[Equest-users] Steam humidification

Jones, Christopher Christopher.r.Jones at wspgroup.com
Mon Dec 7 11:16:46 PST 2015


Yes, it seems like an oversight. I know DHW does respond to a change in ground temperatures. It is short sighted not to account for the heating of the make-up water for humidification.


[cid:image003.png at 01D09C46.E75BA0D0]
Christopher Jones, P.Eng.
Senior Engineer

WSP Canada Inc.
2300 Yonge Street, Suite 2300
Toronto, ON M4P 1E4
T +1 416-644-4226
F +1 416-487-9766
C +1 416-697-0056

www.wspgroup.com<http://www.wspgroup.com/>

From: Lapierre, Patrick [mailto:plapierre at bpa.ca]
Sent: Monday, December 07, 2015 2:08 PM
To: Jones, Christopher; equest-users at lists.onebuilding.org
Subject: RE: Steam humidification

I’ve just tested your suggestion Christopher and there was no variation at all.
Seems wierd to me that such a crucial load is being overlooked.


[cid:image004.jpg at 01D130F9.257D3E90]

Patrick Lapierre_ing.
plapierre at bpa.ca<mailto:plapierre at bpa.ca>


De : Jones, Christopher [mailto:Christopher.r.Jones at wspgroup.com]
Envoyé : 7 décembre 2015 11:52
À : Lapierre, Patrick <plapierre at bpa.ca<mailto:plapierre at bpa.ca>>; equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Objet : RE: Steam humidification

Hello Patrick,
One way to test this would be to change the ground temperatures in the Site Data dialog.


[cid:image003.png at 01D09C46.E75BA0D0]
Christopher Jones, P.Eng.
Senior Engineer

WSP Canada Inc.
2300 Yonge Street, Suite 2300
Toronto, ON M4P 1E4
T +1 416-644-4226
F +1 416-487-9766
C +1 416-697-0056

www.wspgroup.com<http://www.wspgroup.com/>

From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Lapierre, Patrick
Sent: Monday, December 07, 2015 10:14 AM
To: equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: [Equest-users] Steam humidification

I’m questionning myself on the calculations made by DOE towards the humidification load.

Does anyone know if the energy necessary to bring cold water make-up to its boiling point is accounted for by DOE?
After a quick look in the engineer’s manual, it seems to me as if the humidification load only accounts for the heat of vaporisation of water. As if the water supply is already at it’s boiling point.

Did I overlook something?
I need a captain here!


[cid:image005.jpg at 01D130F9.257D3E90]

Patrick Lapierre_ing.
plapierre at bpa.ca<mailto:plapierre at bpa.ca>   |  www.bpa.ca<http://www.bpa.ca>  |  t: 5143833747x2807

Les informations contenues dans le courriel que vous venez de recevoir, y compris les pièces jointes, sont destinées à l’usage exclusif de la (ou des) personne(s) identifiée(s) comme destinataires et sont confidentielles. Si vous n’en êtes pas le destinataire, soyez avisé que tout usage en est interdit. Si vous avez reçu ce courriel par erreur, veuillez le retourner à l’expéditeur et le supprimer complètement de votre système informatique.
________________________________

You are receiving this communication because you are listed as a current WSP contact. Should you have any questions regarding WSP’s electronic communications policy, please consult our Anti-Spam Commitment www.wspgroup.com/casl. For any concern or if you believe you should not be receiving this message, please forward this message to us at caslcompliance at wspgroup.com<mailto:caslcompliance at wspgroup.com> so that we can promptly address your request. This message is intended only for the use of the individual or entity to which it is addressed, and may contain information which is privileged, confidential, proprietary or exempt from disclosure under applicable law. If you are not the intended recipient or the person responsible for delivering the message to the intended recipient, you are strictly prohibited from disclosing, distributing, copying or in any way using this message. If you have received this communication in error, please notify the sender, and destroy and delete any copies you may have received.

WSP provides professional land surveying services through the following entities: WSP Surveys (AB) Limited Partnership and WSP Surveys (BC) Limited Partnership
________________________________

You are receiving this communication because you are listed as a current WSP contact. Should you have any questions regarding WSP’s electronic communications policy, please consult our Anti-Spam Commitment www.wspgroup.com/casl. For any concern or if you believe you should not be receiving this message, please forward this message to us at caslcompliance at wspgroup.com<mailto:caslcompliance at wspgroup.com> so that we can promptly address your request. This message is intended only for the use of the individual or entity to which it is addressed, and may contain information which is privileged, confidential, proprietary or exempt from disclosure under applicable law. If you are not the intended recipient or the person responsible for delivering the message to the intended recipient, you are strictly prohibited from disclosing, distributing, copying or in any way using this message. If you have received this communication in error, please notify the sender, and destroy and delete any copies you may have received.

WSP provides professional land surveying services through the following entities: WSP Surveys (AB) Limited Partnership and WSP Surveys (BC) Limited Partnership
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20151207/d7bc006f/attachment-0005.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.png
Type: image/png
Size: 6574 bytes
Desc: image002.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20151207/d7bc006f/attachment-0005.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image004.jpg
Type: image/jpeg
Size: 1728 bytes
Desc: image004.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20151207/d7bc006f/attachment-0010.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image005.jpg
Type: image/jpeg
Size: 5712 bytes
Desc: image005.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20151207/d7bc006f/attachment-0011.jpg>


More information about the Equest-users mailing list