp file attached).What am I missing?
>>
>>
>>
>> Any insight would be much appreciated.
>>
>>
>>
>>
>>
>> *Vikram Sami*
>> AIA, BEMP, LEED BD+C
>> Associate Partner
>>
>>
>>
>> ZGF ARCHITECTS LLP
>> *T *206.521.3509 *E *vikram.sami at zgf.com
>> 925 Fourth Avenue, Suite 2400
>> Seattle, WA 98104
>>
>>
>> ZGF Email Disclaimer <https://www.zgf.com/ZGF_Email_Disclaimer.html>
>>
>> _______________________________________________
>> Equest-users mailing list
>> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
>> To unsubscribe from this mailing list send a blank message to
>> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>>
>>
>
> _______________________________________________
> Equest-users mailing list
> Equest-users at lists.onebuilding.org
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20150521/edfe3a42/attachment-0005.htm>
More information about the Equest-users
mailing list