[Equest-users] 90.1 G3.1.1 and Manufacturing Facilities
Marcus Eliason
meliason at apollobbc.com
Thu Apr 30 13:08:53 PDT 2015
Nick,
Thanks for the insight. I was able to find an ASHRAE interpretation (IC 90.1-2007-05) that is some help, but as the manufacturing area is the predominant condition, changing it for the G.3.1.1 exceptions does not appear applicable. I did find a few LEED CIRs (#5313 and #2423) that say that if the HVAC serving a “process” space is to meet process requirements, and not occupant comfort, than modeling the systems neutral between the Proposed and Baseline is still allowed. I think either way it is going to be a fight with LEED though. Thanks again for your help.
Regards,
Marcus T Eliason, PE, LEED AP
Consultant
Apollo BBC
Better Building Consultants
713.869.0000
5116 Bissonnet, No 262
Bellaire, Texas 77401
www.apollobbc.com
Better Answers.
> On Apr 28, 2015, at 2:09 PM, Nicholas Caton <ncaton at catonenergy.com> wrote:
>
> Hi Marcus,
>
> Noting the phrase "predominant condition" sources from the subnotes of Table
> G3.1.1A, and addresses separate issues from those tackled by the exceptions
> under section G3.1.1, it is my impression you should be free to leverage
> G3.1.1 exception 'b' for the zones with atypical process loads, even if
> those zones make up the majority of the facility by area. I can't speak for
> LEED precedent in this circumstance, but your proposal passes my gut check
> for what it's worth.
>
> That said, you should ideally:
> 1. Spend at least one hot coffee mug trawling through
> http://www.usgbc.org/leed-interpretations to collect/review any directly
> applicable precedents. If you come up empty, a cursory review of
> http://www.leeduser.com/discuss may be illuminating, but be mindful even
> though GBCI/USGBC staff participate there, those discussions are not
> considered "official" and are less cite-able.
> 2. Take the stance/tone of "does not seem appropriate" and develop that into
> a strong justification to leverage this exception. Have a discussion with
> the mechanical designer(s) so that you can concisely address why a CV system
> makes sense for the actual design in lieu of a VAV system, and further
> outline how the substantially different process/occupancy loads in play
> support this descision.
> 3. Present that justification and proposal to use a Baseline system type #4
> for those spaces to GBCI prior to submission (read: well in advance of your
> own submission deadline), to get an official response you can directly cite
> in documentation. Leverage the "certification question" button here:
> http://www.usgbc.org/contactus
>
> A related point/suggestion: in the past I've handled the conundrum of
> process-heavy facilities of this nature, where the incident process loads
> drown out the otherwise substantially energy-efficient building systems. I
> have since resolved that next time I am handling one of these projects under
> LEED-NC, I would open a discussion with GBCI to propose applying the LEED-CS
> alternative compliance path (ACP) for EAp2/EAc1. From putting that to
> practice, it strikes me as a very fair and appropriate alternative framework
> to adjust LEED EAc1 point thresholds, rewarding efficient design
> hidden/muted behind substantial process loads which the building owner may
> have little/zero influence or control over.
>
> Just food for thought - though that may be a battle you might want to pass
> on ;)
>
> Best of luck,
>
> ~Nick
>
>
> NICK CATON, P.E.
> Owner
>
> Caton Energy Consulting
> 1150 N. 192nd St., #4-202
> Shoreline, WA 98133
> office: 785.410.3317
> www.catonenergy.com
>
> -----Original Message-----
> From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On
> Behalf Of Marcus Eliason
> Sent: Tuesday, April 28, 2015 7:26 AM
> To: equest-users at lists.onebuilding.org
> Subject: [Equest-users] 90.1 G3.1.1 and Manufacturing Facilities
>
> Hello,
>
> I am modeling a large, conditioned manufacturing facility with attached
> offices. The baseline building is modeled as System 8, “VAV with PFP
> Boxes.” The proposed building uses constant volume RTUs. From a design
> perceptive, I see how a VAV system makes sense for a standard office
> building, but using VAV for a large and tall manufacturing space does not
> seem appropriate. Does anyone have any experience using the exceptions in
> Section G3.1.1 to allow for a constant volume system (similar to Sys 4) in a
> manufacturing space?
>
> The manufacturing area will have higher process and occupancy loads than the
> offices, but is the predominant condition when compared to the office
> spaces. I did see some 90.1 interpretations that indicate that only the
> smaller spaces (<25,000 sqft) would be eligible for the G3.1.1 exceptions,
> but wanted to see if anybody had a different experience arguing it to LEED.
>
>
> Thank you,
>
>
> Marcus T Eliason, PE, LEED AP
> Consultant
>
> Apollo BBC
> Better Building Consultants
>
> 713.869.0000
> 5116 Bissonnet, No 262
> Bellaire, Texas 77401
> www.apollobbc.com
>
>
> Better Answers.
>