I looked briefly at Mike's input file.
*Paul,*
It's two-way, so that's ok. For those who may be wondering why you need
two-way valves, that is in order to have a pressure change (as they close)
going back to the VFD for modulation. That's true in real life too.
*Joe,*
Bingo on your 1) point. (see extract of warnings below).
*Mike,*
I suggest you also investigate your tons of warning about insufficient
heating capability, because you do have 1851 hours below heating throttling
range...
-------------------------------------------------------------------------------------------
Here are an extract of the warnings
**WARNING**********************************************************************
Pump: Chlr1 (ElCentHerm) Pump has a total
user-specified flow
of 1300. gpm, but the loop flow is 2325. gpm.
**WARNING**********************************************************************
Pump: Chlr2 (ElCentHerm) Pump has a total
user-specified flow
of 1300. gpm, but the loop flow is 2325. gpm.
**WARNING**********************************************************************
Pump: CW Loop Pump has a total
user-specified flow
of 1500. gpm, but the loop flow is 5649. gpm.
**WARNING**********************************************************************
Pump: CW Loop Pump cannot match the system
flow at the minimum required head.
Required system flow = 2824.3 gpm at head = 47.2
Pump balance point = 2665.2 gpm at head of 43.5
If the pump was sized by default, most likely this
is caused by a primary equipment unit operating at
greater than its design flow, and causing a pressure
drop greater than design. Try increasing the pump
head or head ratio to compensate.
First occurrence is on 1/ 1, hour 9
**WARNING**********************************************************************
Pump: Chlr1 (ElCentHerm) Pump cannot match the system
flow at the minimum required head.
Required system flow = 2325.4 gpm at head = 42.6
Pump balance point = 2314.3 gpm at head of 42.3
If the pump was sized by default, most likely this
is caused by a primary equipment unit operating at
greater than its design flow, and causing a pressure
drop greater than design. Try increasing the pump
head or head ratio to compensate.
First occurrence is on 4/27, hour 15
**WARNING**********************************************************************
Pump: Chlr2 (ElCentHerm) Pump cannot match the system
flow at the minimum required head.
Required system flow = 2325.4 gpm at head = 48.6
Pump balance point = 2289.5 gpm at head of 47.3
If the pump was sized by default, most likely this
is caused by a primary equipment unit operating at
greater than its design flow, and causing a pressure
drop greater than design. Try increasing the pump
head or head ratio to compensate.
First occurrence is on 4/29, hour 10
--
Julien Marrec, EBCP, BPI MFBA
Energy&Sustainability Engineer
T: +33 6 95 14 42 13
LinkedIn (en) : www.linkedin.com/in/julienmarrec
LinkedIn (fr) : www.linkedin.com/in/julienmarrec/fr
<http://www.linkedin.com/in/julienmarrec>
2015-06-18 21:28 GMT+02:00 Joe Fleming <joe at thespinnakergroupinc.com>:
> Hi Michael,
>
>
>
> To add to what Paul mentioned about 2-way valves;
>
>
>
> What are your building loads looking like in the eQuest output reports?
> There are 2 potential scenarios that may lead to limited savings from a
> properly modeled VFD installation;
>
> 1. If the pump is under sized for the loads input
>
> 2. If the loads are constant and mostly internal
>
>
>
> Kind Regards
>
>
>
>
>
> *Joe Fleming *|* PE, *LEED AP BD+C, BEMP
>
> *Commissioning Agent & Energy Consultant *| *The Spinnaker Group*
>
> *joe at thespinnakergroupinc.com <joe at thespinnakergroupinc.com>*
>
> *Cell* 561-602-3132 | *Office* 754-800-3100
>
>
>
> *From:* Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] *On
> Behalf Of *Mike Schaefer
> *Sent:* Thursday, June 18, 2015 2:49 PM
> *To:* equest-users at lists.onebuilding.org
> *Subject:* [Equest-users] VFD Pumping
>
>
>
> I’ve performing an energy model to compare VFD Chiller pumping and
> Constant Volume Chiller pumping for a multi-story office building using
> eQUEST v 3.65. Although I expect to save pump energy utilizing VFD pumping
> I’m not seeing a savings and I believe this is due to my “Pump Properties
> Inputs”.
>
>
>
> For both the VFD and constant volume pump scenarios I’ve input the
> scheduled pump flow (1,300 gpm) and head (200 ft) and the other pump inputs
> are default values. The energy difference between the two pumping scenarios
> is negligible, however, if I set the pump gpm to a default, which inputs a
> 1.00 Flow Ratio, the energy savings is significant in the VFD pumping
> model.
>
>
>
> Am I over defining the pumps by inputting the scheduled pump gpm? Should
> the pump gpm always be set to default?
>
>
>
> Thanks,
>
>
>
> *Michael*
>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20150619/4500f2ea/attachment-0005.htm>
More information about the Equest-users
mailing list