[Equest-users] Terrace and balcony in façade
    Byron Burns 
    B.Burns at ha-inc.com
       
    Thu Apr 23 05:06:50 PDT 2015
    
    
  
Hello Juan,
If you are in the detailed mode save a copy of the file and revert it back to the wizard mode, save a copy of your original file in a separate folder so if all goes to heck you can revert back to it.
Go to Wizard screen 5 and select the "slab penetrates wall plane", select insulation properties as well.
Select finish then let the model compile.
Now you should see in the 3-D view an additional band on the exterior walls that indicates the point where the slab balcony penetrates the wall plane.
Copy all additional slabs, and constructions and insert into another copy of your original detailed model through direct editing the .inp files. You will need to manually edit the .inp file copying the data from your wizard model to the detailed edit model.  I recommend using notepad++ for editing the files.
Adjust the slab band for the proper width of the balcony in the detailed edit mode.  This should take care of the thermal properties of the balcony.
You can use a building shade to model the shading provided by the balcony.
[cid:image004.jpg at 01D07D9C.739725C0]
[cid:image008.jpg at 01D07D9C.739725C0]
Byron D. Burns, EIT, BEMP
Energy Engineer, Building Sciences Studio
H&A | Hankins & Anderson | www.ha-inc.com<http://www.ha-inc.com>
d: (804) 420-1622 p: (804) 285-4171 f: (804) 217-8520
From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Juan Carlos Lopez
Sent: Wednesday, April 22, 2015 5:05 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Terrace and balcony in façade
Hello All
My Project in México city has change and it has terraces and balcony in almost all apartments, is there any way to model it as external  part of the façade? Because they are different kind of terrace, and they are different in every level.
Attached are some images of façade and section of the building.
Hope you can help me out with this.
Thank you & regards.
  Juan Carlos López
  Modelaje Energético y Sustentabilidad
[cid:3465383950_184167943]
   Tel.: + 52 (55)  5253.6030
   Ext. 304
____________________________________________________________________________________
        [Imagen2] <http://1.bp.blogspot.com/-nK_1WDDox5E/UKQLHrHRP6I/AAAAAAAAAHU/aRfm6l1WrPo/s1600/Imagen2.jpg>           Antes de imprimir este correo electrónico, piense bien si es necesario hacerlo: El medio ambiente es cuestión de todos.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20150423/d30116ec/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image005.png
Type: image/png
Size: 15889 bytes
Desc: image005.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20150423/d30116ec/attachment-0002.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image006.jpg
Type: image/jpeg
Size: 942 bytes
Desc: image006.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20150423/d30116ec/attachment-0006.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image004.jpg
Type: image/jpeg
Size: 38252 bytes
Desc: image004.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20150423/d30116ec/attachment-0007.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image008.jpg
Type: image/jpeg
Size: 17738 bytes
Desc: image008.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20150423/d30116ec/attachment-0008.jpg>
    
    
More information about the Equest-users
mailing list