[Equest-users] App G Baseline CHW Pump Power
    Christian Kaltreider 
    ckaltreider at sudassociates.com
       
    Mon Nov 25 12:26:04 PST 2013
    
    
  
Yes, that lays it out pretty clearly.  22 W/GPM system total.  
 
I wonder if future 90.1 versions will prevent gaming of the system (intentional or not) by offering guidance on power allocation among pumps?  
 
Thanks for the helpful replies,
Christian
 
From: Bishop, Bill [mailto:bbishop at pathfinder-ea.com] 
Sent: Monday, November 25, 2013 2:11 PM
To: Joe Fleming; 'Christian Kaltreider'; equest-users at lists.onebuilding.org
Subject: RE: [Equest-users] App G Baseline CHW Pump Power
 
Christian,
 
Confirming what Joe says, an ASHRAE interpretation <https://www.ashrae.org/File%20Library/docLib/StdsInterpretations/IC-90-1-2007-14.pdf>  clarified that 22W/gpm is the total power of all baseline CHW pumps.
 
Regards,
Bill
 
William Bishop, PE, BEMP, BEAP, LEED AP | Pathfinder Engineers & Architects LLP
Senior Energy Engineer
 
134 South Fitzhugh Street                 Rochester, NY 14608
T: (585) 325-6004 Ext. 114            F: (585) 325-6005
 <mailto:wbishop at pathfinder-ea.com> bbishop at pathfinder-ea.com            <http://www.pathfinder-ea.com/> www.pathfinder-ea.com
P   Sustainability – the forest AND the trees. P       
 
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Joe Fleming
Sent: Monday, November 25, 2013 2:07 PM
To: 'Christian Kaltreider'; equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] App G Baseline CHW Pump Power
 
Almost certain that the GBCI interprets it as a whole system divvy, not each pump with 22W/GPM.
 
Regards
 
 
Joe Fleming  |  PE, LEED AP BD+C, BEMP
Commissioning Agent / Energy Modeler | The Spinnaker Group
561.602.3132 | joe at thespinnakergroupinc.com 
 
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Christian Kaltreider
Sent: Monday, November 25, 2013 2:01 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] App G Baseline CHW Pump Power
 
Hello,
 
In November 2010, around the same time someone was modeling a building that looked like a turkey, there was a conversation on this list about baseline CHW pump power:
 
http://lists.onebuilding.org/htdig.cgi/equest-users-onebuilding.org/2010-November/006941.html
 
Part of the discussion was some back and forth about how to apply G 3.1.3.10.  This section calls for baseline pump power to equal 22W/GPM and for the CHW pumping configuration to be primary/secondary.  Some had the opinion that each pump (primary and secondary loops) should have 22 W/GPM assigned to it, while others thought that the total CHW pump system power should sum to 22 W/GPM, and that it was up to the modeler to divvy up the power among pumps as they see fit.  I did not see a clear conclusion.  
 
Does anyone know if a general consensus was reached?
 
Thanks,
Christian
 
 
Christian Kaltreider, LEED AP | Energy Analyst
Sud Associates, P.A. | T 828.255.4691 | F 828.255.4949 | www.sudassociates.com
 
 
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20131125/4f938ad2/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 3248 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20131125/4f938ad2/attachment.jpeg>
    
    
More information about the Equest-users
mailing list