[Equest-users] Simulation Run Help
Lapierre, Patrick
plapierre at bpa.ca
Thu Aug 6 09:46:11 PDT 2015
Looking at your inp file, the wall’s parent space is « E15 SSW Perim Spc (G.SSW3) ».
My guess as to why your wall has a negative net area is because its child window « Window 466 » has a larger area than the wall itself.
[cid:image001.jpg at 01D0D045.DCC4F300]
Patrick Lapierre_ing.
plapierre at bpa.ca
De : Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] De la part de Jill Moreland
Envoyé : 6 août 2015 11:57
À : Equest Users Mailing List
Objet : [Equest-users] Simulation Run Help
Newbie Disclaimer - As mentioned before, this is my first stab at an energy model and it is a 6 story hospital. I have finished the wizard mode and entered doors and windows in detailed mode. I was showing 0 BDL errors but now am showing one for an exterior wall that I can't seem to locate. I am attaching all files and would greatly appreciate any help resolving Exterior Wall error and why I get "Error: 1 standard file writing errors encountered." when I try to run simulation.
[Inline image 1]
Jill Moreland
Connect Program Manager
Plug Smart
Jill.Moreland at PlugSmart.com<mailto:Jill.Moreland at PlugSmart.com>
Cell: 239-233-0993
Fax: 800-518-5576
[http://gtest.plugsmart.net/LogoSprawl.PNG]
Plug Smart is accepting new clients, the best praise you could give us a recommendation to a potential new client. Everyone needs to save money, Plug Smart can make it happen.
Confidential:
This e-mail and any files transmitted with it are the property of Juice Technologies, LLC. and/or its affiliates, are confidential, and are intended solely for the use of the individual or entity to whom this e-mail is addressed. If you are not one of the named recipients or otherwise have reason to believe that you have received this e-mail in error, please notify the sender and delete this message immediately from your computer. Any other use, retention, dissemination, forwarding, printing or copying of this e-mail is strictly prohibited.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20150806/f601e847/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 1728 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20150806/f601e847/attachment-0002.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.png
Type: image/png
Size: 119899 bytes
Desc: image003.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20150806/f601e847/attachment-0002.png>
More information about the Equest-users
mailing list