[Equest-users] PTAC vs WLHP Annual Energy Consumption
Morteza Kasmai
morteza.kasmai at gmail.com
Wed May 6 06:54:15 PDT 2015
Dear eQUEST experts,
I am still struggling to find out the main reason(s) for high-energy
consumption of WLHP system comparing to PTAC system and what can be done to
make this system more efficient that the baseline system. In other words
for complying with EAp2 requirements, for a mid rise residential building
what types of HVAC systems (other than split system HP) can be selected
which consume less annual energy than the PTAC.
I would appreciate it if you would share your experience on this and make
some recommendation.
Morteza
On Mon, May 4, 2015 at 4:03 PM, <equest-users-request at lists.onebuilding.org>
wrote:
> Send Equest-users mailing list submissions to
> equest-users at lists.onebuilding.org
>
> To subscribe or unsubscribe via the World Wide Web, visit
>
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
>
> or, via email, send a message with subject or body 'help' to
> equest-users-request at lists.onebuilding.org
>
> You can reach the person managing the list at
> equest-users-owner at lists.onebuilding.org
>
> When replying, please edit your Subject line so it is more specific
> than "Re: Contents of Equest-users digest..."
>
> Today's Topics:
>
> 1. PTAC vs WLHP Annual Energy Consumption (Morteza Kasmai)
> 2. Re: PTAC vs WLHP Annual Energy Consumption (David Reddy)
>
>
> ---------- Forwarded message ----------
> From: Morteza Kasmai <morteza.kasmai at gmail.com>
> To: "equest-users at lists.onebuilding.org" <
> equest-users at lists.onebuilding.org>
> Cc:
> Date: Mon, 4 May 2015 12:04:23 -0400
> Subject: [Equest-users] PTAC vs WLHP Annual Energy Consumption
>
> Dear all,
>
>
> This is a multifamily mid-rise building, 9 floors above grade. Per ASHRAE
> Table G3.1.1A the Baseline HVAC system is system 1 (PTAC with hot-water
> fossil fuel boiler) 9.3 to 11 EER.
> Selected HVAC system for the proposed design is WLHP (3 Ton High
> efficiency HP by Daikin, 15.9 EER and 4.83 COP) with 2 cell cooling tower,
> DOAS unit (9.8 EER) and 2 Boilers (0.92 Eff.).
>
>
>
> Although the efficiency of the selected HVAC systems is much higher than
> the efficiency of the baseline model, the simulation results indicate
> annual energy consumption of the proposed design is much higher than the
> baseline!
>
>
>
> Am I missing something or did something wrong in the models? Please see
> the attached files of the both models
>
> .
> I would greatly appreciate it if anyone kindly gives some feedback on this,
>
> Morteza
>
>
>
>
>
>
>
>
> ---------- Forwarded message ----------
> From: David Reddy <david at 360-analytics.com>
> To: equest-users at lists.onebuilding.org
> Cc:
> Date: Mon, 04 May 2015 09:39:44 -0700
> Subject: Re: [Equest-users] PTAC vs WLHP Annual Energy Consumption
> Hi Morteza,
> I have not reviewed the results or detailed inputs of your model, but one
> thing to be aware is that depending on the rating conditions of your
> efficiency data, you may have to adjust the EIRs to be consistent with
> DOE-2 performance curves. The default DOE-2 curves are normalized to the
> GSHP rating condition, so if using these and if your efficiency data is @
> the WSHP rating condition, you will need to apply these adjustments.
>
> Here is the table from the DOE-2 help provided with eQUEST. There is a
> library of DOE-2 WSHP curves available from ClimateMaster that do not need
> these adjustments.
>
>
>
> - David
>
> On 5/4/2015 9:04 AM, Morteza Kasmai wrote:
>
> Dear all,
>
>
> This is a multifamily mid-rise building, 9 floors above grade. Per ASHRAE
> Table G3.1.1A the Baseline HVAC system is system 1 (PTAC with hot-water
> fossil fuel boiler) 9.3 to 11 EER.
> Selected HVAC system for the proposed design is WLHP (3 Ton High
> efficiency HP by Daikin, 15.9 EER and 4.83 COP) with 2 cell cooling tower,
> DOAS unit (9.8 EER) and 2 Boilers (0.92 Eff.).
>
>
>
> Although the efficiency of the selected HVAC systems is much higher than
> the efficiency of the baseline model, the simulation results indicate
> annual energy consumption of the proposed design is much higher than the
> baseline!
>
>
>
> Am I missing something or did something wrong in the models? Please see
> the attached files of the both models
>
> .
> I would greatly appreciate it if anyone kindly gives some feedback on this,
>
> Morteza
>
>
>
>
>
>
>
>
> _______________________________________________
> Equest-users mailing listhttp://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
>
> _______________________________________________
> Equest-users mailing list
> Equest-users at lists.onebuilding.org
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20150506/88300d42/attachment-0005.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 8552 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20150506/88300d42/attachment-0005.png>
More information about the Equest-users
mailing list