[Equest-users] Medical building design flowrates - ASHRAE 170
Steve Jacobs
sjacobseng at gmail.com
Thu Jul 16 09:38:19 PDT 2015
For medical buildings that are governed by ASHRAE 170 the airflow
requirements are a bit different. The standard not only mandates minimum OA
flowrates but also general airflow rates (often times 6 ACH or higher). This
airflow rate is typically higher than the autosized rates based on a 20F
differential. It seems like the baseline should use the required flowrates
like the proposed, but has anyone gone through this with a LEED reviewer.
Basically it would mean that the minimum flowrate in the VAV spaces would be
100% resulting in a lot of reheat energy.
Thanks,
Steve
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20150716/bae6de43/attachment-0005.htm>
More information about the Equest-users
mailing list