[Equest-users] Independent Exhaust Fan Power
Sefa Şahin
ssahin at mimtarch.com
Thu Dec 3 07:59:27 PST 2015
Dear All,
We have received the following comment from GBCI regarding the energy
modeling review:
"Table EAp2-4 reports additional electricty consumption for toilet room
exhaust in the baseline case. However, exhaust fans that operate
continuously during occupied periods are considered part of the system
and must be modeled in the Baseline case using a portion of the system
fan power. Revise the baseline model to remove any additional fan power
for toilet room exhaust fans and update Supplemental Table 1.4 and the
form as required."
Our project includes parking exhaust, kitchen exhaust and WC exhaust
fans. These fans operates separately from main HVAC Units. We have
modeled identically these exhaust fans as independent exhaust fan on
sub-meters baseline and proposed model. These fans annual consumption
have been assigned process energy on EAp2-5. Where am i made mistake ?
Thanks for all replies,
Sefa Sahin