[Equest-users] BDL Error Trouble Shooting
Jones, Christopher
Christopher.r.Jones at wspgroup.com
Thu Jul 23 05:44:39 PDT 2015
I believe the issue is more with how the eQuest interface handles the BDL error window. When you close that window, eQuest attempts to fix the BDL errors which is what hangs the system. One solution is to leave that BDL error window open. Then open the .BDL file with a text editor. Search for ERROR to determine what errors are included.
If you close the window, eQuest removes the offending lines from the .INP file and removes the ERROR statements from the .BLD file making it hard to determine exactly is going on.
If I come across a file with a large number of errors I typically move the .INP file to my DOE22 command line installation and do the debugging by fixing each error one at a time. Once the errors are fixed, I move the .INP file back to the eQuest location and open the .PD2 file and continue.
[cid:image003.png at 01D09C46.E75BA0D0]
Christopher Jones, P.Eng.
Senior Engineer
WSP Canada Inc.
2300 Yonge Street, Suite 2300
Toronto, ON M4P 1E4
T +1 416-644-4226
F +1 416-487-9766
C +1 416-697-0065
www.wspgroup.com<http://www.wspgroup.com/>
From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of samuel mason
Sent: Wednesday, July 22, 2015 10:39 PM
To: Julien Marrec
Cc: Equest Users Mailing List
Subject: Re: [Equest-users] BDL Error Trouble Shooting
Hi Jill,
Sharing your BDL and inp files will help figure out the issues.
Encompass Energy, LLC
Sam Mason P.E., LEED AP BD+C, BEMP
Principal
P: 443-410-1534
E: sam.mason at encompassenergyLLC.com
W: www.encompassenergyLLC.com<http://www.encompassenergyLLC.com>
On Wed, Jul 22, 2015 at 4:23 PM, Julien Marrec <julien.marrec at gmail.com<mailto:julien.marrec at gmail.com>> wrote:
Jill,
If you want people to help,
It' be helpful to share the files themselves or at least what errors you are getting so it gets specific enough for people to advise.
By what you are saying (8-10 min to run it) I would tend to postulate you created way more zones than necessary even given the fact that hospital are large buildings. (Or you could have an antique computer)
Best,
Julien
Envoyé de mon iPhone
Le 22 juil. 2015 à 18:31, Jill Moreland <jill.moreland at plugsmart.com<mailto:jill.moreland at plugsmart.com>> a écrit :
Good Afternoon All,
I am working on my first eQuest Energy Model and am quickly feeling overwhelmed. Was able to build the shell in the wizard and assign shell properties (excluding doors and windows as noted in tutorial to add in detailed mode) and was successful with only 4 errors.
The problem is that when I started adding in the HVAC chilled water components without zoning them it generated 34,000 errors. I then scrapped that work and started over with one floor (which has 5 systems) and I properly zoned it and it generated 51,000 errors.
This is a 6 story hospital that was added on over many years. At this point my main question is what is best way to trouble shoot? It seems that once I close the BDL Error Screen I do not have a way of going back in without re-generating which takes 8-10 minutes to see the errors AND I don't see a way to drill down on the errors to try to resolve. I am sure many of them are inter-related but I dont even know where to start.
I am glad to have found this group because I have contacted eQuest with no response and their Forum that I bought a 4 month subscription to is basically worthless (no one responds). I know every one is slammed but any and all help would be greatly appreciated as I think this is a field that I may stay in for awhile.
Jill Moreland BSME, MBA
Connect Program Manager
Plug Smart
Jill.Moreland at PlugSmart.com<mailto:Jill.Moreland at PlugSmart.com>
Cell: 239-233-0993<tel:239-233-0993>
Fax: 800-518-5576<tel:800-518-5576>
[Image removed by sender.]
Plug Smart is accepting new clients, the best praise you could give us a recommendation to a potential new client. Everyone needs to save money, Plug Smart can make it happen.
Confidential:
This e-mail and any files transmitted with it are the property of Juice Technologies, LLC. and/or its affiliates, are confidential, and are intended solely for the use of the individual or entity to whom this e-mail is addressed. If you are not one of the named recipients or otherwise have reason to believe that you have received this e-mail in error, please notify the sender and delete this message immediately from your computer. Any other use, retention, dissemination, forwarding, printing or copying of this e-mail is strictly prohibited.
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG<mailto:EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG>
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG<mailto:EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG>
________________________________
You are receiving this communication because you are listed as a current WSP contact. Should you have any questions regarding WSP’s electronic communications policy, please consult our Anti-Spam Commitment www.wspgroup.com/casl. For any concern or if you believe you should not be receiving this message, please forward this message to us at caslcompliance at wspgroup.com<mailto:caslcompliance at wspgroup.com> so that we can promptly address your request. This message is intended only for the use of the individual or entity to which it is addressed, and may contain information which is privileged, confidential, proprietary or exempt from disclosure under applicable law. If you are not the intended recipient or the person responsible for delivering the message to the intended recipient, you are strictly prohibited from disclosing, distributing, copying or in any way using this message. If you have received this communication in error, please notify the sender, and destroy and delete any copies you may have received.
WSP provides professional land surveying services through the following entities: WSP Surveys (AB) Limited Partnership and WSP Surveys (BC) Limited Partnership
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20150723/abed619f/attachment-0005.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: ~WRD000.jpg
Type: image/jpeg
Size: 823 bytes
Desc: ~WRD000.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20150723/abed619f/attachment-0005.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 6574 bytes
Desc: image001.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20150723/abed619f/attachment-0005.png>
More information about the Equest-users
mailing list