[Equest-users] Interior courtyards

Jeff Haberl jhaberl at tamu.edu
Mon Jul 20 15:19:57 PDT 2015


Hello Jason,

Great building to try to simulate.

However, real courtyard buildings are very difficult to simulate accurately because, depending on climate, they have the potential to expose the building to (2) or more "weather files", one for the exterior surfaces of the building and one for the "courtyard". In addition, if there are any openings from the exterior through the building into the courtyard, then there can be significant cross ventilation, which further complicates things.

Finally, if the building is in an extreme climate (for example hot and dry), and if there is any vegetation in the courtyard or fountain, then you may also have significant evaporative cooling in the courtyard (i.e., wetting of the porous floor and walls) and in such cases you'll need an industrial strength CFD program coupled with the building thermal simulation, that is capable of tracking air flow and moisture in and around the building and its courtyard...not for the faint of heart.

If there is no interaction between the building and the courtyard, if you don't have evaporative cooling and if you have some measured data, then one could develop an empirical or "inverse simulation" of the courtyard, split the building like a donut and "simulate" the weather condition inside the courtyard for the inner portion of the building and the normal weather file outside the building with the outside portions and then knit the two simulations together with adiabatic, mass-type thermal walls after iterating to converge the solutions.

One additional difficult issue is that many of the traditional courtyard buildings have amounts of thermal mass that go way beyond the capabilities of today's whole-building thermal simulation programs, which can require a rather long period to converge (i.e., weeks or months).

Finally, although there has been some previous work in this area, most creditable efforts attempt to resolve one of more of the above issues.

Jeff

8=!  8=)  :=)  8=)  ;=)  8=)  8=(  8=)  8=()  8=)  8=|  8=)  :=')  8=) 8=?
Jeff S. Haberl, Ph.D.,P.E.inactive,FASHRAE,FIBPSA,......jhaberl at tamu.edu<mailto:........jhaberl at tamu.edu>
Professor........................................................................Office Ph: 979-845-6507
Department of Architecture............................................Lab Ph:979-845-6065
Energy Systems Laboratory...........................................FAX: 979-862-2457
Texas A&M University...................................................77843-3581
College Station, Texas, USA, 77843..............................URL:www.esl.tamu.edu
8=/  8=)  :=)  8=)  ;=)  8=)  8=()  8=)  :=)  8=)  8=!  8=)  8=? 8=) 8=0

From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Ng, Jason
Sent: Monday, July 20, 2015 4:01 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Interior courtyards

Of course, I forgot to attach my image......


[cid:image001.jpg at 01D0C30F.5FAD19D0]

Jason Ng_ing. jr. M.Sc.A., LEED green associate
jng at bpa.ca<mailto:jng at bpa.ca>   |  www.bpa.ca<http://www.bpa.ca>  |  t: 5143833747x2813

Les informations contenues dans le courriel que vous venez de recevoir, y compris les pièces jointes, sont destinées à l'usage exclusif de la (ou des) personne(s) identifiée(s) comme destinataires et sont confidentielles. Si vous n'en êtes pas le destinataire, soyez avisé que tout usage en est interdit. Si vous avez reçu ce courriel par erreur, veuillez le retourner à l'expéditeur et le supprimer complètement de votre système informatique.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20150720/4e128fe7/attachment-0005.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 5712 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20150720/4e128fe7/attachment-0005.jpg>


More information about the Equest-users mailing list